P-AXIS-00014 | Identification code for absolute path measurement system | |
Description | If an absolute path measurement system is used, then the parameter must be set to 1. So no homing is necessary. | |
Parameter | kenngr.abs_pos_gueltig | |
Data type | BOOLEAN | |
Data range | 0/1 | |
Axis types | T, R, S | |
Dimension | T: ---- | R,S: ---- |
Default value | 0 | |
Drive types | Simulation, SERCOS, CANopen | |
Remarks |
P-AXIS-00015 | Axis mode | |
Description | Axes can be traversed in different operating modes. | |
Parameter | kenngr.achs_mode | |
Data type | UNS32 | |
Data range | 0x00000001 - 0x10000000 | |
Default value | 0x00000001 | |
Drive types | ---- | |
Remarks |
The following operation modes can be parameterised(1):
Value | Meaning | Axis type | Interpolator type | ||
| Description | ACHSMODE_ |
| path | spindle |
0x00000001 | The axis is operated as a linear axis; no modulo calculation is executed in the channel. For example, rotary axis with restricted motion range; must be set as default for linear axes. | ..LINEAR(1) | T, R | X |
0x00000004 | A modulo calculation always takes place after the destination position has been reached. Regardless of the operation mode selected for rotary axes, a modulo calculation is always executed in the position controller. In this way, modulo circle compensation can be executed if required. | ..MODULO(1) | R | X | X |
0x00000040 | Axis is used as a face turning axis (turning functions). | ..PLANDREHEN | T | X |
0x00000080 | Axis is used as a longitudinal turning axis (turning functions). | ..LAENGSDREHEN | T | X |
0x00000100 | For a spindle an automatic homing before positioning the spindle can be pre-vented. This is only relevant if the axis is not referenced. The function is drive-dependent. | ..KEINE_AUTO_RPF | R |
| X |
0x00000200 | Axis for kinematic 'C axis' transformation. | ..CAX | R | X | X |
0x00000400 | Modulo calculation for linear axis. (Example: conveyor belt with drive motor where the position on the belt is programmed in mm). | ..MODULO_LINEAR | R | X |
0x00000800 | Axis is released for mechanical blocking by the PLC. This axis mode is not available for TwinCAT systems. | ..CLAMPABLE | T, R | X |
0x00001000 | Axis carries a rotary workpiece table. | ..ROT_TABLE | T, R | X |
0x00008000 | Monitoring of axis collision. | ..COLL_CHECK | T | X |
0x00010000 | Master axis of gantry coupling. | ..GANTRY_MASTER | T, R | X |
0x00020000 | Slave axis of gantry coupling. | ..GANTRY_SLAVE | T, R | X |
0x00040000 | Identifier for PLC spindle with axis interface | ..SPINDLE_EXT_CTRL | R |
| X |
0x00080000 | Input axis for additional external position command values (e.g. distance control). | ..EXT_CTRL_INPUT | T | X |
0x00100000 | Pure encoder axis, only to display actual values (e.g. conveyor belt). | ..COUNTER | T, R | X | X |
0x00200000 | Lead axis in combination with single feed axis and G194 (contouring with DIST_MASTER) | ..LEAD_AXIS | T, R | X |
0x00400000 | The resolution (wegaufz/wegaufn) of this axis can be changed. | ..ALLOW_RESOLUTION_ | T, R | X | X |
0x00800000 | Path-dependent dynamic weighting for this axis is possible. | ..DYNAMIC_WEIGHTING | T, R | X |
0x02000000 | Path axis for tool centre point path | ..PATH_LENGTH_TCP | R | X |
0x04000000 | Path axis for contour path | ..PATH_LENGTH_ | R | X |
0x08000000 | Virtual lead axis for path interpolation | ..VIRT_LEAD_AXIS | R | X |
0x10000000 | Axis carries the pressure roller for edge banding. | ..LAH_OFFSET_AXIS | R | X |
![]() | (1) One of the following two axis modes must always be defined: - ACHSMODE_LINEAR or All other bits of the parameter achs_mode are additional specifications. For example, the ACHSMODE_MODULO_LINEAR bit is only useful if combined with the ACHSMODE_MODULO bit. |
