Axis parameter
P-AXIS-00015
Axis mode
Axes can be traversed in different operating modes.
Parameter
kenngr.achs_mode
Data type
UNS32
Data range
0x00000001 - 0x10000000
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
0x00000001
Drive types
Remarks
The following operation modes can be parameterised(1):
Value
Meaning
Axis type
Interpolator type
ACHSMODE_
path
spindle
0x00000001
The axis is operated as a linear axis; no modulo calculation is executed in the channel. For example, rotary axis with restricted motion range; must be set as default for linear axes.
..LINEAR(1)
T, R
X
0x00000004
A modulo calculation always takes place after the destination position has been reached. Regardless of the operation mode selected for rotary axes, a modulo calculation is always executed in the position controller. In this way, modulo circle compensation can be executed if required.
..MODULO(1)
R
X
X
0x00000040
Axis is used as a face turning axis (turning functions).
..PLANDREHEN
T
X
0x00000080
Axis is used as a longitudinal turning axis (turning functions).
..LAENGSDREHEN
T
X
0x00000100
For a spindle an automatic homing before positioning the spindle can be pre-vented. This is only relevant if the axis is not referenced. The function is drive-dependent.
..KEINE_AUTO_RPF
R
X
0x00000200
Axis for kinematic 'C axis' transformation.
..CAX
R
X
X
0x00000400
Modulo calculation for linear axis. (Example: conveyor belt with drive motor where the position on the belt is programmed in mm).
..MODULO_LINEAR
R
X
0x00000800
Axis is released for mechanical blocking by the PLC.
This axis mode is not available for TwinCAT systems.
..CLAMPABLE
T, R
X
0x00001000
Axis carries a rotary workpiece table.
..ROT_TABLE
T, R
X
0x00008000
Monitoring of axis collision.
..COLL_CHECK
T
X
0x00010000
Master axis of gantry coupling.
..GANTRY_MASTER
T, R
X
0x00020000
Slave axis of gantry coupling.
..GANTRY_SLAVE
T, R
X
0x00040000
Identifier for PLC spindle with axis interface
..SPINDLE_EXT_CTRL
R
X
0x00080000
Input axis for additional external position command values (e.g. distance control).
..EXT_CTRL_INPUT
T
X
0x00100000
Pure encoder axis, only to display actual values (e.g. conveyor belt).
..COUNTER
T, R
X
X
0x00200000
Lead axis in combination with single feed axis and G194 (contouring with DIST_MASTER)
..LEAD_AXIS
T, R
X
0x00400000
The resolution (wegaufz/wegaufn) of this axis can be changed.
..ALLOW_RESOLUTION_
CHANGE(2)
T, R
X
X
0x00800000
Path-dependent dynamic weighting for this axis is possible.
..DYNAMIC_WEIGHTING
T, R
X
0x02000000
Path axis for tool centre point path
..PATH_LENGTH_TCP
R
X
0x04000000
Path axis for contour path
..PATH_LENGTH_
CONTOUR
R
X
0x08000000
Virtual lead axis for path interpolation
..VIRT_LEAD_AXIS
R
X
0x10000000
Axis carries the pressure roller for edge banding.
..LAH_OFFSET_AXIS
R
X
(1) One of the following two axis modes must always be defined:
- ACHSMODE_LINEAR or
- ACHSMODE_MODULO
All other bits of the parameter achs_mode are additional specifications. For example, the ACHSMODE_MODULO_LINEAR bit is only useful if combined with the ACHSMODE_MODULO bit.
(2) Changing certain axis parameters may be critical while a controller is running, e.g. path resolution,. Therefore, this parameter can be enabled by setting the bit ALLOW_RESOLUTION_CHANGE in axis mode. Otherwise, these parameters (P-AXIS-00234, P-AXIS-00233) can no longer be changed after controller start-up.
When the bit ALLOW_RESOLUTION_CHANGE is set, a check is first made whether the axis is interpolated, also when other critical parameters change. If the axis is currently in motion, this parameter update is rejected.
P-AXIS-00177
Negative software limit switch
The parameter defines the possible traverse range in the negative direction (negative software limit switch position). The programmed command positions are always checked on 'kenngr.swe_neg', the actual positions on 'kenngr.swe_neg - kenngr.swe_toleranz'.
Parameter
kenngr.swe_neg
Data type
REAL64
Data range
MIN(SGN64-1023) < swe_neg < P-AXIS-00178
Axis types
T, R
Dimension
T: 0.1µm
R: 0.0001 °
Default value
-100000000
Drive types
Remarks
The value of the parameter is adopted on reset, mode change and axis replacement from the axis record.
