MC_StepBlock_BkPlcMc
MC_StepBlock_BkPlcMc 1:
The function block is used for referencing via a fixed stop. The function block triggers a position setting internally after the cam is found.
MC_StepBlock_BkPlcMc 2: Inputs
    Execute:                BOOL;
    Direction:              MC_Direction_BkPlcMc;
    Velocity:               LREAL;
    Acceleration:           LREAL;
    Deceleration:           LREAL;
    Jerk:                   LREAL;
    SetPosition:            LREAL;
    DetectionVelocityLimit: LREAL;
    DetectionVelocityTime:  LREAL;
    TorqueLimit:            LREAL;
    TorqueTolerance:        LREAL;
    TimeLimit:              TIME;
    DistanceLimit:          LREAL;
    BufferMode:             MC_BufferMode_BkPlcMc:=Aborting_BkPlcMc;
Type
Execute
The homing is initiated by a rising edge at this input.
Direction
The direction is specified via MC_Direction_BkPlcMc.
Velocity
LREAL
[mm/s] The required motion velocity in actual value units of the axis per second.
Acceleration
LREAL
[mm/s2] The required acceleration in actual value units of the axis per square second. If this parameter is 0.0, it is replaced by a default value from the axis parameters.
Deceleration
LREAL
[mm/s2] The required deceleration in actual value units of the axis per square second. If this parameter is 0.0, it is replaced by a default value from the axis parameters.
Jerk
LREAL
[mm/s3] The required jerk in actual value units of the axis per square second. If this parameter is 0.0, it is replaced by a default value from the axis parameters.
SetPosition
LREAL
Required position on the referencing cam.
LREAL
[mm/s] Velocity limit to reliably detect a stop
LREAL
[s] Time in which the actual velocity must be below the DetectionVelocityLimit in order to reliably detect the fixed stop.
TorqueLimit
LREAL
[Bar] Limitation for the pressure
TorqueTolerance
LREAL
[Bar] Tolerance for the pressure
TimeLimit
TIME
After this time, the referencing is canceled with error. At zero, time monitoring is disabled.
DistanceLimit
LREAL
After this distance, the referencing will be aborted with an error. At zero, the distance monitoring is disabled.
BufferMode
reserved
MC_StepBlock_BkPlcMc 3: Inputs/outputs
    Axis:               AXIS_REF_BkPlcMc;
Type
Axis
AXIS_REF_BkPlcMc
Here, the address of a variable of type AXIS_REF_BkPlcMc should be transferred.
MC_StepBlock_BkPlcMc 4: Outputs
    Done:               BOOL;
    Busy:               BOOL;
    Active:             BOOL;
    CommandAborted:     BOOL;
    Error:              BOOL;
    ErrorID:            UDINT;
Type
Done
Successful processing is indicated here
Busy
Indicates that a command is being processed.
Active
Readiness for operation is indicated here.
CommandAborted
Here an abort of the command is indicated.
Error
The occurrence of an error is indicated here.
ErrorID
UDINT
An encoded error message is provided here.
On a rising edge at Execute all parameters are transferred to the function block MC_StepBlockDetection_BkPlcMc. If the internal function block MC_StepBlockDetection_BkPlcMc is successfully processed, the determined position is set accordingly via MC_SetPosition_BkPlcMc.
During processing, the function block reports Busy and Active. After successful position setting, Done is reported back. If a subordinate function block reports an error, this is reported via Error and ErrorID.