FB_HVACCirculationPump
This function block serves to control pumps in HVAC systems.
bSetDefault : BOOL;
bEnable : BOOL;
bAuto : BOOL;
eCtrlModeActuator : E_HVACActuatorMode;
rOutsideTemp : REAL;
rValvePosition : REAL;
bFeedbPump : BOOL;
bPumpProtec : BOOL;
bAntiBlocking : BOOL;
bManSwitch : BOOL;
bCtrlVoltage : BOOL;
bReset : BOOL; eDataSecurityType: If eDataSecurityType:= eHVACDataSecurityType_Persistent, the persistent VAR_IN_OUT variables of the function block are stored in the flash of the computer if a value changes. For this to work, the function block FB_HVACPersistentDataHandling must be instanced once in the main program, which is called cyclically. Otherwise the instanced FB is not released internally.
Notice | |
A cyclically changing variable must never be linked with the IN_OUT variable of a function block, if eDataSecurityType:= eHVACDataSecurityType_Persistent. It would lead to early wear of the flash memory. |
bEnable: The function block is enabled if bEnable = TRUE.
bAuto: Input for the request from the automatic program. The request is overridden by eCtrlModeActuator.
eCtrlModeActuator: Enum that defines the operation mode (see E_HVACActuatorMode).
rOutsideTemp: Input for transmitting the outside temperature value.
rValvePosition: If there is a control valve in the hydraulic circuit of the pump, the position of the control valve must be applied here.
bFeedbPump: This input is for displaying the operating message in a visualization system and for monitoring the pump function.
bPumpProtec: A pump error message is connected to the input bPumpProtec. There is a pump error if the input bPumpProtec is FALSE. The output bPump becomes FALSE in the event of a fault. The pump can only be restarted after an acknowledgment on the input bReset.
bAntiBlocking: Input for transferring the anti-blocking request, i.e. if TRUE the request is active.
bManSwitch: If the pump has a manual/emergency switch in the control cabinet, this can be connected to the input bManSwitch; the status of the manual/emergency switch will then be monitored. The output bPump is disabled if bManSwitch= FALSE. The output bPump can only be switched on if bManSwitch = TRUE (quiescent current principle).
bCtrlVoltage: In order to suppress a torrent of messages, the error message from bPumpProtec is only acquired if the input bCtrlVoltage is TRUE.
bReset: Acknowledge input in the event of a fault.
bPump : BOOL;
byState : BYTE;
bStateManSwitch : BOOL;
bReqOutsideTemp : BOOL;
bReqValve : BOOL;
eStateModeActuator : E_HVACActuatorMode;
bErrorPumpProtec : BOOL;
bErrorPumpFeedb : BOOL;
bErrorGeneral : BOOL;
byError : BYTE;
bInvalidParameter : BOOL;bPump: Output variable for controlling a pump.
byState: Output of the pump status as a byte.
byState.0 := bEnable
byState.1 := bPump
byState.2 := bReqOutsideTemp
byState.3 := bReqValve
byState.4 := bAntiblocking
byState.5 := bFeedbPump
byState.6 := NOT bManSwitch
byState.7 := bCtrlVoltage
bStateManSwitch: Indicates the state of the manual/emergency switch. A TRUE signals that the manual/emergency operating level is activated.
bReqOutsideTemp: If the condition for requesting the pump depending on the outside temperature is TRUE, the output variable bReqOutsideTemp is TRUE.
bReqValve: If the condition for requesting the pump depending on the valve position is reached, the variable bReqValve is TRUE.
eStateModeActuator: Indicates which operation mode the actuator is in (see E_HVACActuatorMode).
bErrorPumpProtec: Pump error.
bErrorPumpFeedb: If the input bFeedbPump does not go TRUE within the time of tFeedbPumpDelay (tFeedbPumpDelay must be > t#0s) after setting the output bPump, this is recognized as a fault and this output is set to TRUE and the output bPump to FALSE. The error message must be acknowledged with bReset.
bErrorGeneral: There is a general error.
byError: Output of the error as a byte.
byError.1 := bInvalidParameter
byError.2 := bErrorGeneral
byError.3 := bErrorPumpProtec
byError.4 := bErrorPumpFeedb
bInvalidParameter: TRUE if an error has occurred during the plausibility check. The message must be acknowledged with bReset.
tStopDelay : TIME;
tFeedbPumpDelay : TIME;
rOutsideTempLimit : REAL;
rValvePositionLimit : REAL;
eReqOutsideTemp : E_HVACReqOutsideTemp;
eReqValve : E_HVACReqValve;tStopDelay: The time tStopDelay [s] delays the switching off of the pump after the switch-on conditions are no longer given. The variable is saved persistently. Preset to 0 s.
tFeedbPumpDelay: The monitoring function of the pump feedback message [s] is only active if tFeedbPumpDelay is > t#0s. If tFeedbPumpDelay = t#0s the monitoring function is deactivated (0s..3600s). The variable is saved persistently. Preset to 0 s.
rOutsideTempLimit: Value [°C] above or below which the pump is switched on or off depending on the outside temperature (-60°C..60°C). The variable is saved persistently. Preset to 10 °C.
rValvePositionLimit: Threshold value for the position of a control valve associated with a pump, from which the pump should switch on automatically, e.g. heater pump (0%..100%). The variable is saved persistently. Preset to 3%.
eReqOutsideTemp: Depending on the outside temperature, the pump can be compulsorily switched on, e.g. for frost protection purposes when the temperature limit value rOutsideTempLimit is undershot. The prerequisite is that bEnable = TRUE and that the pump is in automatic mode (see E_HVACRegOutsideTemp). The variable is saved persistently.
Notice | |
Manual off overrides the frost protection function! |
eReqValve: Depending on the position of the valve associated with the pump, the pump can be switched on when the threshold value of rValvePositionLimit is exceeded. The ENUM activates the switch-on via the valve position. In addition, the ENUM determines whether the temperature-dependent and valve position-dependent switch-on conditions are ORed or ANDed together (see E_HVACRegValve). The variable is saved persistently.
The table below shows a summary of all possible combinations:
eReqOutsideTemp | eReqValve | Function | Application |
OTLowerLimit | NoRequest | outsidetemp lower limit |
OTLowerLimit | OrValvePosHigherLimit | outsidetemp OR valve higher limit | Heating circuit, air heater |
OTLowerLimit | AndValvePosHigherLimit | outsidetemp AND valve higher limit |
OTHigherLimit | NoRequest | outsidetemp higher limit |
OTHigherLimit | OrValvePosHigherLimit | outsidetemp OR valve higher limit |
OTHigherLimit | AndValvePosHigherLimit | outsidetemp AND valve higher limit | Cooler pump |
NoRequest | NoRequest | no request | Primary pump |
NoRequest | OrValvePosHigherLimit | valve higher limit |
NoRequest | AndValvePosHigherLimit | not valid |
By means of various combinations of the two variables, eReqOutsideTemp and eReqValve, this function block can be adapted to the requirements of a heating circuit, an air heater, an air cooler or a feed pump.
Development environment | required library | required function |
TwinCAT 3.1 build 4022.16 or higher | Tc2_HVAC V3.3.1.0 | TF8000 | TC3 HVAC V1.0.0.0 |