MC_WriteParameter
MC_WriteParameter 1:
This function block writes a numeric (LREAL) parameter value to the axis.
The command is typically processed synchronously.
Definition:
FUNCTION_BLOCK MC_WriteParameter
    Axis        : Type_PtpReadWriteParameter;
    Execute     : BOOL;
    ParameterId : EAxisParameterId;
    Value       : LREAL;
    Done        : BOOL;
    Busy        : BOOL;
    Error       : BOOL;
    ErrorId     : UDINT;
MC_WriteParameter 2: Inputs
Type
Default
Axis
Reference to the axis
Execute
Triggers the command on a rising edge.
ParameterId
EAxisParameterId
Invalid
Identifier of the parameter to write.
Value
LREAL
Value of the parameter to write.
MC_WriteParameter 3: Outputs
Type
Done
Parameter value has been successfully written.
Busy
Function block is not finished and new output values are to be expected.
Error
Error occurred within function block.
ErrorId
UDINT
Error identifier
Possible error codes
For this function block, the following values, among others, are possible for the ErrorId output:
Error(Hex)
Error(Dec)
Error type
0x8145
33093
Function Block
Mapping of cyclic interface between NC and PLC is missing (e.g., AXIS_REF, AXES_GROUP_REF, ...). A reference used by the function block (e.g., to an axis, group, mover or other motion object) is not linked to the corresponding NC object, or its cyclic mapping is incomplete.
0x8189
33161
Function Block
Invalid reference passed to function block. An invalid reference (or pointer) was used in a function block call. This can happen if a reference type is used before it was initialized.
0x81b1
33201
Function Block
Invalid size passed to function block (e.g., invalid array size or invalid number of elements). An invalid size was passed to the function block (e.g., CamRef.NumberOfPoints less than two on MC_CamTableSelect).
An overview of all NC error codes can be found here:
In conjunction with the hardware, the ADS return code ADSERR_DEVICE_BUSY (0x708; 1800) may also occur if the device is busy.
You can find an overview of all ADS return codes here:
Version information
  • TwinCAT Standard >= v3.1.4026.23.1
  • TF5500 MC3 Base >= v4.0.6