P-AXIS-00750
Order of band-pass filter
This parameter defines the order of the band-pass filter for all modes (P-AXIS-00753).
In addition, this parameter is a value which expresses the fall of frequency response (fall = -order x 20 dB/decade).
Parameter
lr_param.improved_position_control.stage[i].filter.order
Data type
UNS32
Data range
1 <= order <= 3
Axis types
T, R, S
Dimension
T: —-
R, S: —-
Default value
0
Drive types
SERCOS, Profidrive, CANopen
Remarks
P-AXIS-00751
Frequency
This parameter defines a frequency that has a different impact on filter response depending on the filter type setting (P-AXIS-00849).
Filter type - Band-pass filter:
The parameter defines the frequency that is to be actively damped by the "Improved Position Control" function. The middle frequency is specified for all modes P-AXIS-00753. For the “INDIRECT” and SET_POINT modes, the simulation of the mechanical vibration is based on the same frequency.
Filter type - All-pass filter:
This parameter defines the frequency at which the greatest phase rotation occurs. In the case of the all-pass filter, the frequency can be varied slightly from the set frequency of the band-pass filter in order to adjust the phase of the additive speed.
Parameter
lr_param.improved_position_control.stage[i].filter[k].fg_f0
Data type
REAL64
Data range
0.0 < fg_f0 <= 500.0
Axis types
T, R, S
Dimension
T: Hz
R, S: Hz
Default value
-1
Drive types
Remarks
The "Improved Position Control" function achieves the best results when the dominant frequency of the mechanical vibration is precisely met. The measured frequency may deviate from the actual frequency due to measurement inaccuracies. In many cases, the performance of the function can be enhanced by varying the parameter fg_f0 within a narrow range.
Parameter available as of CNC Build V3.1.3077.08
P-AXIS-00752
Quality factor of the filter
Depending on the filter type selected (P-AXIS-00849), the quality factor has a different impact on filter response.
Specifies the inverse value of the bandwidth for the band-pass filter for all modes (P-AXIS-00753).
P-AXIS-00752 = P-AXIS-00751 / bandwidth
In the case of an all-pass filter, the quality factor determines the magnitude and narrowband nature of the phase shift about the centre frequency fg_f0. The higher the quality factor, the steeper and more concentrated the phase rotation.
Parameter
lr_param.improved_position_control.stage[i].filter[k].q_factor
Data type
REAL64
Data range
1.0 <= q_factor <= 10.0
Axis types
T, R, S
Dimension
T: —-
R, S: —-
Default value
-1
Drive types
Remarks
A high filter quality limits the bandwidth of the filtering frequencies. To avoid cutting off any relevant frequencies, it is advisable to raise the filter quality step by step. The filter quality is limited by changing the frequency dependent on machine position and mass inertia. Among other things, a higher filter quality leads to improved damping of the required frequency, whereas a lower quality results in a more robust behaviour of frequency damping.
P-AXIS-00753
Mode for the "Improved Position Control" function
The following modes are provided for the "Improved Position Control" function and they are applicable simultaneously to various stages.
  • NOT_ACTIVE: IPC is not active.
  • DIRECT: IPC uses direct measured values. Direct measured values can either come from a direct measuring system or originate from a motor encoder as the actual velocity.
  • INDIRECT: IPC uses values that are based on the simulation of the mechanical vibration by the measured actual motor velocity.
  • SET_POINT: IPC uses values that are based on the simulation of the mechanical vibration by the command velocity.
Parameter
lr_param.improved_position_control.stage[i].mode
Data type
UNS32
Data range
0 - NOT_ACTIVE
1 - DIRECT
2 - INDIRECT
3 - SET_POINT
Axis types
T, R, S
Dimension
T: —-
R, S: —-
Default value
0
Drive types
Remarks
Parameter available as of CNC Build V3.1.3077.08 and higher
P-AXIS-00754
Weighting factor numerator
Weighting factor numerator. The weighting is calculated from P-AXIS-00754 and P-AXIS-00755:
Weighting factor = P-AXIS-00754 / P-AXIS-00755
The weighting factor affects the output additive velocity per stage. The weighting factor is limited to a maximum value of 7.0.
