Vibration Guard mode
The smoothing curve and therefore the vibration-preventing effect are dependent on parameters and the Vibration Guard mode selected. Each mode has its own characteristic curve and effect.
The following modes are available when using Vibration Guard:
Modes 1 - 3
Mode 4:
Vibration Guard mode 1:
Sensitivity ranges for a residual vibration of 5% at damping=0.1
The figure above results in the following standard values for each of the modes regarding acceptable percentage deviations to obtain residual vibrations of below 5%:
Table of standard values for sensitivity
Permitted deviations for max. 5% residual vibration (at damping=0.1)
max. negative deviation
max. positive deviation
Mode 1:
-3%
+3%
Mode 2:
-13%
+19%
Mode 3:
-20%
+33%
Mode 4:
-10%
+13%
Standard values for permitted percentage deviations between the frequency setting and the real frequency to obtain a residual vibration of below 5% (at damping= 0.1).
Vibration Guard mode 2:
Comparison of Vibration Guard modes at corner contour (10 Hz and damping=0.1)
1
Vibration Guard Mode 1
2
Vibration Guard Mode 2
3
Vibration Guard Mode 3
4
Vibration Guard Mode 4
Example
Selecting the right Vibration Mode for an axis
Basic procedure:
  1. Measurements of machine frequencies at three points
  2. Calculation of percentage deviations
  3. Assessment of calculation results based on the above Table of standard value for sensitivity
Evaluation of results:
The deviations exceed the permitted range of Mode 1 (+/-3%) but are within of the permitted range of Mode 2 (-13%, +19%). The positive deviation for Mode 4 of +15% is greater than the permitted +13%.
So, in this example, Vibration Guard Mode 2 should be set to a frequency of 6 Hz.
A suitable programming command would then be: #VIB GUARD [FREQ=6 MODE=2]