P-AXIS-00750 | Order of band-pass filter | |
Description | This parameter defines the order of the band-pass filter for all modes (P-AXIS-00753). In addition, this parameter is a value which expresses the fall of frequency response (fall = -order x 20 dB/decade). | |
Parameter | lr_param.improved_position_control.stage[i].filter.order | |
Data type | UNS32 | |
Data range | 1 <= order <= 3 | |
Axis types | T, R, S | |
Dimension | T: —- | R, S: —- |
Default value | 0 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks |
P-AXIS-00751 | Frequency | |
Description | This parameter defines a frequency that has a different impact on filter response depending on the filter type setting (P-AXIS-00849). Filter type - Band-pass filter: The parameter defines the frequency that is to be actively damped by the "Improved Position Control" function. The middle frequency is specified for all modes P-AXIS-00753. For the “INDIRECT” and SET_POINT modes, the simulation of the mechanical vibration is based on the same frequency. Filter type - All-pass filter: This parameter defines the frequency at which the greatest phase rotation occurs. In the case of the all-pass filter, the frequency can be varied slightly from the set frequency of the band-pass filter in order to adjust the phase of the additive speed. | |
Parameter | lr_param.improved_position_control.stage[i].filter[k].fg_f0 | |
Data type | REAL64 | |
Data range | 0.0 < fg_f0 <= 500.0 | |
Dimension | T: Hz | R, S: Hz |
Default value | -1 | |
Remarks | The "Improved Position Control" function achieves the best results when the dominant frequency of the mechanical vibration is precisely met. The measured frequency may deviate from the actual frequency due to measurement inaccuracies. In many cases, the performance of the function can be enhanced by varying the parameter fg_f0 within a narrow range. Parameter available as of CNC Build V3.1.3077.08 | |
P-AXIS-00752 | Quality factor of the filter | |
Description | Depending on the filter type selected (P-AXIS-00849), the quality factor has a different impact on filter response.
Filter type - Band-pass filter: Specifies the inverse value of the bandwidth for the band-pass filter for all modes (P-AXIS-00753). P-AXIS-00752 = P-AXIS-00751 / bandwidth
Filter type - All-pass filter: In the case of an all-pass filter, the quality factor determines the magnitude and narrowband nature of the phase shift about the centre frequency fg_f0. The higher the quality factor, the steeper and more concentrated the phase rotation. | |
Parameter | lr_param.improved_position_control.stage[i].filter[k].q_factor | |
Data range | 1.0 <= q_factor <= 10.0 | |
Remarks | A high filter quality limits the bandwidth of the filtering frequencies. To avoid cutting off any relevant frequencies, it is advisable to raise the filter quality step by step. The filter quality is limited by changing the frequency dependent on machine position and mass inertia. Among other things, a higher filter quality leads to improved damping of the required frequency, whereas a lower quality results in a more robust behaviour of frequency damping. Parameter available as of CNC Build V3.1.3077.08 | |
P-AXIS-00753 | Mode for the "Improved Position Control" function | |
Description | The following modes are provided for the "Improved Position Control" function and they are applicable simultaneously to various stages.
