Start-up parameters
P-STUP-00033
Memory size for backward motion
This parameter defines the memory size in bytes used for backward motion on the path. During start-up, the NC checks whether the required minimum size is available. If this is not the case, a warning is output and the memory size is set to the required minimum value. If the size is set to 0, the “forward/ backward motion on the path” function is not available. The maximum size is only limited by the resources available on the PC.
Parameter
fb_storage_size[i] where i = 0 to 11
(maximum number of channels: 12, application-specific)
Data type
UNS32
Data range
0 ... MAX(UNS32)
Dimension
Default value
0
Remarks
Channel parameters
P-CHAN-00650
Definition of interpolator functionalities
This parameter defines individual functionalities and the size of the look-ahead buffer in the interpolator, i.e. it defines the number of blocks required to calculate deceleration distance and dynamic planning.
Parameter
configuration.interpolator.function
Data type
STRING
Data range
See Description
Dimension
Default value
FCT_IPO_DEFAULT
Remarks
Interpolation function table
Identifier
FCT_IPO_DEFAULT
FCT_LOOK_AHEAD_STANDARD
FCT_LOOK_AHEAD_LOW
30 blocks
120 blocks
FCT_LOOK_AHEAD_HIGH
190 blocks
FCT_LOOK_AHEAD_CUSTOM
Number of look-ahead blocks in the interval [ 10; P-CHAN-00653].
FCT_SYNC
Synchronising an axis in coordinated motion
Example: FCT_IPO_DEFAULT | FCT_SYNC
FCT_LOOK_AHEAD_OPT
The path velocity curve can be further improved for HSC machining by additional calculations. This generally reduces machining time. The additional calculations place greater demands on the controller hardware.
FCT_LIFT_UP_TIME
Automatic lifting/lowering of an axis (time-based coupling).
Example: FCT_IPO_DEFAULT | FCT_LIFT_UP_TIME
FCT_SHIFT_NCBL
Path-controlled offset of M functions (dwell time).
Example: FCT_IPO_DEFAULT | FCT_SHIFT_NCBL
FCT_CALC_STATE_AT_T
Calculation of path velocity at a time in the future. Function only available in combination with HSC slope and only as of V3.1.3057.0
| FCT_CALC_STATE_AT_T
FCT_CALC_TIME
Calculation of interpolation time to next feed block (G01,G02,G03).
Example: FCT_IPO_DEFAULT | FCT_CALC_TIME
FCT_CONTOUR_LAH
Contour look-ahead: advance output of motion blocks to the PLC
as of V3.1.3104.07
FCT_DYN_POS_LIMIT
Dynamic limitation of axis positions
FCT_EXTENSION_EQUIDIST
Die-sinking EDM Orbiting
FCT_CALC_POS_V_0
Calculating and supplying the braking distance on the path until velocity and acceleration are 0. Supplying CNC objects on the path and assigned PCS and ACS axis positions at the end of this deceleration process.
as of V3.01.3081.7 or V3.1.3114.0
FCT_DLM
Activate the conveyor tracking function.
as of V4.20.0
The look-ahead buffer size values specified above apply as of CNC Builds V2.11.2800 and higher; the following settings apply to CNC Build V2.11.20xx:
FCT_LOOK_AHEAD_LOW
30 blocks
70 blocks
FCT_LOOK_AHEAD_HIGH
120 blocks
P-CHAN-00658
Maximum number of logged contour elements in the contour look-ahead.
This parameter can be used to set the maximum number of stored motion blocks that can be supplied to the PLC in advance.
The CNC command #CONTOUR LOOKAHEAD LOG [] can be used to activate the save function.
FCT_CONTOUR_LAH must be enabled in P-CHAN-00650 for this functionality.
configuration.interpolator.fct_enable[0]
FCT_IPO_DEFAULT|FCT_CONTOUR_LAH
Parameter
configuration.interpolator.contour_lookahead_log_max
Data type
UNS32
Data range
0 <= contour_lookahead_log_max < MAX_UNS32
Dimension
Default value
128
Remarks
Parameter available as of V3.1.3107.10
