MC_SetHomingState
MC_SetHomingState 1:
This function block sets or resets the homing state (IsPositionValid) of the axis. Optionally, the position is set as well. No movement is caused.
Definition:
FUNCTION_BLOCK MC_SetHomingState
    Axis           : Type_PtpSetHomingState;
    Execute        : BOOL;
    Position       : LREAL;
    Mode           : EHomingMode;
    Done           : BOOL;
    Busy           : BOOL;
    Active         : BOOL;
    CommandAborted : BOOL;
    Error          : BOOL;
    ErrorId        : UDINT;
MC_SetHomingState 2: Inputs
Type
Default
Axis
Reference to the axis
Execute
Triggers the command on a rising edge.
Position
LREAL
#Invalid
New position value ([PosUnit])
Mode
EHomingMode
ForceIsHomed
Homing mode selection
MC_SetHomingState 3: Outputs
Type
Done
Homing state set.
Busy
Function block is not finished and new output values are to be expected.
Active
Function block has active control on the axis.
CommandAborted
Command is aborted by another command.
Error
Error occurred within function block.
ErrorId
UDINT
Error identifier
Possible error codes
For this function block, the following values, among others, are possible for the ErrorId output:
Error(Hex)
Error(Dec)
Error type
0x8145
33093
Function Block
Mapping of cyclic interface between NC and PLC is missing (e.g., AXIS_REF, AXES_GROUP_REF, ...). A reference used by the function block (e.g., to an axis, group, mover or other motion object) is not linked to the corresponding NC object, or its cyclic mapping is incomplete.
0x8151
33105
State
Command is not allowed in current axis state. If the axis has no controller enable, is in error or has been added to a group, some commands are not permitted.
0x81b8
33208
Parameter
No cam event was detected during homing. The axis did not detect the reference cam within the expected travel during homing.
0x81b9
33209
Parameter
No sync event was detected during homing. No sync event (e.g., encoder zero pulse) was detected during homing.
An overview of all NC error codes can be found here:
Version information
  • TwinCAT Standard >= v3.1.4026.23.1
  • TF5500 MC3 Base >= v4.0.6