MC_Jog
MC_Jog 1:
This function block enables an axis to be moved via manual keys in different modes. The outputs are cleared once JogForward and JogBackward are both FALSE and the jog has finished.
Definition:
FUNCTION_BLOCK MC_Jog
    Axis           : Reference To AXIS_REF;
    JogForward     : BOOL;
    JogBackward    : BOOL;
    Mode           : EJogMode;
    Distance       : LREAL;
    Velocity       : LREAL;
    Acceleration   : LREAL;
    Deceleration   : LREAL;
    Jerk           : LREAL;
    Done           : BOOL;
    Busy           : BOOL;
    Active         : BOOL;
    CommandAborted : BOOL;
    Error          : BOOL;
    ErrorId        : UDINT;
MC_Jog 2: Inputs
Type
Default
JogForward
Starts a motion in positive direction on a rising edge if JogBackward is FALSE. The motion stops once JogForward and JogBackward are both FALSE, or after Distance in Inching mode.
JogBackward
Starts a motion in negative direction on a rising edge if JogForward is FALSE. The motion stops once JogForward and JogBackward are both FALSE, or after Distance in Inching mode.
Mode
EJogMode
StandardSlow
Determines the operation mode in which the manual function is executed.
Distance
LREAL
#Ignore
Distance for movements in mode Inching ([PosUnit], positive)
Velocity
LREAL
#Ignore
Jog velocity ([PosUnit]/s, positive). Required for Continuous and Inching modes; StandardSlow and StandardFast use axis defaults.
Acceleration
LREAL
#Default
Maximum acceleration ([PosUnit]/s^2, positive)
Deceleration
LREAL
#Default
Maximum deceleration ([PosUnit]/s^2, positive)
Jerk
LREAL
#Default
Maximum jerk ([PosUnit]/s^3, positive)
MC_Jog 3: In/Outputs
Type
Axis
Reference to the axis
MC_Jog 4: Outputs
Type
Done
Function block has succeeded.
Busy
Function block is not finished and new output values are to be expected.
Active
Function block has active control on the axis.
CommandAborted
Command is aborted by another command.
Error
Error occurred within function block.
ErrorId
UDINT
Error identifier
Further information
The operating mode of the MC_Jog function block is defined via the input Mode of type E_JogMode:
E_JogMode.StandardSlow
The axis moves as long as the signal at either the JogForward or JogBackward TRUE input is TRUE. The velocity specified by the Jog Velocity Slow axis parameter and the dynamics specified by the Acceleration, Deceleration, and Jerk inputs are used.
The Distance and Velocity function block inputs have no effect in this operating mode.
E_JogMode.StandardFast
The axis moves as long as the signal at either the JogForward or JogBackward TRUE input is TRUE. The velocity specified by the Jog Velocity Fast axis parameter and the dynamics specified by the Acceleration, Deceleration, and Jerk inputs are used.
E_JogMode.Continuous
The function block input Distance has no effect in this operating mode.
E_JogMode.Inching
The axis moves by the distance specified at the Distance input of the function block as soon as a rising edge is detected at the JogForward or JogBackward input.
Possible error codes
For this function block, the following values, among others, are possible for the ErrorId output:
Error(Hex)
Error(Dec)
Error type
0x8145
33093
Function Block
Mapping of cyclic interface between NC and PLC is missing (e.g., AXIS_REF, AXES_GROUP_REF, ...). A reference used by the function block (e.g., to an axis, group, mover or other motion object) is not linked to the corresponding NC object, or its cyclic mapping is incomplete.
0x8146
33094
Function Block
Invalid velocity value. The velocity was not set or the entered value is invalid.
0x8151
33105
State
Command is not allowed in current axis state. If the axis has no controller enable, is in error or has been added to a group, some commands are not permitted.
0x8196
33174
Initialization
Invalid position or distance. The actual or specified position or distance could not be determined or is invalid.
0x819a
33178
NC Programming
Direction-dependent feed enable is missing. The execution of this command is not possible because of a missing direction-dependent feed enable.
0x819b
33179
NC Programming
Controller enable is missing. The controller enable of the axis was withdrawn during a movement. The dynamics of the setpoint did not correspond to zero dynamics.
0x81a9
33193
Parameter
Invalid acceleration value. The supplied acceleration value is invalid (e.g. not a finite number, negative or outside the permitted range).
0x81aa
33194
Parameter
Invalid deceleration value. The supplied deceleration value is invalid (e.g. not a finite number, negative or outside the permitted range).
0x81ab
33195
Parameter
Invalid jerk value. The jerk value used for the motion is invalid (e.g., negative, zero, or outside the permitted range of the mover or axis).
An overview of all NC error codes can be found here:
Version information
  • TwinCAT Standard >= v3.1.4026.23.1
  • TF5500 MC3 Base >= v4.0.6