![]() | (2) Changing certain axis parameters may be critical while a controller is running, e.g. path resolution,. Therefore, this parameter can be enabled by setting the bit ALLOW_RESOLUTION_CHANGE in axis mode. Otherwise, these parameters (P-AXIS-00234, P-AXIS-00233) can no longer be changed after controller start-up. When the bit ALLOW_RESOLUTION_CHANGE is set, a check is first made whether the axis is interpolated, also when other critical parameters change. If the axis is currently in motion, this parameter update is rejected. |
P-AXIS-00036 | Access to cam signals | |
Description | The parameter defines the access to cam signals. | |
Parameter | lr_hw[i].cam_direct_access | |
Default value | 1 | |
drive types. | Conventional, Terminal, Lightbus, Profidrive | |
Remarks | This entry is not adopted when the axis parameter list is updated. Updates only become effective when the controller is rebooted. | |
P-AXIS-00038 | Level of cam signals | |
Description | The parameter defines the level of cam signals. | |
Parameter | lr_hw[i].cam_level | |
Data range | 0: 0-signal is active level. When the reference cam switch is actuated, the value of the control unit element pAC[axis_idx]^.addr^.McControlLr_Data.MCControlBoolUnit_ReferenceCam.X_Command on the HLI is FALSE (see [HLI]). 1: 1-signal is active level (default). When the reference cam switch is actuated, the value of the control unit element pAC[axis_idx]^.addr^.McControlLr_Data.MCControlBoolUnit_ReferenceCam.X_Command on the HLI is TRUE (see [HLI]). | |
Remarks |
P-AXIS-00064 | Slow / fast movement down from cam | |
Description | This parameter sets the velocity during reversion down from cam. | |
Parameter | kenngr.fast_from_cam | |
Data range | 0: Slow movement down from cam 1: Fast movement down from cam (default) | |
Axis types | T, R | |
Dimension | T: ---- | R: ---- |
drive types. | ---- | |
Remarks | For further hardware-specific parameters relating to homing with cam, see P-AXIS-00036 - P-AXIS-00039. | |
P-AXIS-00074 | Suppress homing for gantry slave axis | |
Description | This parameter can suppress the homing of gantry slave axes. When homing of the master axis is completed, the reference positions entered in the axis parameter lists of the slave axes are also adopted and monitoring of the gantry difference is started. | |
Parameter | kenngr.gantry_slave_no_homing | |
Remarks | This parameter is not supported in the case of spindle axes. | |
P-AXIS-00084 | Homing only with cam (without zero pulse) | |
Description | The homing position is detected by travel on the cam. | |
Parameter | kenngr.homing_without_zero_pulse | |
Data range | 0: Homing with zero pulse of rotary transducer (default value). 1: Homing without zero pulse of rotary transducer (low accuracy). | |
Dimension | T: ---- | R:---- |
P-AXIS-00152 | Position of the reference point | |
Description | If homing is completed, the value from the parameter P-AXIS-00152 is taken as the absolute position for the axis | |
Parameter | getriebe[i].pos_refpkt | |
Data type | SGN32 | |
Data range | swe_neg < pos_refpkt < swe_pos | |
Dimension | T: 0.1 µm | R,S: 0.0001 ° |
drive types. | Simulation, Conventional, Terminal, Lightbus, Profidrive, CANopen | |
Remarks |
P-AXIS-00156 | Homing without cam | |
Description | A changeover of homing strategy can be carried out so that homing is done without cam (e.g. only with zero pulse), i.e. without reverting. In this case the parameter P-AXIS-00156 should be set to TRUE. | |
Parameter | kenngr.ref_ohne_nocken | |
Remarks | To be assigned for analogue spindles only. If P-AXIS-00156 is assigned with 1 (TRUE), then it is imperative that P-AXIS-00157 is assigned with 1 (TRUE). | |
P-AXIS-00157 | Homing without reverting | |
Description | Via parameter P-AXIS-00157 a restriction of homing can occur that will prohibit any reverting. | |
