Axis control commands

Feed rate enable, axis

Description

Axis-specific feed rate enable

The feed rate enable must be set for all axes to be moved. If this is not the case, no path motion occurs.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Special features

SERCOS drives

With SERCOS drives, the datum is derived from bit 13 of the control word.

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.lr_mc_control.release_feedhold

Commanded, requested and return values

ST element

.command_w

.request_r

Data type

BOOL

Value range

[TRUE = drive enable,

transition TRUE → FALSE: The drive is shut down in compliance with the acceleration parameters.

FALSE = Drive STOP]

Return value

ST element

.state_r

Data type

BOOL

Value range

[TRUE = drive enable, FALSE = drive STOP]

Redirection

ST element

.enable_w

Feedhold ON/OFF, axis

Description

Axis-specific feedhold

The axis-specific feedhold on an axis acts as follows:

  • Axis interpolated and moved in path compound:
    • Stop all axes in path compound immediately
  • Axis interpolated and stopped in path compound:
    • Remaining axes in path compound continue to move,
  • Axis interpolated and stopped in path compound, only moves in the next block:
    • Remaining axes in path compound move to current block end and then stop.
  • Axis interpolated as single axis (manual mode, independent axis, SAI axis, spindle):
    • Only this axis is stopped.

Otherwise, the global feedhold of the channel acts on al axes except for spindles. The operation mode of the global and axis-specific feedhold can be parameterised for these axes (P-AXIS-00529, P-AXIS-00540).

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.ipo_mc_control.feedhold

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

[TRUE = feedhold on, FALSE = feedhold off]

Redirection

ST element

.enable_w

Directional feedhold, axis

Description

Axis-specific directional feedhold

A directional feedhold can be set for all moving axes If an axis command is in the block direction, the axis-specific feedhold is set.

An axis-specific directional feedhold acts on an axis in exactly the same way as an axis-specific feedhold.

  • Axis interpolated and moved in path compound:
    • Stop all axes in path compound immediately
  • Axis interpolated and stopped in path compound:
    • Remaining axes in path compound continue to move,
  • Axis interpolated and stopped in path compound, only moves in the next block:
    • Remaining axes in path compound move to current block end and then stop.
  • Axis interpolated as single axis (manual mode, independent axis, SAI axis, spindle):
    • Only this axis is stopped.

The directional and normal axis-specific feedholds can be superimposed. Otherwise, the global feedhold of the channel acts on al axes except for spindles. The operation mode of the global and axis-specific feedhold can be parameterised for these axes (P-AXIS-00529, P-AXIS-00540).

Data type

MC_CONTROL_UNS08_UNIT, see description of Control unit

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.ipo_mc_control.directional_feedhold

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

USINT

Value range

Value

PLC constant

Meaning

0

HLI_DIRECTIONAL_FEEDHOLD_NO_FEEDHOLD

The axis is not blocked in any motion direction.

1

HLI_DIRECTIONAL_FEEDHOLD_POS

The axis is blocked in the positive motion direction.

2

HLI_DIRECTIONAL_FEEDHOLD_NEG

The axis is blocked in the negative motion direction.

3

HLI_DIRECTIONAL_FEEDHOLD_POS_NEG

The axis is blocked in the positive and negative motion directions.

Redirection

ST element

.enable_w

Special feature

The axis drive is shut down in compliance with the acceleration parameters. This means that the axis moves a short distance in the blocked direction before stopping.

The feedhold always acts on the complete current block, This means that a block can be blocked even if the current direction of axis motion is not pointing in the blocked direction.

Available as of V3.1.3079.26

Examples:

1. Example of a circle:
A full circle is programmed in the XY plane. A directional feedhold in negative direction is set for the X axis. Although the X axis first moves in the blocked direction after 180°, it does move through the entire circle since both motion directions are contained in the block.

2. Example of polynomial contouring:
With polynomial contouring, splitting the contouring movement into several blocks can cause the axis compound to stop before the actual motion in the blocked direction.

3. Special case of a spindle:
With a superimposed spindle motion, the direction of spindle motion is determined by command values. This causes the axis to move a short distance in the blocked direction from standstill before it stops.

