FB_BA_InRngAzm
This function block FB_BA_InRngAzm checks whether the current azimuth angle (horizontal position of the sun) lies within the limits entered. As can be seen in the overview, the function block provides an additionally evaluation as to whether the sun protection of a window group should be activated. Therefore the observations in the remainder of the text always apply to one window group.
The sun incidence azimuth angle on a smooth facade will always be facade orientation-90°... facade orientation+90°.
If the facade has lateral projections, however, this range is limited. This limitation can be checked with the help of this function block. However, the position of the window group on the facade also plays a role. If it lies centrally, this gives rise to the following situation (the values are only examples):
The values change for a group at the edge:
The beginning of the range fSttRng may thereby be larger than the end fEndRng; it is then regarded beyond 0°:
Example
fAzm | 10.0° |
fSttRng | 280.0° |
fEndRng | 20.0° |
bOut | TRUE |
However, the range regarded may not be greater than 180° or equal to 0° – this would be unrealistic. Such entries result in an error on the output bErr – the test output bOut is then additionally set to FALSE.
fAzm : REAL;
fSttRng : REAL;
fEndRng : REAL;
fAzm | REAL | Current azimuth angle |
fSttRng | REAL | Start of range [°] |
fEndRng | REAL | End of range [°]. |
Outputs
bOut : BOOL;
bErr : BOOL;
sErrDescr : T_MAXSTRING;
bOut | BOOL | The facade element is in the sun if the output is TRUE. |
bErr | BOOL | In case of a fault, e.g. if warning stages are active, this output is set to TRUE. |
sErrDescr | Contains the error description |
Error description |
01: Error: fSttRng or fEndRng less than 0° or greater than 360°. |
02: Error: The difference between fSttRng and fEndRng is greater than 180°. This range is too large for analyzing the insolation on a facade. |
TwinCAT from v3.1.4024.22 | Tc3_BA2 from v5.2.5.0 |