A weighting factor of <1 reduces the output additive velocity. A weighting factor of >1 increases the output additive velocity.
Parameter
lr_param.improved_position_control.stage[i].weight_fact_num
Data type
UNS32
Data range
0 < weight_fact_num < MAX(UNS32)
Axis types
T, R, S
Dimension
T: —-
R, S: —-
Default value
1
Drive types
Remarks
To ensure the reliable activation of the "Improved Position Control" function, it is advisable to raise the additive velocity slowly via the weighting factor.
P-AXIS-00755
Weighting factor denominator
Weighting factor denominator. The weighting factor is calculated from P-AXIS-00754 and P-AXIS-00755.
A weighting factor of <1 reduces the output additive velocity; a weighting factor of >1 increases the output additive velocity.
Parameter
lr_param.improved_position_control.stage[i].weight_fact_denom
Data type
UNS32
Data range
0 < weight_fact_denom < MAX(UNS32)
Axis types
T, R, S
Dimension
T: —-
R, S: —-
Default value
1
Drive types
Remarks
To ensure the reliable activation of the Improved Position Control function, it is advisable to raise the additive velocity slowly via the weighting factor.
P-AXIS-00756
Damping the simulated mechanical vibration
The parameter specifies the damping of the simulated mechanical vibration for the modes (P-AXIS-00753) INDIRECT and SET_POINT.
The parameter has no influence on the DIRECT mode.
Parameter
lr_param.improved_position_control.stage[i].filter.damping
Data type
REAL64
Data range
0.0 < damping < 1.0
Axis types
T, R, S
Dimension
T: —-
R, S: —-
Default value
-1
Drive types
Remarks
The lower the damping, the more the simulation of the mechanical vibration and the higher the specified additive velocity. To ensure the reliable start of the "Improved Position Control" function, it is advisable to decrease damping slowly.
P-AXIS-00757
Factor for the maximum permissible additive velocity
This parameter limits the maximum permissible additive velocity of the "Improved Position Control" function.
The additive velocity is limited in proportion to the maximum axis velocity.
max. additive velocity = P-AXIS-00757 / 1000 x P-AXIS-00212
If the additive velocity exceeds the calculated value, the limit value continues to be output as the additive velocity.
Parameter
lr_param.improved_position_control.v_add_max_fact
Data type
UNS16
Data range
0 <= v_add_max_fact <= 2000
Axis types
T, R, S
Dimension
T: 0.1%
R, S: 0.1%
Default value
0
Drive types
Remarks
No warning is output if the maximum velocity is exceeded.
P-AXIS-00758
Enabling the Improved Position Control function
This parameter sets the mode of the “Improved Position Control” function.
Parameter
lr_param.improved_position_control.enable
Data type
STRING
Data range
OFF: “Improved Position Control” function is not enabled
ON: “Improved Position Control” function is enabled
DRYRUN: The “Improved Position Control” function is enabled, however, the additive speed is not output to the drive.
Axis types
T, R, S
Dimension
T: ----
R, S: ----
Default value
OFF
Drive types
Remarks
As of V3.1.3132.0, the following CNC objects can be used for start-up:
P-AXIS-00128
Adapting the drive command value to the drive format (denominator)
The speed setpoint calculated in the position controller must be adapted to the D/A format of the D/A converter. The digital value at the D/A converter input (getriebe[i].multi_gain_z/getriebe[i].mulit_gain_n) must be specified at which the axis travels at the velocity of [1m/min] or at the speed [1000°/min].
Numerator: P-AXIS-00129
Parameter
getriebe[i].multi_gain_n
Data type
UNS32
Data range
1 ≤ multi_gain_n ≤ MAX(UNS32)
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
1
Drive types
Simulation, Conventional, Terminal, Lightbus, Profidrive
Remarks
P-AXIS-00129
Adaptation of command value of drive to the drive format (numerator)
Denominator : P-AXIS-00128
Parameter
Data type
UNS32
Data range
1 ≤ multi_gain_z ≤ MAX(UNS32)
Axis types
T, R, S
Dimension
T: Bit
R,S: Bit
Default value
2000
Drive types
Remarks
P-AXIS-00205
Normalisation of the velocity (denominator)
The conversion factor of the set velocity to drive format is obtained by specifying the value output to the drive and the related path distance covered in the time specified in P-AXIS-00207.
