Limits and options of the motion commands
The Planar mover can execute different types of motion commands. Except for the special case of external setpoint generation, these are similar in structure. The following applies to the rest of the motion commands. The first parameter of the method call is always the feedback for the command that the user transfers. If the user transfers a “0”, this implies that he does not want to have (or use) feedback. The next one or two parameters describe the destination of the motion and they cannot be completely omitted. The next parameters are the dynamic limits that should be observed during motion. If the user transfers a “0” here, the default values are used (TCOM parameters of the mover in the MC Project). The last parameter is the option object, which differs depending on the command.
From version V3.4.45: Optional method parameters (e.g. feedback, dynamic limits, options) have default values ("0") in the PLC API and can be omitted accordingly, see Example "Create Planar movers and move based on coordinates (MoveX, MoveY)" and Example "Create Planar movers with group and move based on coordinates (MoveX, MoveY)".
Limits
Each motion command is executed in the optimal time. For the resulting trajectory to be continuous, the time derivatives of the position must be limited. The limits include maximum values for the velocity, positive and negative acceleration, and jerk. If the values specified here exceed the maximum dynamic limits of the mover (TCOM parameters of the mover in the MC Project), they are reduced accordingly, a warning is issued and the command is executed with reduced dynamic values. There is only one Limit or Constraint object. This is understood to be a limitation of the dynamics tangential to the direction of movement of the mover.
For external setpoint generation, the only parameters are Feedback and Options.
Options
The options vary depending on the command:
MoveToPosition/JoinTrack/LeaveTrack: The option of these commands is the “UseOrientation” flag. This flag indicates whether or not the C coordinate of the XYC target position should also be used. If not, the C coordinate can be moved separately via “MoveC”.
Starting with version V4.0.6: There are two new options: “AdditionalTurns” and “Direction”. These options allow you to specify the target position for the C coordinates using modulo notation. These options work exactly the same as the corresponding options of the MoveC command. For details, see Modulo positioning.
MoveOnTrack: The first option is the “Gap”. This numerical value specifies the minimum distance from the vehicle in front and the vehicle behind while the vehicle is moving (and thereafter until the next motion command on the track). This distance is measured along the track (difference between the track positions of the two movers). Therefore, curvatures in the track must be taken into account, as they reduce the real 2D distance. The gap is calculated from center to center, therefore additionally the width of the movers must be taken into account. The second option is “Direction”, the direction of travel on the track towards the destination. This can assume the values “NonModulo” (= absolute), “Positive” (= forward), “ShortestWay” (= shortest way) and “Negative” (= backward). If the destination is reachable in the appropriate direction, the command is executed.
The third option is “AdditionalTurns”: the number of additional laps driven on a “Closed Loop” track with “Positive” or “Negative” “Direction”. For other “Direction” cases, “AdditionalTurns” must be zero. The fourth option is “ModuloTolerance”. This parameter is used to avoid unintended rotations when the start and target positions are very similar. If the distance between the start and target position is less than or equal to the “ModuloTolerance”, the target position is approached by the shortest route (as with “Direction” = “Shortest Way”), i.e. against the specified “Direction”. For the “NonModulo” “Direction” the ModuloTolerance must be zero. For details, see Modulo positioning.
The sixth option is the "GapMode". This setting can be set to either “Standard1D” or “Fast1D”.
Starting with version V4.0.12: There are two new settings: “Standard2D” and “Fast2D.”
Standard1D: This is the default value and corresponds to the previous behavior. This mode generally results in the distance between two movers being greater than the minimum gap passed as the “Gap” option. The distance between two movers typically increases with greater velocity. This causes the mover chain to spread out during movement.
Notice
Damage due to possible collisions
Please note that changing the parameters during movement can cause damage under the following conditions.
Reducing one or more of the dynamic parameters A, D or J during the movement may result in the parameterized minimum "Gap" not being reached. However, in this mode, any increase in one or more of these parameters can be made without causing such an undershoot. Similarly, the dynamic parameter V can be changed in this mode without causing such an undershoot.
Fast1D: This mode aims to intervene in the motion profiles as late as possible without falling below the distance set as the “Gap” option. This typically results in smaller distances between neighboring movers during movement than in “Standard1D” mode. This allows mover chains to be moved more quickly.
Notice
Any changes (i.e. both increases and decreases) to one or more of the dynamic parameters A, D or J during movement can result in the parameterized minimum "Gap" being undershot. As in "Standard1D" mode, the dynamic parameter V can be changed as required in this mode without causing such an undershoot.
Standard2D: In this mode, the Euclidean distance between the mover geometries is generally greater than the minimum distance specified by the “Gap” option. Typically, the distance between two movers increases as their speed increases. This causes a chain of movers to fan out while moving.
Notice
Please note that changing the parameters while the robot is moving may cause damage under the following conditions.
Reducing one or more of the dynamic parameters A, D, or J while the robot is moving may result in the robot falling below the configured minimum distance (“Gap”). In contrast, increases to one or more of these parameters can be made arbitrarily in this mode without causing the distance to fall below the minimum “Gap” set in the parameters. Similarly, the dynamic parameter V can be changed arbitrarily in this mode without causing the distance to fall below the minimum “Gap”.
Fast2D: This mode aims to intervene in the motion profiles as late as possible without falling below the distance between the mover geometries set as the “Gap” option. This typically results in smaller distances between adjacent movers during operation than in “Standard2D” mode. As a result, mover chains can move more quickly.
Notice
Damage caused by potential runtime errors - Check the cycle time of your application’s MET task with the maximum number of movers
This mode is computationally intensive and can lead to cycle time violations when many movers are used simultaneously or when cycle times are short. In such cases, tracking errors may occur.
