FB_MBReadCoils (Modbus function 1)
This function is used for reading 1 to 2048 digital outputs (coils). One digital output corresponds to one bit of the read data bytes.
sIPAddr : STRING(15);
nTCPPort : UINT:= MODBUS_TCP_PORT;
nUnitID : BYTE:=16#FF;
nQuantity : WORD;
nMBAddr : WORD;
cbLength : UDINT;
pDestAddr : POINTER TO BYTE;
bExecute : BOOL;
tTimeout : TIME;
END_VAR Name | Type | Description |
sIPAddr | STRING (15) | Is a string containing the IP address of the target device. |
nTCPPort | UINT | Port number of the target device. |
nUnitID | BYTE | Identification number of a serial sub-network device. If a device is addressed directly via TCP/IP, this value must be 16#FF. |
nQuantity | WORD | Number of digital inputs (data bits) to be read. The value zero is not permitted. |
nMBAddr | WORD | Start address of the digital inputs to be read (bit offset). |
cbLength | UDINT | Contains the maximum available byte size of the destination buffer into which the data are to be read. The buffer must have at least the byte size: (nQuantity + 7) / 8. |
pDestAddr | POINTER TO BYTE | Contains the address of the destination buffer into which the data are to be read. The buffer can be a single variable, an array or a structure, whose address can be determined with the ADR operator. |
bExecute | BOOL | The function block is enabled by a rising edge at this input. |
tTimeout | TIME | States the length of the timeout that may not be exceeded by execution of the ADS command. |
Outputs
bBUSY : BOOL;
nErrId : UDINT;
cbRead : UDINT;
bBusy | BOOL | When the function block is enabled, this output is set and remains set until a feedback is received. |
bError | BOOL | If an ADS error should occur during the transfer of the command, then this output is set once the bBusy output is reset. |
nErrId | UDINT | Returns the ADS error number when the bError output is set. |
cbRead | UDINT | Contains the number of bytes currently read. |
Sample of calling the function block in FBD
PROGRAM Test
fbReadCoils : FB_MBReadCoils;
bReadCoils : BOOL;
bReadCoilsBusy : BOOL;
bReadCoilsError : BOOL;
nReadCoilsErrorId : UDINT;
nReadCoilsCount : UDINT;
nQuantity. : WORD := 10;
nMBAddr. : WORD := 5;
arrData. : ARRAY [1..2] OF BYTE;
After a rising edge of "bExecute" and successful execution of the ReadCoils command, the content of digital outputs 6 - 15 is written into the arrData array:
Digital outputs | Array offset | Status |
6-13 | 1 | 0x54 Status of output 13 is the MSB of this byte (far left) |
14-15 | 2 | 0x02 as only 10 outputs are to be read, the remaining bits (3-8) are set to 0. |
TwinCAT v3.1.0 | IPC or CX (x86, x64, ARM®) | Tc2_ModbusSrv |