FB_BA_InRngAzm
FB_BA_InRngAzm 1:
The function block FB_BA_InRngAzm checks whether the current azimuth angle (horizontal position of the sun) lies within the limits entered. As can be seen in the overview, the function block provides an additionally evaluation as to whether the sun protection of a window group should be activated. Therefore, all subsequent considerations apply to one window group.
The sun incidence azimuth angle on a flat facade will always be facade orientation-90°... facade orientation+90°.
FB_BA_InRngAzm 2:
If the facade has lateral projections, however, this range is limited. This limitation can be checked with the help of this function block. However, the position of the window group on the facade also plays a role. If it lies centrally, this gives rise to the following situation (the values are only examples):
FB_BA_InRngAzm 3:
The values change for a group at the edge:
FB_BA_InRngAzm 4:
The beginning of the range fSttRng may thereby be larger than the end fEndRng; it is then considered beyond 0°:
Sample
fAzm
10.0°
fSttRng
280.0°
fEndRng
20.0°
bOut
TRUE
However, the area under consideration must not be greater than 180° or equal to 0°, as this would be unrealistic. Such entries result in an error on the output bErr – the test output bOut is then additionally set to FALSE.
FB_BA_InRngAzm 5: Inputs
  fAzm     : REAL;
  fSttRng  : REAL;
  fEndRng  : REAL;
Type
fAzm
REAL
Current azimuth angle.
fSttRng
REAL
Start of range [°].
fEndRng
REAL
End of range [°].
FB_BA_InRngAzm 6: Outputs
  bOut       : BOOL;
  bErr       : BOOL;
  sErrDescr  : T_MAXSTRING;
Type
bOut
The facade element is in the sun if the output is TRUE.
bErr
In case of a fault, e.g. if warning stages are active, this output is set to TRUE.
sErrDescr
T_MAXSTRING
Contains the error description.
Error description
01: Error: fSttRng or fEndRng less than 0° or greater than 360°.
02: Error: The difference between fSttRng and fEndRng is greater than 180°. This range is too large for analyzing the insolation on a facade.
Development environment
Required PLC library
TwinCAT from v3.1.4024.22
Tc3_BA2 from v5.2.5.0