Init Parameter tab
General
Name | Default value | Unit | Type | |
Simulation Mode | TRUE |
| BOOL | |
Position Unit | mm | [PosUnit] | ||
Is Modulo Axis | FALSE |
| BOOL | |
| Position Modulus | 360.0 | [PosUnit] | LREAL |
| Position Modulo Tolerance Window | 0.0 | [PosUnit] | LREAL |
Simulation Mode
The Simulation Mode indicates whether the I/O connection to the drive and encoder should be active (FALSE) or simulated (TRUE). The parameter can be written at runtime if the axis is not enabled by the controller.
Position Unit
The Position Unit field is used for display purposes, such as on the commissioning interface. Inputs and outputs on function blocks are not converted.
Is Modulo Axis
Enable this parameter to use modulo functionality in function blocks for this axis. The setpoint and actual values are calculated as absolute and modulo values in the cyclic interface. To exchange Modulo information - for example, with the PLC - you must enable the Modulo data area .
- Position Modulus
Modulo value used to calculate the modulo position - Position Modulo Tolerance Window
Movement in the opposite direction to the specified direction is permitted, provided that the target position lies within this position tolerance of the command’s starting position. This parameter affects the behavior of MC_MoveModulo. It interacts with the setting selected at theDirectioninput of the function block.
Maximum Dynamics
Maximum Velocity | 2000.0 | [PosUnit]/s | LREAL |
Maximum Acceleration | 10000.0 | [PosUnit]/s2 | LREAL |
Maximum Deceleration | 10000.0 | [PosUnit]/s2 | LREAL |
Maximum Jerk | 100000.0 | [PosUnit]/s3 | LREAL |
Maximum Velocity
Maximum velocity taken into account during profile generation. Input values for function blocks are automatically reduced to this limit if values that are too high are specified. If the constant #Maximum is specified at the Velocity input of a function block, the value defined here is used as the limit value for the velocity.
Maximum acceleration taken into account during profile generation. Input values for function blocks are automatically reduced to this limit if values that are too high are specified. If the constant #Maximum is specified at the Acceleration input of a function block, the value defined here is used as the limit value for acceleration.
Maximum delay taken into account during profile generation. Input values for function blocks are automatically reduced to this limit if values that are too high are specified. If the constant #Maximum is specified at the Deceleration input of a function block, the value defined here is used as the limit value for the delay.
Maximum Jerk
Maximum jerk taken into account during profile generation. Input values for function blocks are automatically reduced to this limit if values that are too high are specified. If the constant #Maximum is specified at the Jerk input of a function block, the value defined here is used as the limit value for jerk.
Default Dynamics
Default Velocity | 1000.0 | [PosUnit]/s | LREAL |
Default Acceleration | 2000.0 | [PosUnit]/s2 | LREAL |
Default Deceleration | 2000.0 | [PosUnit]/s2 | LREAL |
Default Jerk | 4000.0 | [PosUnit]/s3 | LREAL |
Default Velocity
This value is used as the velocity limit for the input parameter Velocity of the function blocks, unless the value has been explicitly specified. If the constant #Default is specified at the input of a function block, the value defined here is used as the limit value for the velocity. This parameter is available from software version 4.0.24.
This value is used as the acceleration at the Acceleration input on function blocks, unless it is explicitly set. If the constant #Default is specified at the input of a function block, the value defined here is used as the limit value for acceleration.
This value is used as the delay at the Deceleration input on function blocks, unless it is explicitly set. If the constant #Default is specified at the input of a function block, the value defined here is used as the limit value for the delay.
Default Jerk
This value is used as jerk at the Jerk input on function blocks, unless it is explicitly set. If the constant #Default is specified at the input of a function block, the value defined here is used as the limit value for jerk.
Manual Motion
Jog Velocity Slow | 100.0 | [PosUnit]/s | LREAL |
Jog Velocity Fast | 250.0 | [PosUnit]/s | LREAL |
Jog Velocity Slow
This target velocity is used for slow movement of an axis using manual control buttons. This procedure can be performed using MC_Jog as well as through the commissioning interface.
Jog Velocity Fast
This target velocity is used for rapid movement of an axis using manual control buttons. This procedure can be performed using MC_Jog as well as through the commissioning interface.
Monitoring
Position Limit Enforcement Enabled | FALSE |
| BOOL | |
| Minimum Position | #Ignore | [PosUnit] | LREAL |
| Maximum Position | #Ignore | [PosUnit] | LREAL |
Position Lag Monitoring Enabled | TRUE |
| BOOL | |
| Maximum Position Lag Value | 5.0 | [PosUnit] | LREAL |
| Maximum Position Lag Filter Time | 0.02 | s | LREAL |
Position Lag Calculation | HardwareProvidedIfAvailable |
This parameter specifies whether position limits are taken into account when generating motion profiles. If the value is TRUE, the following two parameters must be set.
- Minimum Position
The minimum allowed position for the axis. Use#Ignoreto disable enforcement of the position limit in this direction of motion. It is not possible to move an axis beyond this limit. If an axis is outside its position limits when TwinCAT starts up, it can move toward the valid position range. Commands with a target position outside this lower limit will be rejected. - Maximum Position
The maximum allowable position for the axis. Use#Ignoreto disable enforcement of the position limit in this direction of motion. It is not possible to move the axis beyond this limit. If an axis is outside its position limits when TwinCAT starts up, it can move toward the valid position range. Commands with a target position outside this lower limit will be rejected.
This parameter specifies whether the position lag for the axis should be monitored. If the value is TRUE, the following two parameters are displayed for configuring position and time. If the parameterized limits are exceeded, a runtime error is output.
The calculation is performed as follows:
Position lag value = current target position - actual position
- Maximum Position Lag Value and Maximum Position Lag Filter Time
Maximum Position Lag Valueis the position lag value, which must not be exceeded for longer than the specified time (Maximum Position Lag Filter Time)). Otherwise, the axis is stopped immediately by direct shutdown, and an error is generated.
This parameter specifies whether the position lag is calculated by the software from the MC axis (InternallyCalculated) or read directly from the linked hardware (HardwareProvidedIfAvailable). If HardwareProvidedIfAvailable is set but no hardware is available, the system falls back to the internally calculated value. For a simulation axis, HardwareProvidedIfAvailable uses data from the simulation drive.
Error event handling
Control Error Setpoint Mode | HardStop |
If there is a hardware error (e.g., in the control loop) and the MC no longer has control over the axis, you can configure the behavior of setpoint generation here. HardStop causes the axis to stop abruptly in the event of a fault.
Diagnostics
TraceLevel | tlWarning |
| TcTraceLevel |
Specify which messages should be sent to the TwinCAT error list.
Additional Encoder
Main Position Encoder |
| OTCID_PositionEncoder |
Load Control Type | None |
If an additional encoder is available, select its object ID here.
Load Control Type
Set the type of load to be controlled here.