FB_BA_SpRmT
The function block FB_BA_SpRmT assigns setpoints for cooling and heating operation to each of the energy levels Protection, Economy, PreComfort and Comfort.
The following graphics illustrates the behavior of the function block; the entered values should be regarded as examples:
The parameter fShiftHtg is applied to the Comfort and Precomfort values for the heating mode as central setpoint shift. In addition, winter compensation fWinCpsn is applied.
Similarly, the following applies for the cooling mode: The parameter fShiftCol is applied to the Comfort and Precomfort values. In addition, the summer compensation value fSumCpsn is applied.
Auto-correction
The temperature adjustment is intended for small corrections of the values. Although it is possible to enter any input values, a heating system will only work in a meaningful manner if the setpoints have ascending values in the following order:
- Protection Heating
- Economy Heating
- Precomfort Heating
- Comfort Heating
- Comfort Cooling
- Precomfort Cooling
- Economy Cooling
- Protection Cooling
Auto-correction works according to the following principle: Starting with the value Economy Heating, the system checks whether this value is smaller than the lower value of Protection Heating. If this is the case, the value for Economy Heating is adjusted to match the value for Protection Heating. The system then checks whether the value for Precomfort Heating is less than Economy Heating and so on, until the value for Protection Cooling is compared with the value for Economy Cooling. If one or several values were corrected, this is indicated with a TRUE signal at output bValCorr.
fPrtcHtg : REAL;
fEcoHtg : REAL;
fPreCmfHtg : REAL;
fCmfHtg : REAL;
fCmfCol : REAL;
fPreCmfCol : REAL;
fEcoCol : REAL;
fPrtcCol : REAL;
fShiftHtg : REAL;
fShiftCol : REAL;
fSumCpsn : REAL;
fWrWinCpsn : REAL;
fPrtcHtg | REAL | Basic setpoint "Protection Heating". |
fEcoHtg | REAL | Basic setpoint "Economy Heating". |
fPreCmfHtg | REAL | Basic setpoint "PreComfort Heating". |
fCmfHtg | REAL | Basic setpoint "Comfort Heating". |
fCmfCol | REAL | Basic setpoint "Comfort Cooling". |
fPreCmfCol | REAL | Basic setpoint "PreComfort Cooling". |
fEcoCo | REAL | Basic setpoint "Economy Cooling". |
fPrtcCol | REAL | Basic setpoint "Protection Cooling". |
fShiftHtg | REAL | Setpoint value shift "Heating". |
fShiftCol | REAL | Setpoint value shift "Cooling". |
fSumCpsn | REAL | Value Summer compensation. |
fWinCpsn | REAL | Value Winter compensation. |
Outputs
bValCorr : BOOL;
fPrPrtcHtg : REAL;
fPrEcoHtg : REAL;
fPrPreCmfHtg : REAL;
fPrCmfHtg : REAL;
fPrCmfCol : REAL;
fPrPreCmfCol : REAL;
fPrEcoCol : REAL;
fPrPrtcCol : REAL;
stPrSp : ST_BA_SpRmT;
bValCorr | BOOL | Autocorrection for the values was performed, see above. |
fPrPrtcHtg | REAL | Resulting "Protection Heating" setpoint. |
fPrEcoHtg | REAL | Resulting setpoint "Economy Heating". |
fPrPreCmfHtg | REAL | Resulting setpoint "PreComfort Heating". |
fPrCmfCol | REAL | Resulting setpoint "Comfort Cooling". |
fPrPreCmfCol | REAL | Resulting setpoint "PreComfort Cooling". |
fPrEcoCol | REAL | Resulting setpoint Economy Cooling. |
fPrPrtcCol | REAL | Resulting setpoint "Protection Cooling". |
stPrSp | Consolidated output of the resulting values in a structure. |
TwinCAT from v3.1.4024.22 | Tc3_BA2 from v5.2.5.0 |