Parameter | kenngr.ref_ohne_rev | |
Remarks | The speed during reversing is set with the parameter P-AXIS-00064 (fast_from_cam). By reverting, it is possible to repeatedly move to the reference cam at slow speed. To be assigned for analogue spindles only. P-AXIS-00157 must be assigned with 1 (TRUE) if P-AXIS-00156 is assigned with 1 (TRUE). | |
P-AXIS-00158 | Preferred direction of axis for homing | |
Description | The parameter P-AXIS-00158 specifies the direction of travel if the axis does not remain on a cam. The declaration of the signal level when the reference switch is actuated is given by the axis parameter P-AXIS-00038. | |
Parameter | kenngr.ref_richt | |
Data range | 0: Negative direction 1: Positive direction | |
drive types. | Simulation, Conventional, Terminal, Lightbus, Profidrive | |
Remarks | Positive direction signifies that the coordinate values increase. Negative direction signifies that the coordinate values decrease. | |
P-AXIS-00161 | Tool path up to zero pulse during homing simulation | |
Description | The parameter defines the tool path up to zero pulse during homing simulation. | |
Parameter | antr.simu.rpf_weg_bis_nip | |
Data range | MIN(SGN32) ≤ rpf_weg_bis_nip ≤ MAX(SGN32) | |
Dimension | T: 0.1µm | R,S: 0.0001 ° |
Default value | 10 | |
drive types. | Simulation | |
Remarks |
P-AXIS-00218 | Slow velocity for exact detection of reference position | |
Description | Not only the traverse downwards of cam but also the traverse on cam with homing takes place at the velocity P-AXIS-00218. | |
Parameter | getriebe[i].vb_reflow | |
Data range | 1 ≤ vb_reflow ≤ P-AXIS-00219 | |
Dimension | T: µm/s | R,S: 0.001°/s |
Default value | 16666 | |
Remarks |
P-AXIS-00219 | Fast velocity for detection of reference cam | |
Description | At start of homing, if the axis is not on the cam, then travel on the cam takes place at the velocity defined in P-AXIS-00219. | |
Parameter | getriebe[i].vb_refmax | |
Data range | P-AXIS-00218 ≤ vb_refmax ≤ P-AXIS-00212 | |
Default value | 83333 | |
Remarks |
P-AXIS-00294 | Selection of the homing method 'Evaluation of encoder overflow' | |
Description | This homing method is selected with the parameter P-AXIS-00294. To use this option, the parameter P-AXIS-00084 must be assigned the value 0. The number of bits used to detect encoder overflow has to be set in parameter P-AXIS-00355 . | |
Parameter | kenngr.homing_overflow_evaluation | |
Data range | 0: No evaluation of encoder overflow (default). 1: Evaluation of encoder overflow. | |
drive types. | Lightbus | |
Remarks | This homing method only leads to a repeatable homing position of the axis when encoder overflow occurs every time at the same mechanical position of the axis. This is true for example for resolver encoders. | |
P-AXIS-00299 | Homing type | ||||||
Description | There are two different homing methods: 1. NC-controlled homing With NC-controlled homing, the generation of command values and sequence control (evaluation of reference cams and zero pulses) are handled in the CNC. With drive-controlled homing, motion generation and the evaluation of cam signals and zero pulses are handled in the drive. The homing method can be set up for drives types (P-AXIS-00018) for which both homing methods are implemented with this parameter. | ||||||
Parameter | kenngr.homing.homing_type * (Note: see *-note below) | ||||||
Data type | STRING | ||||||