As of V3.1.3132.0 and/or V4.29.0, the data type is REAL64; in earlier versions SGN32. This also affects the related data range.
P-AXIS-00178
Positive software limit switch
The parameter defines the possible traverse range in the positive direction (positive software limit switch position). The programmed command positions are always checked on 'kenngr.swe_pos', the actual positions on 'kenngr.swe_pos + kenngr.swe_toleranz'.
Parameter
kenngr.swe_pos
Data type
REAL64
Data range
P-AXIS-00177 < swe_pos < MAX(SGN64-1023)
Axis types
T, R
Dimension
T: 0.1µm
R,S: 0.0001 °
Default value
100000000
Drive types
Remarks
P-AXIS-00555
Select method to monitor the workspace when using the conveyor tracking functionality.
This parameter influences the monitoring of the workspace when workpieces are machined on a linear conveyor.
With machines that have the conveyor tracking functionality, the tool should remain as close as possible to the end position defined in P-CHAN-00374 in order to utilise the workspace to the full extent. In the event of a movement in the opposite conveying direction, the controller brakes the tool accordingly to prevent the position from being exceeded.
When contour elements are fed through in the opposite conveying direction at a higher feed rate than the conveyor belt velocity, a check must be made whether the workspace is exited in the opposite conveyor belt direction. This requires a more complex check of the workspace and can be activated by this parameter.
Parameter
kenngr.conv_sync_optim
Data type
BOOLEAN
Data range
0: Simplified method with low computing time requirement. It is only suitable when the conveyor velocity is significantly higher than the programmed feed rate.
1: The programmed contour is checked for collision. In this method, the tool travels to the required end position if possible.
Axis types
T
Dimension
T: ----
Default value
0
Drive types
Remarks
Available as of CNC Build V4.20.0
P-AXIS-00620
Enable position actual value filter for the conveyor axis
This parameter enables and disables the filter for the position actual values of the conveyor axis.
Parameter
conv_sync.enable_filter
Data type
BOOLEAN
Data range
0: Position actual value filter off
1: Position actual value filter on
Axis types
T, R, S
Dimension
T: ----
R, S: ----
Default value
0
Drive types
Remarks
P-AXIS-00623
Order of the velocity actual value filter of the conveyor axis
This parameter defines the order (number of filtered values) of the velocity actual value filter of the conveyor axis. The filter is off in the case of order 0. An FIR low-pass filter is used automatically.
Parameter
conv_sync.order_v_filter
Data type
UNS32
Data range
0 ≤ order_v_filter ≤ 1000
Axis types
T, R, S
Dimension
T: ----
R, S: ----
Default value
20
Drive types
Remarks
P-AXIS-00624
Order of the downstream velocity actual value filter in the case of feedhold on the conveyor axis
This parameter defines the order (number of filtered values) of the downstream velocity actual value filter of a feedhold is defined on the conveyor axis. The filter is off in the case of order 0. An average value filter is used automatically.
Parameter
conv_sync.order_post_v_filter
Data type
UNS32
Data range
0 ≤ order_post_v_filter ≤ 1000
Axis types
T, R, S
Dimension
T: ----
R, S: ----
Default value
6
Drive types
Remarks
P-AXIS-00625
Order of the velocity actual value filter in the case of feedhold on the conveyor axis
This parameter defines the order (number of filtered values) of the velocity actual value filter if a feedhold is defined on the conveyor axis. The filter is off in the case of order 0. An FIR low-pass filter is used automatically.
Parameter
conv_sync.order_v_filter_dyn
Data type
UNS32
Data range
0 ≤ order_v_filter_dyn ≤ 1000
Axis types
T, R, S
Dimension
T: ----
R, S: ----
Default value
10
Drive types
Remarks
P-AXIS-00626
Delay time between the latch moment of the actual values and generating the command value
This parameter defines the delay time between the read-in actual value of the conveyor axis and the output command value of the machine axis. This delay time is used for feedforward control of the conveyor axis velocity.
Parameter
conv_sync.delay_time
Data type
UNS32
Data range
0 ≤ delay_time ≤ MAX(UNS32)
Axis types
T, R, S
Dimension
T: [µs]
R, S: [µs]
Default value
0
Drive types
Remarks
P-AXIS-00708
Definition of the conveyor axis
This parameter defines the axis representing the linear conveyor.
Parameter
conv_sync.is_master
Data type
BOOLEAN
Data range
0: Axis is not a conveyor axis
1: Axis is the conveyor axis
Axis types
T, R, S
Dimension
T: ----
R, S: ----
Default value
0
Drive types
Remarks