FB_HVACHeatingCurveEx
The heating curve serves to determine the setpoint for the flow temperature of a heating circuit, depending on the outside temperature. Compared with the FB_HVACHeatingCurve, the heating curve is shown as a function.
z = 20 - rDesignTemp;
u = 20 - rOutsideTemp;
bSetDefault : BOOL;
rOutsideTempDamped : REAL;
bDayOperation : BOOL;
bReset : BOOL; eDataSecurityType: If eDataSecurityType:= eHVACDataSecurityType_Persistent, the persistent VAR_IN_OUT variables of the function block are stored in the flash of the computer if a value changes. For this to work, the function block FB_HVACPersistentDataHandling must be instanced once in the main program, which is called cyclically. Otherwise the instanced FB is not released internally.
Notice | |
A cyclically changing variable must never be linked with the IN_OUT variable of a function block, if eDataSecurityType:= eHVACDataSecurityType_Persistent. It would lead to early wear of the flash memory. |
rOutsideTempDamped: This input variable transfers the current damped outside temperature to the function block.
bReset: Acknowledge input in the event of a fault.
rTempSetpoint : REAL;
bInvalidParameter : BOOL;rTempSetpoint: The calculated setpoint [°C] for the flow temperature.
bInvalidParameter: Indicates that there is an incorrect input parameter. bInvalidParameter must be acknowledged with bReset.
rMinTempSetpoint : REAL;
rMaxTempSetpoint : REAL;
rDesignTemp : REAL;
rSlope : REAL;
rCurve : REAL;rMinTempSetpoint: The minimum value for the setpoint of the flow temperature [°C] is defined by this variable. The variable is saved persistently. Preset to 20.
rMaxTempSetpoint: The maximum value for the setpoint of the flow temperature [°C] is defined by this variable. The variable is saved persistently. Preset to 90.
rDesignTemp: Design temperature [°C] for the dimensioning of a heating system. Typical values for Germany lie between -12 ° C and -16 ° C. The variable is saved persistently. Preset to -16.
rSlope: Factor for the slope. The variable is saved persistently. Preset to 1.
rCurve: Factor for the curve. The variable is saved persistently. Preset to 0.5.
Course of the heating characteristic curves
Flow temperature of 50 °C at approx. -9.2 °C
Flow temperature of 50 °C at approx. -9.4 °C
Flow temperature of 50 °C at approx. -7.8 °C
Flow temperature of 50 °C at approx. -8.3 °C
Flow temperature of 60 °C at approx. -0.2 °C
Flow temperature of 60 °C at approx. -3.0 °C
Development environment | required library | required function |
TwinCAT 3.1 build 4022.16 or higher | Tc2_HVAC V3.3.1.0 | TF8000 | TC3 HVAC V1.0.0.0 |