Data range | CNC_CONTROLLED: CNC-controlled homing is done. DRIVE_CONROLLED: Drive-controlled homing is done. DISABLED: This axis cannot be homed. The CNC generates the error message P-ERR-50685 or P-ERR-60313 if homing is commanded for the axis (e.g. G74). This setting is only intended for axes with an absolute measuring system (see P-AXIS-00014). IGNORE_ABS_POS: Axes with this setting are ignored during homing, i.e. the axis is not homed even if G74 <axis_name> is programmed. In this case the CNC generates no error message contrary to the setting DISABLED. The mode IGNORE_ABS_POS is only permitted for axis with an absolute position measuring system, meaning the parameter kenngr.abs_pos_gueltig (see P-AXIS-00014) must be set to 1. Otherwise, the CNC generates the error warning P-ERR-110584. | ||||||
Axis types | T, R, S | ||||||
Dimension | T: ---- | R,S: ---- | |||||
Default value | CNC_CONTROLLED | ||||||
Drive types | ---- | ||||||
Remarks | * alternative: kenngr.homing_type (old syntax) If the homing command G74 involves multiple axes with different homing type setting e.g. G74 X1 Y1 Z2, the axis with kenngr.homing_type != IGNORE_ABS_POS/ DISABLED will move and try to find the homing switch while there is no movement on the homing suppressed axes. Therefore it must be ensured that no collision can occur. If a homing type which is not supported by the drive type is set up, an error P-ERR-110384 is generated and default homing type is corrected. If this entry is not present in the parameter list, the default homing type is used according to the drive type: | ||||||
| Drive type | CNC_CONTROLLED | DRIVE_CONTROLLED | ||||
Simulation | X* |
SERCOS | X | X* | |||||
Terminal | X* |
Lightbus | X* |
RT-Ethernet | X* |
PROFIDRIVE | X* |
CANopen | X* | X | |||||
* Default homing type | |||||||
P-AXIS-00321 | Input interface for reference cam signal | ||
Description | In the default setting with CNC-controlled homing, the reference cam signal is read from the HLI [HLI]. For some drive types it is possible to use the drive digital inputs as reference cam input. In this case the appropriate input has to be configured in P-AXIS-00321. If this parameter is not set, the reference cam signal is read from the PLC interface. | ||
Parameter | antr.reference_cam_signal | ||
Data range | Dependent on the drive type the following different names for the digital inputs are possible:
Drive type SERCOS: PLC Read reference cam signal from HLI (default) RT_STATUS_BIT_1 Read reference cam signal from real time status bit 1 RT_STATUS_BIT_2 Read reference cam signal from real time status bit 2
Drive type CANopen: PLC Read reference cam signal from HLI (default) STATUS_DIG_INPUTS (*) Reference cam signal from object 0x60FD : Digital inputs
Default value | PLC | ||
drive types. | SERCOS, Lightbus,CANopen | ||
Remarks | Caution: It is only possible to use real-time status bits with NC-controlled homing, see also [CMS-A1].
If the drive digital inputs are used, they must also be parameterised using the drive manufacturer’s set-up tool. The transmission of the digital inputs in the cyclic telegram must also be configured. (*) For the transmission of the reference cam state, the object 0x60FD: Digital inputs must be configured (see DS402 drive profile). Otherwise, the error message with error code P-ERR-70292 is output. | ||
P-AXIS-00354 | Shifting of encoder overflow | |
Description | When homing with encoder overflow this parameter can shift the reference position. A positive value for P-AXIS-00354 will shift the reference position in the positive movement direction of the axis. | |
Parameter | antr.encoder_overflow_offset | |
Data range | application-specific | |
Dimension | T: 0.1 µm | R,S: 0.1 µm |
Remarks | The reference position can only be shifted within one encoder revolution. If larger values for P-AXIS-00354 are defined, the error message P-ERR-70310 is output and P-AXIS-00354 is corrected to 0. | |
P-AXIS-00355 | Number of bits for evaluation of encoder overflow | |
