P-AXIS-00014
Identification code for absolute path measurement system
If an absolute path measurement system is used, then the parameter must be set to 1. So no homing is necessary.
Parameter
kenngr.abs_pos_gueltig
Data type
BOOLEAN
Data range
0/1
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
0
Drive types
Simulation, SERCOS, CANopen
Remarks
P-AXIS-00015
Axis mode
Axes can be traversed in different operating modes.
Parameter
kenngr.achs_mode
Data type
UNS32
Data range
0x00000001 - 0x10000000
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
0x00000001
Drive types
Remarks
The following operation modes can be parameterised(1):
Value
Meaning
Axis type
Interpolator type
ACHSMODE_
path
spindle
0x00000001
The axis is operated as a linear axis; no modulo calculation is executed in the channel. For example, rotary axis with restricted motion range; must be set as default for linear axes.
..LINEAR(1)
T, R
X
0x00000004
A modulo calculation always takes place after the destination position has been reached. Regardless of the operation mode selected for rotary axes, a modulo calculation is always executed in the position controller. In this way, modulo circle compensation can be executed if required.
..MODULO(1)
R
X
X
0x00000040
Axis is used as a face turning axis (turning functions).
..PLANDREHEN
T
X
0x00000080
Axis is used as a longitudinal turning axis (turning functions).
..LAENGSDREHEN
T
X
0x00000100
For a spindle an automatic homing before positioning the spindle can be pre-vented. This is only relevant if the axis is not referenced. The function is drive-dependent.
..KEINE_AUTO_RPF
R
X
0x00000200
Axis for kinematic 'C axis' transformation.
..CAX
R
X
X
0x00000400
Modulo calculation for linear axis. (Example: conveyor belt with drive motor where the position on the belt is programmed in mm).
..MODULO_LINEAR
R
X
0x00000800
Axis is released for mechanical blocking by the PLC.
This axis mode is not available for TwinCAT systems.
..CLAMPABLE
T, R
X
0x00001000
Axis carries a rotary workpiece table.
..ROT_TABLE
T, R
X
0x00008000
Monitoring of axis collision.
..COLL_CHECK
T
X
0x00010000
Master axis of gantry coupling.
..GANTRY_MASTER
T, R
X
0x00020000
Slave axis of gantry coupling.
..GANTRY_SLAVE
T, R
X
0x00040000
Identifier for PLC spindle with axis interface
..SPINDLE_EXT_CTRL
R
X
0x00080000
Input axis for additional external position command values (e.g. distance control).
..EXT_CTRL_INPUT
T
X
0x00100000
Pure encoder axis, only to display actual values (e.g. conveyor belt).
..COUNTER
T, R
X
X
0x00200000
Lead axis in combination with single feed axis and G194 (contouring with DIST_MASTER)
..LEAD_AXIS
T, R
X
0x00400000
The resolution (wegaufz/wegaufn) of this axis can be changed.
..ALLOW_RESOLUTION_
CHANGE(2)
T, R
X
X
0x00800000
Path-dependent dynamic weighting for this axis is possible.
..DYNAMIC_WEIGHTING
T, R
X
0x02000000
Path axis for tool centre point path
..PATH_LENGTH_TCP
R
X
0x04000000
Path axis for contour path
..PATH_LENGTH_
CONTOUR
R
X
0x08000000
Virtual lead axis for path interpolation
..VIRT_LEAD_AXIS
R
X
0x10000000
Axis carries the pressure roller for edge banding.
..LAH_OFFSET_AXIS
R
X
(1) One of the following two axis modes must always be defined:
- ACHSMODE_LINEAR or
- ACHSMODE_MODULO
All other bits of the parameter achs_mode are additional specifications. For example, the ACHSMODE_MODULO_LINEAR bit is only useful if combined with the ACHSMODE_MODULO bit.
(2) Changing certain axis parameters may be critical while a controller is running, e.g. path resolution,. Therefore, this parameter can be enabled by setting the bit ALLOW_RESOLUTION_CHANGE in axis mode. Otherwise, these parameters (P-AXIS-00234, P-AXIS-00233) can no longer be changed after controller start-up.
When the bit ALLOW_RESOLUTION_CHANGE is set, a check is first made whether the axis is interpolated, also when other critical parameters change. If the axis is currently in motion, this parameter update is rejected.
P-AXIS-00036
Access to cam signals
The parameter defines the access to cam signals.