Take the following measures to avoid potential runtime errors and resulting tracking errors:
  • Increase the cycle time. The complexity of the calculation increases linearly with the number of movers, the number of tracks, and the length of the braking ramps.
  • The CPU used and its clock speed are also relevant.
Notice
In this mode, the distance between the geometries is numerically approximated. This can result in distances between the mover geometries that are either smaller or larger than those set in the command. If this is not acceptable, the “Standard2D” mode should be used.
Note that changing the parameters while the system is in motion can cause damage under the following conditions.
Any change (i.e., both increases and decreases) to one or more of the dynamic parameters A, D, or J during motion may result in the distance falling below the parameterized minimum distance (“Gap”). As in “Standard1D” mode, the dynamic parameter V can be changed arbitrarily in this mode without causing the distance to fall below the minimum.
The fifth option is the "DynamicsReductionMode". This function can be used to automatically adjust the dynamic behavior of a mover along a track, for example to limit radial acceleration in curves. This setting has two possible values: "None" and "AccelerationLimitedVelocity".
None: This is the default value and corresponds to the previous behavior. In this mode, the mover is not subject to any additional restrictions of dynamics due to external conditions. The mover moves according to the parameters defined for it, without any additional adjustments.
AccelerationLimitedVelocity: This new mode ensures that the maximum allowed radial acceleration in curves is not exceeded. This is achieved by reducing the mover's tangential velocity in accordance with the track's current curve radius. The limits in the X and Y directions of the mover must be set to the same values. An error is output if the limits are set differently and as soon as a movement is started on a track. An example can be found under Coupling a Planar mover to a track and moving it with DynamicsReductionMode.
Limits and options of the motion commands 1:
Higher total acceleration possible
Only the radial acceleration is reduced. The total acceleration can still be higher, for example if the mover also accelerates tangentially in a curve.
MoveC: The first option is “AdditionalTurns”: the number of additional whole C-turns related to the “C coordinate modulus” parameter of the mover with “Positive” or “Negative” “Direction”. For other “Direction” cases, “AdditionalTurns” must be zero. The second option is “Direction”: the direction of rotation of the C coordinate towards the target. This can assume the values “NonModulo” (= absolute), “Positive” (= forward), “ShortestWay” (= shortest way) and “Negative” (= backward). For details, see Modulo positioning.
AdoptTrackOrientation: The first option is “AdditionalTurns”: The number of additional whole C-turns related to the “C coordinate modulus” parameter of the mover with “Positive” or “Negative” “Direction”. For other “Direction” cases, “AdditionalTurns” must be zero. The second option is “Direction”: the direction of rotation of the C coordinate towards the target. This can assume the values “NonModulo” (= absolute), “Positive” (= forward), “ShortestWay” (= shortest way) and “Negative” (= backward). For details, see Modulo positioning.
GearInPosOnTrack: The first option is the “Gap”, which has the same interpretation here as with MoveOnTrack. The second parameter is the “InSyncToleranceDistance”. It specifies how far the master and slave may move away from each other before the active Planar mover loses its synchronicity. The following two options are “Direction” and “ModuloTolerance”, which both refer to the “SlaveSyncPosition” parameter (as input at the function call). These options are only available if the Planar track that the Planar mover performs its synchronization movement on is a closed loop. In this case, the interpretation of these options is analogous to that for MoveC, where here the modulus is given by the length of the Planar track. For details, see Modulo positioning. The last “AllowedSlaveSyncDirections” parameter specifies in which direction, i.e. positive (default), negative or both, the Planar mover is allowed to move during the synchronization phase. This parameter can be used, for example, to prevent a back oscillation, which would occur with the option “Both”, in order to achieve the fastest possible synchronization. If the Planar mover is in sync, or has been in sync, and is currently trying to get back in sync, this parameter has no further effect.
GearInPosOnTrackWithMasterMover: The first four options, “Gap”, “InSyncToleranceDistance”, as well as the two modulo options for the SlaveSyncPosition, are identical to the first four options of the GearInPosOnTrack command in terms of their meaning. This is followed by two “Direction” and “ModuloTolerance” parameters for the MasterSyncPosition, which are available in the same way as the modulo parameters for the SlaveSyncPosition when the Master Planar mover is on a closed-loop track. The following option “AllowedSlaveSyncDirections” has exactly the same function as the GearInPosOnTrack command. If the last option, “FollowMover”, is set, it ensures that the Slave Planar Mover does not need to obtain a Planar TrackTrail to determine which Planar tracks it will move over. The Slave Planar Mover will simply follow the Master Planar mover as it moves through the network. When the motion command is received and the "FollowMover" option is set, and the Master Planar mover and the Slave Planar mover are on different Planar tracks, the Slave Planar mover will try to reach the Planar track that the MasterSyncPosition is on by the shortest route. In addition to the “FollowMover” option, a Planar TrackTrail can be specified for the Slave Planar Mover. In this case, it is used to command the path to the Planar track that the MasterSyncPosition lies on (e.g. if it is to deviate from the shortest path). If it does not fully reach this Planar track, the remaining path is filled with the shortest route. If a Planar TrackTrail is specified when the “FollowMover” option is set, the SlaveSyncPosition can be specified on a different Planar track than its initial one. In general, the following rule applies: if the “FollowMover” option is set, the Slave Planar Mover follows the master from the Planar track that the MasterSyncPosition is located on, regardless of whether a Planar TrackTrail object has been specified.
StartExternalSetpointGeneration: Here the user can choose between "Absolute" and "Relative" mode. In absolute mode, the mover follows only the external setpoints specified by the user and is in ExternalSetpointGeneration command mode; otherwise, the mover is in any other command mode and adds the user's external setpoints as an offset to its current setpoint.