Description | When homing on encoder overflow, this parameter defines the number of bits of the drive's actual position value that are taken into account to detect encoder overflow. The actual position value of the drive system is AND-combined with the value (2P-AXIS-00355 -1) and the underflow or overflow of the resulting value is considered as encoder overflow. | |
Parameter | antr.encoder_bit_range | |
Data type | UNS08 | |
Data range | 1 … 31 | |
Remarks |
P-AXIS-00386 | Drive supported execution of the CNC based homing (SERCOS) | |
Description | By default CNC-controlled homing for SERCOS drives is only executed in the controller; the drive-internal positions are not altered. If the drive supports the SERCOS command S-0-146 (CNC-controlled homing), this parameter can enable the command S-0-146 for CNC-controlled homing. The advantage of this method is that, after homing is finished, the drive-internal positions are also referenced so that drive-internal software limit switches can be used, for example. The reference position used for homing is P-AXIS-00152. This value is transferred to the drive during homing | |
Parameter | antr.sercos.drive_supports_cnc_homing | |
drive types. | SERCOS | |
Remarks | This parameter is currently not supported for spindles. In addition to command S-0-146 the drive must support the following commands:
For further information please refer to the drive manufacturer's documentation.. | |
P-AXIS-00387 | Assignment of control and status bits for CNC based homing (SERCOS) | |
Description | To execute CNC-controlled homing with drive support, two control bits and two status bits are required. The real-time control and status bits can be used in the drive control and status word or alternatively as bits in the signal status and signal control word. | |
Parameter | antr.sercos.cnc_homing_rt_bit_layout | |
Data type | UNS16 | |
Data range | 1 ≤ cnc_homing_rt_bit_layout ≤ 16 | |
Remarks | When the status and control bits are transferred in the signal status and control words, they must be configured in the cyclic process data, otherwise the error message P-ERR-70295 is output. | |
Assign the values of P-AXIS-00387 to the possible bit assignments:
Value | Process data | Bit number | Meaning | Ident |
1 | Control word | Real-time bit 1 (S-0-301) | Homing enable | S-0-407 |
| Real-time bit 2 (S-0-303) | Position command value referenced | S-0-404 | |
Status word | Real-time bit 1 (S-0-305) | Position marker pulse detected | S-0-408 | |
| Real-time bit 2 (S-0-307) | Actual value referenced | S-0-403 | |
2 | Signal control word | Bit 0 (S-0-27[0]) | Homing enable | S-0-407 |
| Bit 1 (S-0-27[1]) | Position command value referenced | S-0-404 | |
Signal status word | Bit 0 (S-0-26[0]) | Position marker pulse detected | S-0-408 | |
| Bit 1 (S-0-26[1]) | Actual value referenced | S-0-403 | |
3 | Signal control word | Bit 1 (S-0-27[1]) | Homing enable | S-0-407 |
| Bit 2 (S-0-27[2]) | Position command value referenced | S-0-404 | |
Signal status word | Bit 1 (S-0-26[1]) | Position marker pulse detected | S-0-408 | |
| Bit 2 (S-0-26[2]) | Actual value referenced | S-0-403 | |
4 | Signal control word | Bit 2 (S-0-27[2]) | Homing enable | S-0-407 |
| Bit 3 (S-0-27[3]) | Position command value referenced | S-0-404 | |
Signal status word | Bit 2 (S-0-26[2]) | Position marker pulse detected | S-0-408 | |
| Bit 3 (S-0-26[3]) | Actual value referenced | S-0-403 | |
5 | Signal control word | Bit 3 (S-0-27[3]) | Homing enable | S-0-407 |
| Bit 4 (S-0-27[4]) | Position command value referenced | S-0-404 | |
Signal status word | Bit 3 (S-0-26[3]) | Position marker pulse detected | S-0-408 | |
| Bit 4 (S-0-26[4]) | Actual value referenced | S-0-403 | |
6 | Signal control word | Bit 4 (S-0-27[4]) | Homing enable | S-0-407 |
| Bit 5 (S-0-27[5]) | Position command value referenced | S-0-404 | |
Signal status word | Bit 4 (S-0-26[4]) | Position marker pulse detected | S-0-408 | |