Feedhold watchdog

Description

This control unit is the interface of a watchdog which stops the CNC interpolator by activating a feedhold if the PLC fails. If the axis for which the watchdog was triggered is a member of an axis group and is currently commanded to be in motion, all other axes moved by this command also stop.

If this control unit is enabled, the PLC must set the element command_w to TRUE in every PLC cycle. The NC kernel than resets the command back to FALSE.

To enable this control unit function, the axis parameter enable_feed_enable (P-AXIS-00313) must be set in many versions of the NC kernel. In other version the function of this control unit is still available.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.ipo_mc_control.enable_feed_wdg

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

[TRUE = signals that PLC is invoked cyclically and executes its function, FALSE]

Redirection

ST element

.enable_w

Feed override, axis

Description

Axis-specific feed override

The axis-specific feed override permits weighting the axis path velocity with an additional factor. The axis-specific feed override only acts on an axis if the axis is currently moved in manual mode or as an independent axis and but in a path compound. Otherwise the global override of the channel acts on the axis.

The axis-specific feed override also acts on single axes and spindles.

With spindles the feed override also acts on the velocity acknowledgement of programmed M3/ M4 or MC_MoveVelocity commands.

Velocity acknowledgement occurs when the weighted feed rate is reached and in extreme cases when the feed rate is 0.

(see lr_state.rev_erreicht_r)

Data type

MC_CONTROL_UNS16_UNIT, see description of Control unit

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.ipo_mc_control.override

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

UINT

Unit

0.1%

Value range

[0, P-AXIS-00109]

The parameter P-AXIS-00109 is an axis-specific parameter. The value is typically 1000.

Redirection

ST element

.enable_w

Feed override valid, axis

Description

Axis-specific feed override valid.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.ipo_mc_control.override_valid

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

[TRUE = axis-specific feed override valid, FALSE]

Redirection

ST element

.enable_w

Drive ON

Description

Drive ON

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Special features

SERCOS drives

With SERCOS drives, the datum is derived from bit 15 of the control word.

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.lr_mc_control.drive_on

Commanded and requested values

ST element

.command_w

.request_r

Data type

BOOL

Value range

[TRUE = drive ON,

transition TRUE → FALSE: The drive is shut down in the best possible manner.

FALSE = Drive OFF]

Return value

ST element

.state_r

Data type

BOOL

Value range

[TRUE = drive ON, FALSE = drive OFF]

Redirection

ST element

.enable_w

Controller enable

Description

Control unit enable ↔ axis-specific torque connection.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Special features

SERCOS drives

With SERCOS drives, the datum is derived from bit 14 of the control word.

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.lr_mc_control.torque_permission

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

[TRUE = torque connection, FALSE = drive is torque-free]

Redirection

ST element

.enable_w

The diagram below shows the relationship between HLI control units and the SERCOS control word or the SERCOS status word for SERCOS drives.

Axis control commands 1:
Interaction of control units and SERCOS control or status words

Reference cam

Description

Reference cam signal when homing.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

 

Special features

When this signal is commanded, it only acts if the parameter lr_hw[i].cam_direct_access = 0 (P-AXIS-00036) is set in the axis machine data record of the associated axis.

When the characteristic value lr_hw[i].cam_level (P-AXIS-00038) is used in the axis machine data record, the action of this command can be set from high-active to low-active.

The default action is described below.

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.lr_mc_control.reference_cam

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

[TRUE = reference cam switched, FALSE = reference cam not switched]

Redirection

ST element

.enable_w

Reduced velocity, axis

Description

When this signal is set, the axis velocity in G00 and G01 is reduced to the values defined in the axis parameters P-AXIS-00214 or P-AXIS-00155.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Special features

If this axis is in a channel, the limits of the other axes participating in the motion are also considered. The effective value for reduced velocity is determined so that none of the axes participating in the motion overshoots its configured limit. The response is then identical to the command via a channel.

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.ipo_mc_control.reduced_speed

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

[TRUE = reduced velocity active, FALSE = reduced velocity not active]

Redirection

ST element

.enable_w

Reduced velocity in zone 1, axis

Description

By setting this signal, the axis velocity is limited to the velocity defined in the axis parameter P-AXIS-00030 when the axis is located within the range defined by the parameters P-AXIS-00085 and P-AXIS-00093. If necessary the axis is decelerated after entering the zone.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Special features

If the axis is in a channel, the limits of the other axes participating in the motion and also located within their configured zone are considered.