This parameter specifies the conversion factor numerator. (P-AXIS-00206 is the numerator)
This parameter indicates the path covered in the time specified in P-AXIS-00207, provided the value in P-AXIS-00206 is output to the drive. The path is specified in 1 µm or 0.001°.
Parameter
antr.v_reso_denom
Data type
UNS32
Data range
1 ≤ v_reso_denom ≤ MAX(UNS32)
Axis types
T, R, S
Dimension
T: 1µm
R,S: 0,001°
Default value
36
Drive types
All drive types
Remarks
P-AXIS-00206
Normalisation of command velocity (numerator)
The conversion factor of the command velocity to drive format is defined by specifying the value output to the drive and the related distance covered in the time specified in P-AXIS-00207 .
This parameter specifies the conversion factor numerator. (P-AXIS-00205 is the denominator)
The factor indicates the number of velocity increments output.
Parameter
antr.v_reso_num
Data type
UNS32
Data range
0 ≤ v_reso_num ≤ MAX(UNS32)
Axis types
T, R, S
Dimension
T: increments
R,S: increments
Default value
1
Drive types
All drive types
Remarks
P-AXIS-00207
Time base for normalisation of velocity
The time base for adapting the velocity interface to the unit used in the drive can be specified as value per minute, second or sampling interval. If normalisation per sampling interval is selected, the output value changes proportionally depending on the CNC cycle time at constant velocity. This may be essential depending on the drive.
Parameter
antr.v_time_base
Data type
UNS16
Data range
0: per minute
1: per second
2: per sampling interval
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
0
Drive types
SERCOS
Remarks
P-AXIS-00848
Prototypes for the band-pass filter
This parameter can affect the basic form and response of a band-pass filter The following prototypes are available:
  • Critically damped
    • Advantages: Highly stable broadband response with minimum oscillations.
    • Disadvantages: Low selectivity of centre frequency
  • Butterworth
    • Advantages: Excellent selectivity and steep edges
    • Disadvantages: Greater phase delay
  • Bessel
    • Advantages: Best phase accuracy and good time response
Parameter
lr_param.improved_position_control.stage[i].filter[k].prototype
Data type
STRING
Data range
CRIT_DAMPING: Critically damped prototype
BUTTERWORTH: Butterworth prototype
BESSEL: Bessel prototype
Axis types
T, R, S
Dimension
T: ----
R, S: ----
Default value
CRIT_DAMPING
Drive types
Remarks
Available as of V3.1.3132.0
If a band-pass filter is parameterised in a filter stage >Y0, a prototype must be specified without fail.
P-AXIS-00849
Filter type used for each filter stage
Specifies the filter type used for each filter stage (filter[k]).
Parameter
lr_param.improved_position_control.stage[i].filter[k].type
Data type
STRING
Data range
NO_FILTER: No filter on this stage
BANDPASS: Band-pass filter
ALLPASS: All-pass filter
Axis types
T, R, S
Dimension
T: ----
R, S: ----
Default value
filter[0].type = BANDPASS, filter[1].type = NO_FILTER
Drive types
Remarks
If no filter type is specified, the band-pass filter at filter stage 0 is assumed. Filter stage 1 is disabled by default.
At least one band-pass filter per stage must be configured for the “Improved Position Control” function.
The order of the band-pass and all-pass filters does not matter.
P-AXIS-00850
Parameter
lr_param.improved_position_control.stage[i]osc_damping
Data type
REAL64
Data range
0.0 < damping < 1.0
Axis types
T, R, S
Dimension
T: ----
R, S: ----
Default value
-1
Drive types
Remarks
Note:
This parameter replaces the parameter P-AXIS-00756 as of V3.1.3132.0. The parameter continues to be valid, but should not be combined with the new parameterisation.