| Bit 5 (S-0-26[5]) | Actual value referenced | S-0-403 | |
7 | Signal control word | Bit 5 (S-0-27[5]) | Homing enable | S-0-407 |
| Bit 6 (S-0-27[6]) | Position command value referenced | S-0-404 | |
Signal status word | Bit 5 (S-0-26[5]) | Position marker pulse detected | S-0-408 | |
| Bit 6 (S-0-26[6]) | Actual value referenced | S-0-403 | |
8 | Signal control word | Bit 6 (S-0-27[6]) | Homing enable | S-0-407 |
| Bit 7 (S-0-27[7]) | Position command value referenced | S-0-404 | |
Signal status word | Bit 6 (S-0-26[6]) | Position marker pulse detected | S-0-408 | |
| Bit 7 (S-0-26[7]) | Actual value referenced | S-0-403 | |
9 | Signal control word | Bit 7 (S-0-27[7]) | Homing enable | S-0-407 |
| Bit 8 (S-0-27[8]) | Position command value referenced | S-0-404 | |
Signal status word | Bit 7 (S-0-26[7]) | Position marker pulse detected | S-0-408 | |
| Bit 8 (S-0-26[8]) | Actual value referenced | S-0-403 | |
10 | Signal control word | Bit 8 (S-0-27[8]) | Homing enable | S-0-407 |
| Bit 9 (S-0-27[9]) | Position command value referenced | S-0-404 | |
Signal status word | Bit 8 (S-0-26[8]) | Position marker pulse detected | S-0-408 | |
| Bit 9 (S-0-26[9]) | Actual value referenced | S-0-403 | |
11 | Signal control word | Bit 9 (S-0-27[9]) | Homing enable | S-0-407 |
| Bit 10 (S-0-27[10]) | Position command value referenced | S-0-404 | |
Signal status word | Bit 9 (S-0-26[9]) | Position marker pulse detected | S-0-408 | |
| Bit 10 (S-0-26[10]) | Actual value referenced | S-0-403 | |
12 | Signal control word | Bit 10 (S-0-27[10]) | Homing enable | S-0-407 |
| Bit 11 (S-0-27[11]) | Position command value referenced | S-0-404 | |
Signal status word | Bit 10 (S-0-26[10]) | Position marker pulse detected | S-0-408 | |
| Bit 11 (S-0-26[11]) | Actual value referenced | S-0-403 | |
13 | Signal control word | Bit 11 (S-0-27[11]) | Homing enable | S-0-407 |
| Bit 12 (S-0-27[1]2) | Position command value referenced | S-0-404 | |
Signal status word | Bit 11 (S-0-26[11]) | Position marker pulse detected | S-0-408 | |
| Bit 12 (S-0-26[1]2) | Actual value referenced | S-0-403 | |
14 | Signal control word | Bit 12 (S-0-27[12]) | Homing enable | S-0-407 |
| Bit 13 (S-0-27[13]) | Position command value referenced | S-0-404 | |
Signal status word | Bit 12 (S-0-26[12]) | Position marker pulse detected | S-0-408 | |
| Bit 13 (S-0-26[13]) | Actual value referenced | S-0-403 | |
15 | Signal control word | Bit 13 (S-0-27[13]) | Homing enable | S-0-407 |
| Bit 14 (S-0-27[1]4) | Position command value referenced | S-0-404 | |
Signal status word | Bit 13 (S-0-26[13]) | Position marker pulse detected | S-0-408 | |
| Bit 14 (S-0-26[14]) | Actual value referenced | S-0-403 | |
16 | Signal control word | Bit 14 (S-0-27[14]) | Homing enable | S-0-407 |
| Bit 15 (S-0-27[15]) | Position command value referenced | S-0-404 | |
Signal status word | Bit 14 (S-0-26[14]) | Position marker pulse detected | S-0-408 | |
| Bit 15 (S-0-26[15]) | Actual value referenced | S-0-403 |
P-AXIS-00388 | Encoder, used for CNC controlled homing (SERCOS) | |
Description | Some drive types support the use of multiple encoders (motor encoder and external encoder). This parameter defines which encoder is used for homing. | |
Parameter | antr.cnc_homing_encoder | |
Data type | SGN16 | |
Data range | 0: Value is not configured. If P-AXIS-00386 is set to 1, set this parameter to a valid value (0, 1, 2). 1: The encoder used for homing is determined automatically, e.g. for SERCOS drives, by reading drive parameter S-0-147. 2: Motor encoder 3: External encoder | |
Remarks | At the moment this parameter is supported only for SERCOS. With SERCOS drives, if the encoder set in S-0-147 does not fit to the value set in P-AXIS-00388, the error message error message P-ERR-70453 is output. This value is only effective when P-AXIS-00386 has the value 1. | |
