FB_BA_SpSupVis
FB_BA_SpSupVis 1:
Function block FB_BA_SpSupVis for processing and checking the lower and upper setpoint of a supply air humidity or temperature control.
Checks and limits for the setpoints
The function block limits the setpoints. The following two tables show which parameters are checked and what the response is in the event of an error.
Checking
Action
fSpLo > fSpHi
The last valid values of fSpLo and fSpHi are used.
fSpMin >= fSpMax
The last valid values of fSpMin and fSpMax are used.
fSpHi > fSpMax
fPrSpHi = fSpMax
fSpLo < fSpMin
fPrSpLo = fSpMin
Checking
bErr
Action
fSpMin >= fSpMax
TRUE
fSpErr = ((fSpMin + fSpMax) / 2)
fPrSpHi = fPrSpLo = fPrRcv = fSpErr
fSpHi < fSpMin
fSpLo > fSpMax
The difference between the setpoints describes an energy-neutral zone. With supply air control, no heating or cooling would take place within the neutral zone.
FB_BA_SpSupVis 2:
The checked and possibly limited setpoints are output at the function block output as fPrSpHi and fPrSpLo (Present Setpoint).
Setpoint for heat recovery
For a heat recovery system, the setpoint fSpRcv is calculated either from the average of the upper and lower setpoints, fSpHi and fSpLo or as a function of the control direction of the heat recovery system.
The method is defined by the input variable bSlcnSpRcv:
bSlcnSpRcv
fSpRcv
TRUE
Average of fSpLo and fSpHi
FALSE
Depends on control direction, defined through input bActRcv
If the setpoint is defined depending on the control direction, the following applies:
bActRcv
Control direction
fSpRcv
TRUE
direct (cooling)
fSpHi
FALSE
indirect (heating)
fSpLo
Heat recovery
FB_BA_SpSupVis 3:
FB_BA_SpSupVis 4: Inputs
  bEn         : BOOL;
  fSpHi       : REAL;
  fSpLo       : REAL;
  fSpMax      : REAL;
  fSpMin      : REAL;
  bActnRcv    : BOOL;
  bSlcnSpRcv  : BOOL;
Type
bEn
Function block enable. If bEn = FALSE, all output parameters are 0.0.
fSpHi
REAL
Upper setpoint input value to be checked.
fSpLo
REAL
Lower setpoint input value to be checked.
fSpMax
REAL
Maximum setpoint.
fSpMin
REAL
Minimum setpoint.
bActnRcv
Direction of action of the downstream heat recovery.
bSlcnSpRcv
Setpoint selection of the downstream heat recovery system.
FB_BA_SpSupVis 5: Outputs
  fPrSpHi    : REAL;
  fPrSpLo    : REAL;
  fSpRcv     : REAL;
  bErr       : BOOL;
  sErrDescr  : T_MAXSTRING;
Type
fPrSpHi
REAL
Output value for the upper setpoint.
fPrSpLo
REAL
Output value for the lower setpoint.
fSpRcv
REAL
Output value for the resulting heat recovery setpoint.
bErr
In case of a fault, e.g. if warning stages are active, this output is set to TRUE.
sErrDescr
T_MAXSTRING
Contains the error description.
Error description
01: Warning: The setpoints are not in a logical order: Either (fSpMin >= fSpMax) OR (fSpHi < fSpMin) OR (fSpLo > fSpMax)
Development environment
Required PLC library
TwinCAT from v3.1.4024.22
Tc3_BA2 from v5.2.5.0