MC_Stop
This function block commands a motion stop and transfers the axis to the state Stopping. It aborts any ongoing function block execution. While the axis is in state Stopping, no other function block can perform any motion on the same axis. The Done output is set immediately after zero dynamics is reached. The axis remains in the state Stopping as long as Execute is TRUE or zero dynamics is not yet reached. As soon as Done is SET TRUE and Execute is FALSE the axis goes to state Standstill.
Definition:
FUNCTION_BLOCK MC_Stop
Axis : Reference To AXIS_REF;
Execute : BOOL;
Deceleration : LREAL;
Jerk : LREAL;
CommandHandle : Reference To MC_CommandHandle;
Done : BOOL;
Busy : BOOL;
Active : BOOL;
CommandAborted : BOOL;
Error : BOOL;
ErrorId : UDINT;
Name | Type | Default | Description |
Execute | BOOL |
| Triggers the command on a rising edge. While Execute is TRUE, other function blocks are rejected for the axis. |
Deceleration | LREAL | #Default | Maximum deceleration ([PosUnit]/s^2, positive) |
Jerk | LREAL | #Default | Maximum jerk ([PosUnit]/s^3, positive) |
CommandHandle | Reference To MC_CommandHandle |
| Optional. On a rising edge of Execute the handle is cleared and then attached to the command sent. Each call also updates the outputs of the handle. Like any input, it keeps the handle last passed, which must stay valid as long as the function block is called. |
Outputs
Name | Type | Description |
Done | BOOL | Zero dynamics reached. |
Busy | BOOL | Function block is not finished and new output values are to be expected. |
Active | BOOL | Function block has active control on the axis. |
CommandAborted | BOOL | Command is aborted by another command. |
Error | BOOL | Error occurred within function block. |
ErrorId | UDINT | Error identifier |
Further information
The function block MC_Stop is used to stop an axis with a defined deceleration ramp and to lock the axis against other motion commands. Only when the axis is at a standstill (MC_Stop.Done = TRUE) and the input MC_Stop.Execute = FALSE is the axis unlocked for other motion commands.
For the braking ramp, the maximum values of deceleration and jerk from the previous command and those specified in the function block are used.
Alternatively, an axis can be stopped with MC_Halt without locking.
If MC_Stop is applied to a coupled slave axis, the axis is automatically decoupled, and the stop command is then executed.
Effects on the axis state
The MC_Stop function block can be called in any motion state of the axis. This sets the axis to the Stopping state. In addition to bringing the axis to a stop using a defined braking ramp, the Stopping state locks the axis against other motion commands. Therefore, it is also possible to call MC_Stop while in the Standstill state to lock the axis. Only when the axis is no longer moving and the input MC_Stop.Execute = FALSE is the axis set to the Standstill state, thereby releasing the axis lock.
Note on the migration from NC2 to MC3
In MC3, the parameterization of the dynamics is not possible with a value of 0 (implicit use of the last commanded dynamics).
Possible error codes
For this function block, the following values, among others, are possible for the ErrorId output:
Error(Hex) | Error(Dec) | Error type | Description |
0x8145 | 33093 | Function Block | Mapping of cyclic interface between NC and PLC is missing (e.g., AXIS_REF, AXES_GROUP_REF, ...). A reference used by the function block (e.g., to an axis, group, mover or other motion object) is not linked to the corresponding NC object, or its cyclic mapping is incomplete. |
0x81aa | 33194 | Parameter | Invalid deceleration value. The supplied deceleration value is invalid (e.g. not a finite number, negative or outside the permitted range). |
0x81ab | 33195 | Parameter | Invalid jerk value. The jerk value used for the motion is invalid (e.g., negative, zero, or outside the permitted range of the mover or axis). |
An overview of all NC error codes can be found here:
Version information
- TwinCAT Standard >= v3.1.4026.23.1
- TF5500 MC3 Base >= v4.0.6