Parameter
lr_hw[i].cam_direct_access
Data type
BOOLEAN
Data range
0/1
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
1
drive types.
Conventional, Terminal, Lightbus, Profidrive
Remarks
This entry is not adopted when the axis parameter list is updated. Updates only become effective when the controller is rebooted.
P-AXIS-00038
Level of cam signals
The parameter defines the level of cam signals.
Parameter
lr_hw[i].cam_level
Data type
BOOLEAN
Data range
0: 0-signal is active level.
When the reference cam switch is actuated, the value of the control unit element
gpAx[axis_idx]^.lr_mc_control.reference_cam.command_w on the HLI is FALSE.
1: 1-signal is active level (default).
gpAx[axis_idx]^.lr_mc_control.reference_cam.command_w on the HLI is TRUE.
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
1
Drive types
Remarks
P-AXIS-00064
Slow / fast movement down from cam
This parameter sets the velocity during reversion down from cam.
Parameter
kenngr.fast_from_cam
Data type
BOOLEAN
Data range
0: Slow movement down from cam
1: Fast movement down from cam (default)
Axis types
T, R
Dimension
T: ----
R: ----
Default value
1
drive types.
Remarks
For further hardware-specific parameters relating to homing with cam, see P-AXIS-00036 - P-AXIS-00039.
P-AXIS-00074
Suppress homing for gantry slave axis
This parameter can suppress the homing of gantry slave axes. When homing of the master axis is completed, the reference positions entered in the axis parameter lists of the slave axes are also adopted and monitoring of the gantry difference is started.
Parameter
kenngr.gantry_slave_no_homing
Data type
BOOLEAN
Data range
0/1
Axis types
T, R
Dimension
T: ----
R: ----
Default value
0
drive types.
Remarks
This parameter is not supported in the case of spindle axes.
P-AXIS-00084
Homing only with cam (without zero pulse)
The homing position is detected by travel on the cam.
Parameter
kenngr.homing_without_zero_pulse
Data type
BOOLEAN
Data range
0: Homing with zero pulse of rotary transducer (default value).
1: Homing without zero pulse of rotary transducer (low accuracy).
Axis types
T, R
Dimension
T: ----
R:----
Default value
0
drive types.
Remarks
P-AXIS-00152
Position of the reference point
If homing is completed, the value from the parameter P-AXIS-00152 is taken as the absolute position for the axis
Parameter
getriebe[i].pos_refpkt
Data type
SGN32
Data range
swe_neg < pos_refpkt < swe_pos
Axis types
T, R, S
Dimension
T: 0.1 µm
R,S: 0.0001 °
Default value
0
drive types.
Simulation, Conventional, Terminal, Lightbus, Profidrive, CANopen
Remarks
P-AXIS-00156
Homing without cam
A changeover of homing strategy can be carried out so that homing is done without cam (e.g. only with zero pulse), i.e. without reverting.
In this case the parameter P-AXIS-00156 should be set to TRUE.
Parameter
kenngr.ref_ohne_nocken
Data type
BOOLEAN
Data range
0/1
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
0
drive types.
Remarks
To be assigned for analogue spindles only. If P-AXIS-00156 is assigned with 1 (TRUE), then it is imperative that P-AXIS-00157 is assigned with 1 (TRUE).
P-AXIS-00157
Homing without reverting
Via parameter P-AXIS-00157 a restriction of homing can occur that will prohibit any reverting.
Parameter
kenngr.ref_ohne_rev
Data type
BOOLEAN
Data range
0/1
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
0
drive types.
Remarks
The speed during reversing is set with the parameter P-AXIS-00064 (fast_from_cam). By reverting, it is possible to repeatedly move to the reference cam at slow speed.
To be assigned for analogue spindles only. P-AXIS-00157 must be assigned with 1 (TRUE) if P-AXIS-00156 is assigned with 1 (TRUE).
P-AXIS-00158
Preferred direction of axis for homing
The parameter P-AXIS-00158 specifies the direction of travel if the axis does not remain on a cam.
The declaration of the signal level when the reference switch is actuated is given by the axis parameter P-AXIS-00038.
Parameter
kenngr.ref_richt
Data type
BOOLEAN
Data range
0: Negative direction
1: Positive direction
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
0
drive types.
Remarks
Positive direction signifies that the coordinate values increase.
