MC_AxRtReadForceDiff_BkPlcMc
MC_AxRtReadForceDiff_BkPlcMc 1:
MC_AxRtReadForceDiff_BkPlcMc 2:
Available from version 3.0
The function block handles determination of the actual force of the axis from the input data of two analog input terminals. The actual pressure on the A- and B-sides is converted to the force acting on the load, taking into account the areas and the sliding friction.
If only one input signal is available, a function block of type MC_AxRtReadForceSingle_BkPlcMc should be used. If the actual pressure is to be determined, a function block of type MC_AxRtReadPressureDiff_BkPlcMc should be used.
MC_AxRtReadForceDiff_BkPlcMc 3: Inputs
    AdcValueA     :   INT:=0;
    AdcValueB     :   INT:=0;
    ScaleFactorA  :   LREAL:=0.0;
    ScaleOffsetA  :   LREAL:=0.0;
    ScaleFactorB  :   LREAL:=0.0;
    ScaleOffsetB  :   LREAL:=0.0;
    SlippingOffset:   LREAL:=0.0;
    ReadingMode   :   E_TcMcPressureReadingMode:=iTcHydPressureReadingDefault;
    PressureInBar :   BOOL;
Type
AdcValueA
INT
These parameters are used to transfer the input data of the analog terminals.
AdcValueB
INT
ScaleFactorA
LREAL
[N/ADC_INC] This value represents the weighting. It determines which pressure increase corresponds to a stage of the AD converter.
ScaleOffsetA
LREAL
[N/ADC_INC] This offset is used to correct the zero point of the pressure scale.
ScaleFactorB
LREAL
ScaleOffsetB
LREAL
SlippingOffset
LREAL
[N] If the function block is used for calculating the active force, the force required to overcome the sliding friction can be entered here.
ReadingMode
The actual value to be determined can be specified here. AXIS_REF_BkPlcMc.ST_TcHydAxRtData.fActPressure is selected as default target.
PressureInBar
Option for non-atmospheric force calculation.
MC_AxRtReadForceDiff_BkPlcMc 4: Inputs/outputs
    Axis:       AXIS_REF_BkPlcMc;
Type
Axis
AXIS_REF_BkPlcMc
Here, the address of a variable of type AXIS_REF_BkPlcMc should be transferred.
MC_AxRtReadForceDiff_BkPlcMc 5: Outputs
    Error  :     BOOL;
    ErrorID:     UDINT;
Type
Error
The occurrence of an error is indicated here.
ErrorID
UDINT
An encoded indication of the cause of the error is provided here.
Behaviour of the function block:
The function block determines the actual pressure and the actual force of the axis by evaluating the variables AdcValueA and AdcValueB. The result is entered in ST_TcHydAxRtData.fActPressure.
MC_AxRtReadForceDiff_BkPlcMc 6:
The parameters assigned to an axis can be saved in ST_TcHydAxParam.fCustomerData[...], for example. This ensures that the data are loaded, saved and backed up together with the standard parameters of the axis and are also exported and imported, as required.
Determining a differential actual pressure
Commissioning is usually done in one of three ways.
Commissioning option A (preferred for ±10V)
In this case, no movement of the axis is required. The achievable accuracy is sufficient for high-quality pressure sensors in most cases.
Commissioning option B
For this option it is necessary that a function block can be approached with full system pressure in both directions. A genuine movement of the axis is not required. Approaching of the end stops can be modeled by limiting the axis movement through provisional limits or even complete mechanical fixing.
Commissioning option C
Alternatively, commissioning can be carried out without axis control. However, the accuracy that can be achieved in this way is much lower.
Determining an active force
To determine an active force, first determine the actual pressure, as described above. Entering the active areas under ScaleArreaA and ScaleArreaA causes the function block to convert the pressures on both sides into forces, taking into account the areas.