MC_SetPosition
MC_SetPosition 1:
This function block shifts the coordinate system of an axis by manipulating both the setpoint position as well as the actual position of an axis with the same value without any movement caused (Re-calibration with same following error). This can be used for instance for a reference situation.
Definition:
FUNCTION_BLOCK MC_SetPosition
    Axis             : Type_PtpSetPosition;
    Execute          : BOOL;
    Position         : LREAL;
    Relative         : BOOL;
    ClearPositionLag : BOOL;
    Done             : BOOL;
    Busy             : BOOL;
    Error            : BOOL;
    ErrorId          : UDINT;
MC_SetPosition 2: Inputs
Type
Default
Axis
Type_PtpSetPosition
Reference to the axis
Execute
Triggers the command on a rising edge.
Position
LREAL
#Invalid
New position value ([PosUnit]) or distance if Relative = TRUE
Relative
false
Shift axis position by value
ClearPositionLag
Resets position lag to zero.
MC_SetPosition 3: Outputs
Type
Done
Position set.
Busy
Function block is not finished and new output values are to be expected.
Error
Error occurred within function block.
ErrorId
UDINT
Error identifier
Further information
The MC_SetPosition function block sets the current axis position to a parameterizable value. To do this, the axis must be at a standstill.
In the default case (input Relative = FALSE), the actual position is set to the parameterized absolute value of input Position. In the relative case (input Relative = TRUE), the actual position is offset by the value of the Position input. In both cases, the target position of the axis is set so that any potential position lag is retained. If the position lag is to be cleared, this can be done via the Options.ClearPositionLag input.
Note on the migration from NC2 to MC3
The Relative input corresponds to the Mode input of the Tc2_MC2.MC_SetPosition function block.
Possible error codes
For this function block, the following values, among others, are possible for the ErrorId output:
Error(Hex)
Error(Dec)
Error type
0x8145
33093
Function Block
Mapping of cyclic interface between NC and PLC is missing (e.g., AXIS_REF, AXES_GROUP_REF, ...). A reference used by the function block (e.g., to an axis, group, mover or other motion object) is not linked to the corresponding NC object, or its cyclic mapping is incomplete.
0x8148
33096
Function Block
Invalid input value. At least one input of the function block is outside its allowed range or inconsistent with the other inputs.
0x8151
33105
State
Command is not allowed in current axis state. If the axis has no controller enable, is in error or has been added to a group, some commands are not permitted.
0x8182
33154
Monitoring
Software position limit violation. Software position limits of at least one axis have been or would have been violated by a command.
0x8196
33174
Initialization
Invalid position or distance. The actual or specified position or distance could not be determined or is invalid.
0x818c
33164
Parameter
Position is out of modulo range. Position must be larger or equal to zero and less or equal to the modulus when using modulo positioning. When using modulo positioning, the target position is interpreted in consideration of the AdditionalTurns variable at the Options input.
An overview of all NC error codes can be found here:
Version information
  • TwinCAT Standard >= v3.1.4026.23.1
  • TF5500 MC3 Base >= v4.0.6