Negative direction signifies that the coordinate values decrease.
P-AXIS-00161
Tool path up to zero pulse during homing simulation
The parameter defines the tool path up to zero pulse during homing simulation.
Parameter
antr.simu.rpf_weg_bis_nip
Data type
SGN32
Data range
MIN(SGN32) ≤ rpf_weg_bis_nip ≤ MAX(SGN32)
Axis types
T, R, S
Dimension
T: 0.1µm
R,S: 0.0001 °
Default value
10
drive types.
Simulation
Remarks
P-AXIS-00218
Slow velocity for exact detection of reference position
Not only the traverse downwards of cam but also the traverse on cam with homing takes place at the velocity P-AXIS-00218.
Parameter
getriebe[i].vb_reflow
Data type
UNS32
Data range
1 ≤ vb_reflow ≤ P-AXIS-00219
Axis types
T, R, S
Dimension
T: µm/s
R,S: 0.001°/s
Default value
16666
drive types.
Remarks
P-AXIS-00219
Fast velocity for detection of reference cam
At start of homing, if the axis is not on the cam, then travel on the cam takes place at the velocity defined in P-AXIS-00219.
Parameter
getriebe[i].vb_refmax
Data type
UNS32
Data range
P-AXIS-00218 ≤ vb_refmax ≤ P-AXIS-00212
Axis types
T, R, S
Dimension
T: µm/s
R,S: 0.001°/s
Default value
83333
drive types.
Remarks
P-AXIS-00294
Selection of the homing method 'Evaluation of encoder overflow'
This homing method is selected with the parameter P-AXIS-00294. To use this option, the parameter P-AXIS-00084 must be assigned the value 0.
The number of bits used to detect encoder overflow has to be set in parameter P-AXIS-00355 .
Parameter
kenngr.homing_overflow_evaluation
Data type
BOOLEAN
Data range
0: No evaluation of encoder overflow (default).
1: Evaluation of encoder overflow.
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
0
drive types.
Lightbus
Remarks
This homing method only leads to a repeatable homing position of the axis when encoder overflow occurs every time at the same mechanical position of the axis. This is true for example for resolver encoders.
P-AXIS-00299
Homing type
There are two different homing methods:
  1. NC-controlled homing
  2. Drive-controlled homing
With NC-controlled homing, the generation of command values and sequence control (evaluation of reference cams and zero pulses) are handled in the CNC.
With drive-controlled homing, motion generation and the evaluation of cam signals and zero pulses are handled in the drive.
The homing method can be set up for drives types (P-AXIS-00018) for which both homing methods are implemented with this parameter.
Parameter
kenngr.homing.homing_type *
(Note: see *-note below)
Data type
STRING
Data range
CNC_CONTROLLED: CNC-controlled homing is done.
DRIVE_CONROLLED: Drive-controlled homing is done.
TORQ: CNC-controlled homing to a fixed stop is executed, see Homing to fixed stop (as of V3.1.3080.11).
DISABLED: This axis cannot be homed. The CNC generates the error message ID 50685 or ID 60313 if homing is commanded for the axis (e.g. G74). This setting is only intended for axes with an absolute measuring system (see P-AXIS-00014).
IGNORE_ABS_POS: Axes with this setting are ignored during homing, i.e. the axis is not homed even if G74 <axis_name> is programmed. In this case the CNC generates no error message contrary to the setting DISABLED. The mode IGNORE_ABS_POS is only permitted for axis with an absolute position measuring system, meaning the parameter kenngr.abs_pos_gueltig (see P-AXIS-00014) must be set to 1. Otherwise the CNC generates the error warning ID 110584.
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
CNC_CONTROLLED
Drive types
Remarks
* alternative: kenngr.homing_type (old syntax)
If the homing command G74 involves multiple axes with different homing type setting e.g. G74 X1 Y1 Z2, the axis with kenngr.homing_type != IGNORE_ABS_POS/ DISABLED will move and try to find the homing switch while there is no movement on the homing suppressed axes. Therefore it must be ensured that no collision can occur.
If a homing type which is not supported by the drive type is set, the error message ID 110384 is output and the value is corrected to the default homing type.