P-AXIS-00412 | Maximum distance during homing | |
Description | This parameter defines a maximum distance for homing for spindles and rotary axes. If the maximum permissible homing distance is exceeded, homing is aborted and error message P-ERR-70394 is output. It achieves that homing is aborted if, for example, the reference cam is not found due to a wiring error. This parameter works only for spindles and rotary axes, see P-AXIS-00018. If this parameter is set for linear axes to a value unequal to zero, the error message P-ERR-110545 is output and the parameter is corrected to 0. A value of 0 disables distance monitoring during homing. | |
Parameter | kenngr.distc.a_max | |
Data range | 0 ≤ homing_max_movement_dist ≤ MAX(UNS32) | |
Axis types | R, S | |
Dimension |
| R,S: 0.0001 ° |
Remarks | This parameter has to be set to a value which is at least equal to the modulo range of the axis in order to complete homing successfully. | |
P-AXIS-00425 | Bit number of signal 'Drive is referenced' during reference monitoring | |
Description | In this parameter enter the number of the bit which is used for transmission of the signal 'Drive is referenced' from the drive to the controller during active reference monitoring. The least significant bit has bit number 0. The maximum value depends on the length of the configured telegram element which is used for transmission. | |
Length of telegram element | Max. bit number | |
-1 | No reference monitoring | |
2 | 15 | |
4 | 31 | |
Setting the parameter to an invalid bit number leads to the output of error message P-ERR-110549. | ||
Parameter | antr.reference_check.bit_nr | |
Data range | 0 ≤ bit_nr ≤ Max. bit number | |
Default value | -1 | |
Remarks | This parameter is supported for SERCOS drive types only. | |
P-AXIS-00426 | Element name of signal 'Drive is referenced' during reference monitoring | |
Description | In this parameter enter the name of the element of the cyclic input process data which is used for transmission of the signal 'Drive is referenced' from the drive. When the set-up value of P-AXIS-00426 is not found within the cyclic process, the error message P-ERR-70401 is output. | |
Parameter | antr.reference_check.element_name | |
Data range | <Empty string>: Reference monitoring is disabled S-0-0135: When the SERCOS state word is used for transmission of the reference signal, the parameter has to be set to 'S-0-0135'… <Telegram_element_Name>: ...or, alternatively, the name of a telegram element configured in the cyclic process data. | |
Default value | * | |
Drive types | SERCOS | |
Remarks | * Note: The default value of variables is a blank string. Reference monitoring is activated by assigning a value to this parameter. When reference monitoring is activated, the parameter P-AXIS-00425 must also be assigned a valid value. At the moment, this parameter is supported for drive type SERCOS only. Changing this parameter by a list update is not possible (P-ERR-110550). | |
P-AXIS-00494 | Delayed activation of zero pulse logic | |
Description | For CNC-controlled homing (see P-AXIS-00299) the parameter delays the activation of the zero pulse logic after the actuation of the reference switch. This can be useful if the reference cam and the zero pulse are situated closely together and the detection of the zero pulse is therefore not reliably possible. In this case the next or the next but one zero pulse after the reference cam could be detected depending on the actuation speed of the reference cam. | |
Parameter | kenngr.shift_offset_zero_pulse_activation | |
Data range | 0 ≤ shift_offset_zero_pulse_activation ≤ MAX_UNS32 | |
drive types. | Conventional, SERCOS, Terminal, Lightbus, Profidrive, CANopen | |
Remarks |