FB_HVACScale
A raw analog value is scaled to the specified measuring range and returned as the function value. If the raw value extends beyond the upper or lower measuring range, the corresponding limit value is output. There must be a difference of at least 0.01 between the upper and lower limit values for the raw data. If this is not the case, the lower limit value is output. The difference between the limits is necessary so as to avoid division by zero during the internal calculation of the linear equation.
bSetDefault : BOOL;
rRawData : REAL;eDataSecurityType: If eDataSecurityType:= eHVACDataSecurityType_Persistent, the persistent VAR_IN_OUT variables of the function block are stored in the flash of the computer if a value changes. For this to work, the function block FB_HVACPersistentDataHandling must be instanced once in the main program, which is called cyclically. Otherwise the instanced FB is not released internally.
Notice | |
A cyclically changing variable must never be linked with the IN_OUT variable of a function block, if eDataSecurityType:= eHVACDataSecurityType_Persistent. It would lead to early wear of the flash memory. |
rRawData: Raw value from the terminal.
rScaledValue : REAL;rScaledValue: Scaled value.
rRawDataLowOffLimit : REAL;
rRawDataHighOffLimit : REAL;
rScaleDataLowOffLimit : REAL;
rScaleDataHighOffLimit : REAL;rRawDataLowOffLimit: Lower limit for raw value. The variable is saved persistently. Preset to 0.
rRawDataHighOffLimit: Upper limit for raw value. The variable is saved persistently. Preset to 32767.
rScaleDataLowOffLimit: Lower limit of scaled measured value. The variable is saved persistently. Preset to 0.
rScaleDataHighOffLimit: Upper limit of scaled measured value. The variable is saved persistently. Preset to 100.
Example in FBD:
Development environment | required library | required function |
TwinCAT 3.1 build 4022.16 or higher | Tc2_HVAC V3.3.1.0 | TF8000 | TC3 HVAC V1.0.0.0 |