If this entry is not present in the parameter list, the default homing type is used according to the drive type:
Drive type
CNC_CONTROLLED
DRIVE_CONTROLLED
simulation
X*
SERCOS
X
X*
Terminal
X*
Lightbus
X*
RT Ethernet
X*
PROFIDRIVE
X*
CANopen
X*
X
* Default homing_type
P-AXIS-00321
Input interface for reference cam signal
In the default setting with CNC-controlled homing, the reference cam signal is read from the HLI [HLI].
For some drive types it is possible to use the drive digital inputs as reference cam input. In this case the appropriate input has to be configured in P-AXIS-00321.
If this parameter is not set, the reference cam signal is read from the PLC interface.
Parameter
antr.reference_cam_signal
Data type
STRING
Data range
Dependent on the drive type the following different names for the digital inputs are possible:
Drive type SERCOS:
PLC                  Read reference cam signal from HLI (default)
RT_STATUS_BIT_1 Read reference cam signal from real time status bit 1
RT_STATUS_BIT_2 Read reference cam signal from real time status bit 2
Drive type CANopen:
STATUS_DIG_INPUTS (*) Reference cam signal from object 0x60FD : Digital inputs
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
PLC
drive types.
SERCOS, Lightbus,CANopen
Remarks
Caution: It is only possible to use real-time status bits with NC-controlled homing, see also [CMS-A1].
If the drive digital inputs are used, they must also be parameterised using the drive manufacturer’s set-up tool.
The transmission of the digital inputs in the cyclic telegram must also be configured.
(*) For the transmission of the reference cam state, the object 0x60FD: Digital inputs must be configured (see DS402 drive profile). Otherwise, the error message with error code P-ERR-70292 is output.
P-AXIS-00354
Shifting of encoder overflow
When homing with encoder overflow this parameter can shift the reference position. A positive value for P-AXIS-00354 will shift the reference position in the positive movement direction of the axis.
Parameter
antr.encoder_overflow_offset
Data type
SGN32
Data range
application-specific
Axis types
T, R, S
Dimension
T: 0.1 µm
R,S: 0.1 µm
Default value
0
drive types.
Remarks
The reference position can only be shifted within one encoder revolution. If larger values for P-AXIS-00354 are defined, the error message P-ERR-70310 is output and P-AXIS-00354 is corrected to 0.
P-AXIS-00355
Number of bits for evaluation of encoder overflow
When homing on encoder overflow, this parameter defines the number of bits of the drive's actual position value that are taken into account to detect encoder overflow.
The actual position value of the drive system is AND-combined with the value (2P-AXIS-00355 -1) and the underflow or overflow of the resulting value is considered as encoder overflow.
Parameter
antr.encoder_bit_range
Data type
UNS08
Data range
1 … 31
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
0
drive types.
Remarks
P-AXIS-00386
Drive supported execution of the CNC based homing (SERCOS)
By default CNC-controlled homing for SERCOS drives is only executed in the controller; the drive-internal positions are not altered.
If the drive supports the SERCOS command S-0-146 (CNC-controlled homing), this parameter can enable the command S-0-146 for CNC-controlled homing. The advantage of this method is that, after homing is finished, the drive-internal positions are also referenced so that drive-internal software limit switches can be used, for example.
The reference position used for homing is P-AXIS-00152. This value is transferred to the drive during homing
Parameter
antr.sercos.drive_supports_cnc_homing
Data type
BOOLEAN
Data range
0/1
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
0
drive types.
SERCOS
Remarks
This parameter is currently not supported for spindles.
In addition to command S-0-146 the drive must support the following commands:
  • S-0-171 (Calculate displacement)
  • S-0-172 (Displacement to referenced system)
  • S-0-191 (Cancel reference point procedure)
For further information please refer to the drive manufacturer's documentation..
P-AXIS-00387
Assignment of control and status bits for CNC based homing (SERCOS)
To execute CNC-controlled homing with drive support, two control bits and two status bits are required. The real-time control and status bits can be used in the drive control and status word or alternatively as bits in the signal status and signal control word.
Parameter
antr.sercos.cnc_homing_rt_bit_layout
Data type
UNS16
Data range
1 ≤ cnc_homing_rt_bit_layout ≤ 16
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
0
drive types.
SERCOS
Remarks
When the status and control bits are transferred in the signal status and control words, they must be configured in the cyclic process data, otherwise the error message P-ERR-70295 is output.
