FB_MBUdpReadRegs (Modbus function 3)
FB_MBUdpReadRegs (Modbus function 3) 1:
This function is used for reading 1 to 128 output registers (16 bit). The first byte contains the lower eight bits and the second byte the upper eight bits.
FB_MBUdpReadRegs (Modbus function 3) 2: Inputs
    sIPAddr       : STRING(15);
    nTCPPort      : UINT:= MODBUS_TCP_PORT;
    nUnitID       : BYTE:=16#FF;
    nQuantity     : WORD;
    nMBAddr       : WORD;
    cbLength      : UDINT;
    pDestAddr     : POINTER TO BYTE;
    bExecute      : BOOL;
    tTimeout      : TIME;
Type
sIPAddr
STRING (15)
Is a string containing the IP address of the target device.
nTCPPort
UINT
Port number of the target device.
nUnitID
BYTE
Identification number of a serial sub-network device. If a device is addressed directly via TCP/IP, this value must be 16#FF.
nQuantity
WORD
Number of output registers (data words) to be read. The value zero is not permitted.
nMBAddr
WORD
Start address of the output register (word offset) to be read.
cbLength
UDINT
Contains the maximum byte size available in the destination buffer for the register values to be read. The buffer must have at least the byte size: nQuantity * 2.
pDestAddr
POINTER TO BYTE
Contains the address of the destination buffer into which the data are to be read. The buffer can be a single variable, an array or a structure, whose address can be determined with the ADR operator.
bExecute
The function block is enabled by a rising edge at this input.
tTimeout
TIME
States the length of the timeout that may not be exceeded by execution of the ADS command.
FB_MBUdpReadRegs (Modbus function 3) 3: Outputs
    bBUSY      : BOOL;
    bError     : BOOL;
    nErrId     : UDINT;
    cbRead     : UDINT;
Type
bBusy
When the function block is enabled, this output is set and remains set until a feedback is received.
If an ADS error should occur during the transfer of the command, then this output is set once the bBusy output is reset.
nErrId
UDINT
Returns the ADS error number when the bError output is set.
cbRead
UDINT
Contains the number of bytes currently read.
Development environment
Target platform
PLC libraries to include
TwinCAT v3.1.0
IPC or CX (x86, x64, ARM®)
Tc2_ModbusSrv