Parameter | lr_param.improved_position_control.stage[i].mode | |
Data range | 0 - NOT_ACTIVE 1 - DIRECT 2 - INDIRECT 3 - SET_POINT | |
Remarks | Parameter available as of CNC Build V3.1.3077.08 and higher | |
P-AXIS-00754 | Weighting factor numerator | |
Description | Weighting factor numerator. The weighting is calculated from P-AXIS-00754 and P-AXIS-00755: Weighting factor = P-AXIS-00754 / P-AXIS-00755 The weighting factor affects the output additive velocity per stage. The weighting factor is limited to a maximum value of 7.0. A weighting factor of <1 reduces the output additive velocity. A weighting factor of >1 increases the output additive velocity. | |
Parameter | lr_param.improved_position_control.stage[i].weight_fact_num | |
Data range | 0 < weight_fact_num < MAX(UNS32) | |
Default value | 1 | |
Remarks | To ensure the reliable activation of the "Improved Position Control" function, it is advisable to raise the additive velocity slowly via the weighting factor. Parameter available as of CNC Build V3.1.3077.08 and higher | |
P-AXIS-00755 | Weighting factor denominator | |
Description | Weighting factor denominator. The weighting factor is calculated from P-AXIS-00754 and P-AXIS-00755. Weighting factor = P-AXIS-00754 / P-AXIS-00755 The weighting factor affects the output additive velocity per stage. The weighting factor is limited to a maximum value of 7.0. A weighting factor of <1 reduces the output additive velocity; a weighting factor of >1 increases the output additive velocity. | |
Parameter | lr_param.improved_position_control.stage[i].weight_fact_denom | |
Data range | 0 < weight_fact_denom < MAX(UNS32) | |
Remarks | To ensure the reliable activation of the Improved Position Control function, it is advisable to raise the additive velocity slowly via the weighting factor. | |
P-AXIS-00756 | Damping the simulated mechanical vibration | |
Description | The parameter specifies the damping of the simulated mechanical vibration for the modes (P-AXIS-00753) INDIRECT and SET_POINT. The parameter has no influence on the DIRECT mode. | |
Parameter | lr_param.improved_position_control.stage[i].filter.damping | |
Data range | 0.0 < damping < 1.0 | |
Remarks | The lower the damping, the more the simulation of the mechanical vibration and the higher the specified additive velocity. To ensure the reliable start of the "Improved Position Control" function, it is advisable to decrease damping slowly. Parameter available as of CNC Build V3.1.3077.08 and higher | |
P-AXIS-00757 | Factor for the maximum permissible additive velocity | |
Description | This parameter limits the maximum permissible additive velocity of the "Improved Position Control" function. The additive velocity is limited in proportion to the maximum axis velocity. max. additive velocity = P-AXIS-00757 / 1000 x P-AXIS-00212 If the additive velocity exceeds the calculated value, the limit value continues to be output as the additive velocity. | |
Parameter | lr_param.improved_position_control.v_add_max_fact | |
Data type | UNS16 | |
Data range | 0 <= v_add_max_fact <= 2000 | |
Dimension | T: 0.1% | R, S: 0.1% |
Remarks | No warning is output if the maximum velocity is exceeded. Parameter available as of CNC Build V3.1.3077.08 and higher | |
P-AXIS-00758 | Enabling the Improved Position Control function | |
Description | This parameter sets the mode of the “Improved Position Control” function. | |
Parameter | lr_param.improved_position_control.enable | |
Data type | STRING | |
Data range | OFF: “Improved Position Control” function is not enabled ON: “Improved Position Control” function is enabled DRYRUN: The “Improved Position Control” function is enabled, however, the additive speed is not output to the drive. | |
Dimension | T: ---- | R, S: ---- |
Default value | OFF | |
Remarks | Parameter available as of CNC Build V3.1.3077.08 As of V3.1.3132.0, the following CNC objects can be used for start-up:
P-AXIS-00128 | Adapting the drive command value to the drive format (denominator) | |
Description | The speed setpoint calculated in the position controller must be adapted to the D/A format of the D/A converter. The digital value at the D/A converter input (getriebe[i].multi_gain_z/getriebe[i].mulit_gain_n) must be specified at which the axis travels at the velocity of [1m/min] or at the speed [1000°/min]. Numerator: P-AXIS-00129 | |
Parameter | getriebe[i].multi_gain_n | |
