FB_BA_Anlg3Pnt
FB_BA_Anlg3Pnt 1:
The function block FB_BA_Anlg3Pnt is intended for control of three-point actuators for valves or dampers. A continuous control signal for positioning an actuator is converted into the binary commands for opening and closing.
If the deviation between the position setpoint fIn and the calculated actual position value fPos of the actuator is greater than the set threshold fHys / 2, the function block starts to correct the position by switching the outputs bOpn or bCls, depending on the amount of the control deviation:
bOpn
bCls
fIn - fPos > fHys / 2
TRUE
FALSE
fIn - fPos < - fHys / 2
FALSE
TRUE
If the function block reaches an end position fOut = 0 or fOut = 100 due to a corresponding input value fIn, the corresponding switching output is switched off. After a certain period of time, however, forced referencing takes place:
Any deactivation of the continuous signal must be implemented by the user through external programming.
The input fIn is automatically limited internally to the range of 0...100 %.
This also applies to the inputs fHys and fRefVal. The travel times nTiCls as well as nTiOpn are both limited downwards to 10 (milliseconds).
A rising edge at bRef triggers a referencing command (setting the calculated actual position to fRefVal).
If the drive has limit switches, these can also be detected directly by means of a digital input and used for referencing at bRef.
FB_BA_Anlg3Pnt 2: Inputs
  fIn         : REAL;
  fHys        : REAL;
  nTiCls      : UDINT;
  nTiOpn      : UDINT;
  bRef        : BOOL;
  fRefVal     : REAL;
  bCloseInit  : BOOL;
Type
fIn
REAL
Setpoint for the actuator position [0…100 %]. Internally limited to values between 0 and 100.
fHys
REAL
Hysteresis for the actuator position [0…100 %]. Internally limited to values between 0 and 100.
nTiCls
UDINT
Run time of the actuator from open to closed [ms]. Internally limited to values between 0 and 100.
nTiOpn
UDINT
Run time of the actuator from closed to open [ms]. Internally limited to values between 0 and 100.
bRef
Edge references the internal position memory of the drive to value of fRefVal [0…100 %].
fRefVal
REAL
Value for referencing the actuator with bRef [0…100 %]. Internally limited to values between 0 and 100.
bCloseInit
If this input is TRUE, output bCls is TRUE for the time nTiOpn [ms].
FB_BA_Anlg3Pnt 3: Outputs
  bCls    : BOOL;
  bOpn    : BOOL;
  fPos    : REAL;
Type
bCls
Output for closing the actuator.
bOpn
Output for opening the actuator.
fPos
REAL
Current calculated actuator position [0…100 %].
Development environment
Required PLC library
TwinCAT from v3.1.4024.22
Tc3_BA2 from v5.2.5.0