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAX[axis_idx]^.ipo_mc_control.reduced_speed_zone

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

[TRUE = reduced velocity in zone 1 active, FALSE = reduced velocity in zone 1 not active]

Redirection

ST element

.enable_w

Reduced velocity in zone 2, axis

Description

By setting this signal, the axis velocity is limited to the velocity defined in the axis parameter P-AXIS-00030 when the axis is located within the range defined by the parameters P-AXIS-00097 and P-AXIS-00105. If necessary the axis is decelerated after entering the zone.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Special features

If the axis is in a channel, the limits of the other axes participating in the motion and also located within their configured zone are considered.

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAX[axis_idx]^.ipo_mc_control.reduced_speed_2_zone

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

[TRUE = reduced velocity in zone 2 active, FALSE = reduced velocity in zone 2 not active]

Redirection

ST element

.enable_w

Suppress read-in enable

Description

Suppress read-in enable

When the read-in enable (setting NoEfg) is cleared, the interpolator does not read any new previously decoded NC motion information, i.e. the motion is stopped at the end of the current commands in the interpolator.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.ipo_mc_control.no_efg

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

[TRUE = no read-in enable, FALSE = read-in enable]

Redirection

ST element

.enable_w

Machining simulation, axis

Description

Activates and deactivates an axis-specific machining simulation.

During machining simulation, all axis-specific technology commands of the NC program are no longer output to the PLC but are acknowledged internally.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.ipo_mc_control.machining_simulation

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

[TRUE = machining simulation active, FALSE = machining simulation inactive]

Redirection

ST element

.enable_w

Ignore minimum tool velocity

Description

If a value for minimum tool velocity is configured at tool change, the NC kernel monitors that this limit is not undershot by specifying an override.

This control unit can switch this response off and the override acts on the axis as specified.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Special features

Control unit is only effective if the axis is a spindle.

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.ipo_mc_control.ignore_vb_min_tool

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

[TRUE = undershooting minimum tool velocity permitted, FALSE]

Redirection

ST element

.enable_w

OTC offset

Description

When this wear offset is set, wear in the direction of this axis can be compensated.

When the SURF_NORM_ORI mode is used (wear in the direction of the surface normal), the offset value must be assigned in the third axis.

Data type

MC_CONTROL_SGN32_UNIT, see description of Control unit

Special features

The wear offset is distributed by the CNC over several cycles.

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.ipo_mc_control.otc_offset

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

DINT

Unit

0.1 µm

Value range

[-P-TOOL-00031, P-TOOL-00031]

Redirection

ST element

.enable_w

Move back manual mode offset

Description

If manual mode is active in the channel and if the commanded axis fails to move, the axis is moved by this command so that afterwards manual mode offset is 0.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Special features

A rising edge (FALSE → TRUE) at command_w initiates the process. The signal is ignored if a manual mode motion is still active or manual mode offset is already 0.

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.ipo_mc_control.manual_mv_back_to_start

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

rising edge (FALSE → TRUE) triggers backward motion

Redirection

ST element

.enable_w

Stop the motion “Move back manual mode offset”

Description

The motion that was started by the control unit command “Move back manual mode offset” is stopped by the control unit with this command.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Special features

A rising edge (FALSE → TRUE) initiates the command. Up to final axis standstill, the data item Axis-specific interpolator, state shows that the stop process is active with the HLI_AX_MAN_MV_BACK_WAIT_STOP bit.

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.ipo_mc_control.manual_mv_back_stop

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

[TRUE = rising edge stops the motion, FALSE]

Redirection

ST element

.enable_w

Tracking mode

Description

The axis is set to tracking mode, i.e. the command value is set identical to the actual value read in. Setting the command and actual values equal is executed and command_w = TRUE.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Special features

By setting the command and actual value equal, the current position lag is = 0. This may result in an external force (weight of the axis) slowly changing the axis position (drift).

