MC_HaltPhasing
This function block commands a phase shift stop in the master position of a synchronized slave axis. It is only valid for camming synchronization. The master axis is not aware of the phase shift.
Definition:
FUNCTION_BLOCK MC_HaltPhasing
Master : Type_Master1D;
Slave : Type_Phasing1D;
Execute : BOOL;
Deceleration : LREAL;
Jerk : LREAL;
Done : BOOL;
Busy : BOOL;
Active : BOOL;
CommandAborted : BOOL;
Error : BOOL;
ErrorId : UDINT;
Name | Type | Default | Description |
Master |
| Reference to the master axis | |
Slave |
| Reference to the slave axis | |
Execute | BOOL |
| Triggers the command on a rising edge. |
Deceleration | LREAL | #Invalid | Maximum deceleration ([PosUnit]/s^2, positive) |
Jerk | LREAL | #Invalid | Maximum jerk ([PosUnit]/s^3, positive) |
Outputs
Name | Type | Description |
Done | BOOL | Zero dynamics of the phase shift reached. |
Busy | BOOL | Function block is not finished and new output values are to be expected. |
Active | BOOL | Function block has active control on the axis. |
CommandAborted | BOOL | Command is aborted by another command. |
Error | BOOL | Error occurred within function block. |
ErrorId | UDINT | Error identifier |
Possible error codes
For this function block, the following values, among others, are possible for the ErrorId output:
Error(Hex) | Error(Dec) | Error type | Description |
0x8145 | 33093 | Function Block | Mapping of cyclic interface between NC and PLC is missing (e.g., AXIS_REF, AXES_GROUP_REF, ...). A reference used by the function block (e.g., to an axis, group, mover or other motion object) is not linked to the corresponding NC object, or its cyclic mapping is incomplete. |
0x8151 | 33105 | State | Command is not allowed in current axis state. If the axis has no controller enable, is in error or has been added to a group, some commands are not permitted. |
0x81aa | 33194 | Parameter | Invalid deceleration value. The supplied deceleration value is invalid (e.g. not a finite number, negative or outside the permitted range). |
0x81ab | 33195 | Parameter | Invalid jerk value. The jerk value used for the motion is invalid (e.g., negative, zero, or outside the permitted range of the mover or axis). |
An overview of all NC error codes can be found here:
Version information
- TwinCAT Standard >= v3.1.4026.23.1
- TF5500 MC3 Base >= v4.0.6