Data range | 1 ≤ multi_gain_n ≤ MAX(UNS32) | |
Dimension | T: ---- | R,S: ---- |
Drive types | Simulation, Conventional, Terminal, Lightbus, Profidrive | |
Remarks |
P-AXIS-00129 | Adaptation of command value of drive to the drive format (numerator) | |
Description | The speed setpoint calculated in the position controller must be adapted to the D/A format of the D/A converter. The digital value at the D/A converter input (getriebe[i].multi_gain_z/getriebe[i].mulit_gain_n) must be specified at which the axis travels at the velocity of [1m/min] or at the speed [1000°/min]. Denominator : P-AXIS-00128 | |
Parameter | getriebe[i].multi_gain_z | |
Data range | 1 ≤ multi_gain_z ≤ MAX(UNS32) | |
Dimension | T: Bit | R,S: Bit |
Default value | 2000 | |
Remarks |
P-AXIS-00205 | Normalisation of the velocity (denominator) | |
Description | The conversion factor of the set velocity to drive format is obtained by specifying the value output to the drive and the related path distance covered in the time specified in P-AXIS-00207. This parameter specifies the conversion factor numerator. (P-AXIS-00206 is the numerator) This parameter indicates the path covered in the time specified in P-AXIS-00207, provided the value in P-AXIS-00206 is output to the drive. The path is specified in 1 µm or 0.001°. | |
Parameter | antr.v_reso_denom | |
Data range | 1 ≤ v_reso_denom ≤ MAX(UNS32) | |
Dimension | T: 1µm | R,S: 0,001° |
Default value | 36 | |
Drive types | All drive types | |
Remarks |
P-AXIS-00206 | Normalisation of command velocity (numerator) | |
Description | The conversion factor of the command velocity to drive format is defined by specifying the value output to the drive and the related distance covered in the time specified in P-AXIS-00207 . This parameter specifies the conversion factor numerator. (P-AXIS-00205 is the denominator) | |
Parameter | antr.v_reso_num | |
Data range | 0 ≤ v_reso_num ≤ MAX(UNS32) | |
Dimension | T: increments | R,S: increments |
Remarks |
P-AXIS-00207 | Time base for normalisation of velocity | |
Description | The time base for adapting the velocity interface to the unit used in the drive can be specified as value per minute, second or sampling interval. If normalisation per sampling interval is selected, the output value changes proportionally depending on the CNC cycle time at constant velocity. This may be essential depending on the drive. | |
Parameter | antr.v_time_base | |
Data range | 0: per minute 1: per second 2: per sampling interval | |
Drive types | SERCOS | |
Remarks |
P-AXIS-00848 | Prototypes for the band-pass filter | |
Description | This parameter can affect the basic form and response of a band-pass filter The following prototypes are available:
Parameter | lr_param.improved_position_control.stage[i].filter[k].prototype | |
Data range | CRIT_DAMPING: Critically damped prototype BUTTERWORTH: Butterworth prototype BESSEL: Bessel prototype | |
Default value | CRIT_DAMPING | |
Remarks | Available as of V3.1.3132.0 If a band-pass filter is parameterised in a filter stage >Y0, a prototype must be specified without fail. | |
P-AXIS-00849 | Filter type used for each filter stage | |
Description | Specifies the filter type used for each filter stage (filter[k]). | |
Parameter | lr_param.improved_position_control.stage[i].filter[k].type | |
Data range | NO_FILTER: No filter on this stage BANDPASS: Band-pass filter ALLPASS: All-pass filter | |
Default value | filter[0].type = BANDPASS, filter[1].type = NO_FILTER | |
Remarks | Available as of V3.1.3132.0 If no filter type is specified, the band-pass filter at filter stage 0 is assumed. Filter stage 1 is disabled by default. At least one band-pass filter per stage must be configured for the “Improved Position Control” function. The order of the band-pass and all-pass filters does not matter. | |
P-AXIS-00850 | Damping the simulated mechanical vibration | |
Parameter | lr_param.improved_position_control.stage[i]osc_damping | |
Remarks | Available as of V3.1.3132.0 The lower the damping, the more the simulation of the mechanical vibration and the higher the specified additive velocity. To ensure the reliable start of the "Improved Position Control" function, it is advisable to decrease damping slowly. Note: This parameter replaces the parameter P-AXIS-00756 as of V3.1.3132.0. The parameter continues to be valid, but should not be combined with the new parameterisation. | |