FB_MBReadRegs (Modbus function 3)
This function is used for reading 1 to 128 output registers (16 bit). The first byte contains the lower eight bits and the second byte the upper eight bits.
sIPAddr : STRING(15);
nTCPPort : UINT:= MODBUS_TCP_PORT;
nUnitID : BYTE:=16#FF;
nQuantity : WORD;
nMBAddr : WORD;
cbLength : UDINT;
pDestAddr : POINTER TO BYTE;
bExecute : BOOL;
tTimeout : TIME;
END_VAR Name | Type | Description |
sIPAddr | STRING (15) | Is a string containing the IP address of the target device. |
nTCPPort | UINT | Port number of the target device. |
nUnitID | BYTE | Identification number of a serial sub-network device. If a device is addressed directly via TCP/IP, this value must be 16#FF. |
nQuantity | WORD | Number of output registers (data words) to be read. The value zero is not permitted. |
nMBAddr | WORD | Start address of the output register (word offset) to be read. |
cbLength | UDINT | Contains the maximum byte size available in the destination buffer for the register values to be read. The buffer must have at least the byte size: nQuantity * 2. |
pDestAddr | POINTER TO BYTE | Contains the address of the destination buffer into which the data are to be read. The buffer can be a single variable, an array or a structure, whose address can be determined with the ADR operator. |
bExecute | BOOL | The function block is enabled by a rising edge at this input. |
tTimeout | TIME | States the length of the timeout that may not be exceeded by execution of the ADS command. |
Outputs
bBUSY : BOOL;
nErrId : UDINT;
cbRead : UDINT;
bBusy | BOOL | When the function block is enabled, this output is set and remains set until a feedback is received. |
bError | BOOL | If an ADS error should occur during the transfer of the command, then this output is set once the bBusy output is reset. |
nErrId | UDINT | Returns the ADS error number when the bError output is set. |
cbRead | UDINT | Contains the number of bytes currently read. |
Sample of calling the function block in FBD
PROGRAM Test
fbReadRegs : FB_MBReadRegs;
bReadRegs : BOOL;
bReadRegsBusy : BOOL;
bReadRegsError : BOOL;
nReadRegsErrorId : UDINT;
nReadRegsCount : UDINT;
nQuantity : WORD:=2;
nMBAddr : WORD:=24;
arrData : ARRAY [1..2] OF WORD;
After a rising edge of "bExecute" and successful execution of the ReadRegs command, the content of registers 25 and 26 is located in the arrData array:
Register | Array offset | Status |
25 | 1 | 0x1234 ( as byte 0x34 0x12) |
26 | 2 | 0x5563 ( as byte 0x63 0x55) |
TwinCAT v3.1.0 | IPC or CX (x86, x64, ARM®) | Tc2_ModbusSrv |