MC_Power
MC_Power 1:
This function block controls the power stage (on or off).
Definition:
FUNCTION_BLOCK MC_Power
    Axis           : Reference To AXIS_REF;
    Enable         : BOOL;
    EnablePositive : BOOL;
    EnableNegative : BOOL;
    Status         : BOOL;
    Error          : BOOL;
    ErrorId        : UDINT;
MC_Power 2: Inputs
Type
Default
Enable
General software enable for the axis
EnablePositive
false
Feed enable in positive direction. Only effective if Enable = TRUE.
EnableNegative
false
Feed enable in negative direction. Only effective if Enable = TRUE.
MC_Power 3: In/Outputs
Type
Axis
Reference to the axis
MC_Power 4: Outputs
Type
Status
Axis is ready for motion commands.
Error
Error occurred within function block or axis already signaling an error.
ErrorId
UDINT
Error identifier of function block or axis
Further information
The MC_Power function block is used to enable an axis in the software. The enable can be applied to both directions or only to a specific direction. A TRUE at the Status output indicates that the axis is ready for operation.
Depending on the drive type, Status also indicates that the drive is ready for operation. Digital drives provide feedback on operational readiness, while analog drives are unable to indicate their operational readiness. In the latter case Status only indicated operational readiness of the control side.
MC_Power 5:
Hardware enable signal
In addition to software enable it may be necessary to activate a hardware enable signal in order to enable a drive. This signal is not influenced by MC_Power and must be activated separately by the PLC.
Effects on the axis state
MC_Power.Enable affects the axis state as follows:
MC_Power 6:
Note on the migration from NC2 to MC3
For MC3 axes, the override is set to 100% by default. The MC_SetOverride function block is available for setting the override.
Possible error codes
For this function block, the following values, among others, are possible for the ErrorId output:
Error(Hex)
Error(Dec)
Error type
0x8145
33093
Function Block
Mapping of cyclic interface between NC and PLC is missing (e.g., AXIS_REF, AXES_GROUP_REF, ...). A reference used by the function block (e.g., to an axis, group, mover or other motion object) is not linked to the corresponding NC object, or its cyclic mapping is incomplete.
0x8151
33105
State
Command is not allowed in current axis state. If the axis has no controller enable, is in error or has been added to a group, some commands are not permitted.
0x819d
33181
NC Programming
The Motion UI has sovereignty for the controller enable. The PLC has handed over the controller enable and feed enable to the Motion UI.
0x81a2
33186
Environment
I/O data for more than n consecutive MC cycles invalid. Hardware process data was invalid for several consecutive MC cycles (e.g. EtherCAT slave not in OP, WcState error).
An overview of all NC error codes can be found here:
Version information
  • TwinCAT Standard >= v3.1.4026.23.1
  • TF5500 MC3 Base >= v4.0.6