Assign the values of P-AXIS-00387 to the possible bit assignments:
Value
Process data
Bit number
Meaning
Ident
1
Control word
Real-time bit 1 (S-0-301)
Homing enable
S-0-407
Real-time bit 2 (S-0-303)
Position command value referenced
S-0-404
Status word
Real-time bit 1 (S-0-305)
Position marker pulse detected
S-0-408
Real-time bit 2 (S-0-307)
Actual value referenced
S-0-403
2
Signal control word
Bit 0 (S-0-27[0])
Homing enable
S-0-407
Bit 1 (S-0-27[1])
S-0-404
Signal status word
Bit 0 (S-0-26[0])
S-0-408
Bit 1 (S-0-26[1])
S-0-403
3
Signal control word
Bit 1 (S-0-27[1])
Homing enable
S-0-407
Bit 2 (S-0-27[2])
S-0-404
Signal status word
Bit 1 (S-0-26[1])
S-0-408
Bit 2 (S-0-26[2])
S-0-403
4
Signal control word
Bit 2 (S-0-27[2])
Homing enable
S-0-407
Bit 3 (S-0-27[3])
S-0-404
Signal status word
Bit 2 (S-0-26[2])
S-0-408
Bit 3 (S-0-26[3])
S-0-403
5
Signal control word
Bit 3 (S-0-27[3])
Homing enable
S-0-407
Bit 4 (S-0-27[4])
S-0-404
Signal status word
Bit 3 (S-0-26[3])
S-0-408
Bit 4 (S-0-26[4])
S-0-403
6
Signal control word
Bit 4 (S-0-27[4])
Homing enable
S-0-407
Bit 5 (S-0-27[5])
S-0-404
Signal status word
Bit 4 (S-0-26[4])
S-0-408
Bit 5 (S-0-26[5])
S-0-403
7
Signal control word
Bit 5 (S-0-27[5])
Homing enable
S-0-407
Bit 6 (S-0-27[6])
S-0-404
Signal status word
Bit 5 (S-0-26[5])
S-0-408
Bit 6 (S-0-26[6])
S-0-403
8
Signal control word
Bit 6 (S-0-27[6])
Homing enable
S-0-407
Bit 7 (S-0-27[7])
S-0-404
Signal status word
Bit 6 (S-0-26[6])
S-0-408
Bit 7 (S-0-26[7])
S-0-403
9
Signal control word
Bit 7 (S-0-27[7])
Homing enable
S-0-407
Bit 8 (S-0-27[8])
S-0-404
Signal status word
Bit 7 (S-0-26[7])
S-0-408
Bit 8 (S-0-26[8])
S-0-403
10
Signal control word
Bit 8 (S-0-27[8])
Homing enable
S-0-407
Bit 9 (S-0-27[9])
S-0-404
Signal status word
Bit 8 (S-0-26[8])
S-0-408
Bit 9 (S-0-26[9])
S-0-403
11
Signal control word
Bit 9 (S-0-27[9])
Homing enable
S-0-407
Bit 10 (S-0-27[10])
S-0-404
Signal status word
Bit 9 (S-0-26[9])
S-0-408
Bit 10 (S-0-26[10])
S-0-403
12
Signal control word
Bit 10 (S-0-27[10])
Homing enable
S-0-407
Bit 11 (S-0-27[11])
S-0-404
Signal status word
Bit 10 (S-0-26[10])
S-0-408
Bit 11 (S-0-26[11])
S-0-403
13
Signal control word
Bit 11 (S-0-27[11])
Homing enable
S-0-407
Bit 12 (S-0-27[1]2)
S-0-404
Signal status word
Bit 11 (S-0-26[11])
S-0-408
Bit 12 (S-0-26[1]2)
S-0-403
14
Signal control word
Bit 12 (S-0-27[12])
Homing enable
S-0-407
Bit 13 (S-0-27[13])
S-0-404
Signal status word
Bit 12 (S-0-26[12])
S-0-408
Bit 13 (S-0-26[13])
S-0-403
15
Signal control word
Bit 13 (S-0-27[13])
Homing enable
S-0-407
Bit 14 (S-0-27[1]4)
S-0-404
Signal status word
Bit 13 (S-0-26[13])
S-0-408
Bit 14 (S-0-26[14])
S-0-403
16
Signal control word
Bit 14 (S-0-27[14])
Homing enable
S-0-407
Bit 15 (S-0-27[15])
S-0-404
Signal status word
Bit 14 (S-0-26[14])
S-0-408
Bit 15 (S-0-26[15])
S-0-403
P-AXIS-00388
Encoder, used for CNC controlled homing (SERCOS)
Some drive types support the use of multiple encoders (motor encoder and external encoder). This parameter defines which encoder is used for homing.
