FB_IEC870_5_104Master
An instance of the function block FB_IEC870_5_104Master can be used to implement an IEC 60870-5-104 central station (master, high-level) in the TwinCAT PLC. A connection to the slave is established for each instance of the function block.
The function block features the following tasks;
- STARTDT (starts the data exchange);
- STOPDT (stops the data exchange);
Normally, the data exchange starts automatically once the connection has been established. This is the default configuration of the function block. If required the data exchange can be stopped or started by calling the actions.
hTable : T_HAODBTable;
END_VARhTable: Application object database handle (hash table handle). The table handle must be initialised once with the function F_iecCreateTableHnd before it can be used.
sSrvNetID : T_AmsNetID := '';
protPara : ST_IEC870_5_104ProtocolParams := ( bControlDT := TRUE, bDTControlled := FALSE,
sRemoteHost := '', nRemotePort := 2404 );
sysPara : ST_IEC870_5_101SystemParams := ( bEndOfInit := FALSE, asduAddr := 11, tSyncTimeut := T#0s );
acqPara : ST_IEC870_5_101AcquisitionParams;
pAOEntries : POINTER TO ARRAY[0..IEC870_ANYSIZE_ARRAY] OF ST_IEC870_5_101AODBEntry := 0;
cbAOEntries : UDINT := 0;
pInputs : PVOID := 0;
cbInputs : UDINT := 0;
pOutputs : PVOID := 0;
cbOutputs : UDINT := 0;
pMemory : PVOID := 0;
cbMemory : UDINT := 0;
pData : PVOID := 0;
cbData : UDINT := 0;
bEnable : BOOL := TRUE;
END_VARsSrvNetID: String containing the network address of the TwinCAT TCP/IP Connection Server. For the local computer (default) an empty string may be specified.
protPara: IEC 60870-5-104 protocol parameters.
sysPara: System parameter.
acqPara: Parameter for cyclic data acquisition.
pAOEntries: Address of the first application object database variable.
cbAOEntries: Byte size of the application object database variables.
pInputs: Address of the PLC process data area for the inputs.
cbInputs: Byte size of the PLC process data area for the inputs.
pOutputs: Address of the PLC process data area for the outputs.
cbOutputs: Byte size of the PLC process data area for the outputs.
pMamory: Address of the PLC process data area for the flags.
cbMamory: Byte size of the PLC process data area for the flags.
pData: Address of the PLC data area.
cbData: Byte size of the PLC data area.
bEnable: Activates/deactivates the function block (communication and connections).
The addresses can be determined with the ADR operator and the byte sizes with the SIZEOF operator.
system : ST_IEC870_5_104ExSystemInterface;
eConnState : E_SocketConnectionState := eSOCKET_DISCONNECTED;
eDTState : E_IEC870_5_104DataTransferState := eIEC870_STOPDT;
END_VARsystem: System interface. This variable is used by other IEC application functions as a communication interface for the IEC device (here: central station).
- Member variable system.device is expected by the F_iecSetAOQuality function as VAR_IN_OUT parameter, for example.
- Member variable system.device.errors is a device error FIFO. The PLC application can read and analyse registered errors.
eConnState: Status of the TCP/IP connection with the slave..
eDTState: Status of the IEC60870-5-104 data exchange (STARTDT, STOPDT)
Examples (High-Level interface):
Further examples:
In the following example the device error FIFO is read cyclically, and the registered errors are written into the TwinCAT XAE->"Error List" window.
fbClient : FB_IEC870_5_104Master;(* IEC 60870-5-104 master function
block instance *)
REPEAT
fbClient.system.device.errors.RemoveError( );
IF fbClient.system.device.errors.bOk THEN
ADSLOGSTR( ADSLOG_MSGTYPE_ERROR OR ADSLOG_MSGTYPE_LOG,
'IEC60870-5-104 master error: 0x%s',
DWORD_TO_HEXSTR(
fbClient.system.device.errors.getError.nErrId, 8, FALSE) );
END_IF
UNTIL NOT fbClient.system.device.errors.bOk
END_REPEAT
...Requirements
Development environment | Target system type | PLC libraries to be linked (category group) |
TwinCAT v3.1.4012.0 | PC oder CX (x86, x64, Arm®) | Tc2_IEC60870_5_10x (Communication->IEC60870) |