Parameter
antr.cnc_homing_encoder
Data type
SGN16
Data range
0: Value is not configured. If P-AXIS-00386 is set to 1, set this parameter to a valid value (0, 1, 2).
1: The encoder used for homing is determined automatically, e.g. for SERCOS drives, by reading drive parameter S-0-147.
2: Motor encoder
3: External encoder
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
0
Drive types
SERCOS
Remarks
At the moment this parameter is supported only for SERCOS.
If the encoder set in S-0-147 for SERCOS drives fails to match the value set in P-AXIS-00388, the error message ID 70453 is output.
This value is only effective when P-AXIS-00386 has the value 1.
P-AXIS-00412
Maximum distance during homing
This parameter defines a maximum distance for homing for spindles and rotary axes. If the maximum permissible homing distance is exceeded, homing is aborted and error message P-ERR-70394 is output.
It achieves that homing is aborted if, for example, the reference cam is not found due to a wiring error.
This parameter works only for spindles and rotary axes, see P-AXIS-00018. If this parameter is set for linear axes to a value unequal to zero, the error message P-ERR-110545 is output and the parameter is corrected to 0.
A value of 0 disables distance monitoring during homing.
Parameter
kenngr.distc.a_max
Data type
UNS32
Data range
0 ≤ homing_max_movement_dist ≤ MAX(UNS32)
Axis types
R, S
Dimension
R,S: 0.0001 °
Default value
0
drive types.
Remarks
This parameter has to be set to a value which is at least equal to the modulo range of the axis in order to complete homing successfully.
P-AXIS-00425
Bit number of signal 'Drive is referenced' during reference monitoring
In this parameter enter the number of the bit which is used for transmission of the signal 'Drive is referenced' from the drive to the controller during active reference monitoring.
The least significant bit has bit number 0.
The maximum value depends on the length of the configured telegram element which is used for transmission.
Length of telegram element
Max. bit number
-1
No reference monitoring
2
15
4
31
Entering an invalid bit number in the parameter results in the output of error message ID 110549.
Parameter
antr.reference_check.bit_nr
Data type
SGN16
Data range
0 ≤ bit_nr ≤ Max. bit number
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
-1
Drive types
SERCOS, CANopen
Remarks
This parameter is used for SERCOS and CANopen drives only.
P-AXIS-00426
Element name of signal 'Drive is referenced' during reference monitoring
In this parameter enter the name of the element of the cyclic input process data which is used for transmission of the signal 'Drive is referenced' from the drive.
If the parameter entered in P-AXIS-00426 is not found in the cyclic process data of the drive, an error message ID 70401 is output.
Parameter
antr.reference_check.element_name
Data type
STRING
Data range
<Empty string>: Reference monitoring is disabled
S-0-0135: When the SERCOS state word is used for transmission of the reference signal, the parameter has to be set to 'S-0-0135'…
<Telegram_element_Name>: ...or, alternatively, the name of a telegram element configured in the cyclic process data.
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
Drive types
SERCOS, CANopen
Remarks
* Note: The default value of variables is a blank string.
Reference monitoring is activated by assigning a value to this parameter. When reference monitoring is activated, the parameter P-AXIS-00425 must also be assigned a valid value.
This parameter is currently used for SERCOS and CANopen drives only.
It is not possible to change by a list update (ID 110550).
P-AXIS-00494
Delayed activation of zero pulse logic
For CNC-controlled homing (see P-AXIS-00299) the parameter delays the activation of the zero pulse logic after the actuation of the reference switch. This can be useful if the reference cam and the zero pulse are situated closely together and the detection of the zero pulse is therefore not reliably possible. In this case the next or the next but one zero pulse after the reference cam could be detected depending on the actuation speed of the reference cam.
Parameter
kenngr.shift_offset_zero_pulse_activation
Data type
UNS32
Data range
0 ≤ shift_offset_zero_pulse_activation ≤ MAX_UNS32
Axis types
T, R, S
Dimension
T: 0.1 µm
R,S: 0.0001 °
Default value
0
drive types.
Conventional, SERCOS, Terminal, Lightbus, Profidrive, CANopen
Remarks