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.lr_mc_control.follow_up

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

[TRUE = control loop open, FALSE]

Redirection

ST element

.enable_w

Run out gantry difference

Description

If the axis is a gantry slave axis and both the master and slave are referenced, the gantry difference is run out.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.lr_mc_control.gantry_on

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

[TRUE = gantry difference runout permitted, FALSE]

Redirection

ST element

.enable_w

Accept reference position

Description

Accept the reference position and mark the axis as referenced on a rising edge of this control unit. Depending on the value of the parameter P-AXIS-00278 the actual axis position is set to the following value:

P-AXIS-00278

Reference position of the axis

ABSOLUT

Value of P-AXIS-00152

OFFSET

Encoder position of the drive + P-AXIS-00279

PLC

Value in the refpos_position control unit.

PLC_OFFSET

Encoder position of the drive + value in the refpos_position control unit.

The state_r variable indicates whether the reference position was set manually and the coordinate system was shifted as a result. The manual setting can be cleared by CNC-controlled homing (G74).

The reference position can also be set manually for an axis with absolute measuring system.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Special features

Edge evaluation: The function is triggered on the rising edge at the command input.

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.lr_mc_control.set_reference_position

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

[TRUE, FALSE]

Redirection

ST element

.enable_w

Reference position to be set

Description

If the parameter P-AXIS-00278 in the axis parameter list is set to the value “PLC” or “PLC_OFFSET”, the value of this control unit is used to calculate the setting position when acceptance of the reference position is triggered via the HLI (see also the control unit set_reference_position).

In this case, there are options on how to use the value of this control unit. See below:

P-AXIS-00278

Reference position of the axis

PLC

Value in this control unit.

PLC_OFFSET

Encoder position of the drive + value in this control unit.

Data type

MC_CONTROL_SGN32_UNIT, see description of Control unit

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.lr_mc_control.refpos_position

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

DINT

Unit

0.1 µm or 10-4°

Value range

[MIN_SGN32, MAX_SGN32]

Redirection

ST element

.enable_w

Clear referencing

Description

If an axis was homed by setting the reference position or by G74, this state can be cleared by using the actual control unit.

If an axis has an absolute measuring system, the axis is subsequently considered as not referenced (it can by referenced again by a G74).

This switches off the software limit switches temporarily, for example.

Any offset activated by the control unit “Setting the reference position” is not cleared.

The variable state_r indicates whether the axis is currently not referenced.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Special features

As long as the command (command_w) of the control unit is TRUE, the axis is regarded as not referenced and can also be marked as referenced by triggering acceptance of the reference position (see also the control unit set_reference_position).

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.lr_mc_control.clear_reference_position

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

[TRUE, FALSE]

Redirection

ST element

.enable_w

Disable position lag monitoring

Description

Suppress / disable position lag monitoring.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.lr_mc_control.disable_pos_lag_mon

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

[TRUE, FALSE]

Redirection

ST element

.enable_w

Probing signal

Description

This control unit can transfer the probing signal. When this control unit is used, set the entry kenngr.measure.signal (P-AXIS-00516) to “PLC” or “PLC_TIMESTAMP” in the parameter list of the associated axis.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Special features

Edge evaluation: Use the edge parameterised in the axis parameter list in the entry kenngr.mess_neg_flanke (P-AXIS-00518) to accept the measured value.

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.lr_mc_control.probing_signal

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

[TRUE, FALSE]

Redirection

ST element

.enable_w

Measured value, axis

Description

If the axis parameter P-AXIS-00257 or the NC command #MEAS […SIGNAL=PLC] changed over the probing signal source to the probing_signal control unit, activate this control unit in addition to the to transfer the measured value via the HLI.

Data type

MC_CONTROL_SGN32_UNIT, see description of Control unit

Special features

If this control unit is not activated, the actual position of the axis on the rising edge of command_w of the probing_signal control unit is used as the measured value.

The value assigned to the element command_w of the probing_position control unit is transferred to the decoder without any changes and is then available for further calculations.

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.lr_mc_control.probing_position

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

DINT

Unit

0.1 µm or 10-4 °

Value range

[MIN_SGN32, MAX_SGN32]

Redirection

ST element

.enable_w

Deactivate an axis (park)

Description

Axis-specific deactivation of an axis.

With a deactivated axis the following actions are not executed by the NC kernel:

Error monitoring: errors signalled by the drive are not indicated by the CNC.

HLI control bits are not transferred to the drive.

A CNC reset does not trigger a drive reset.

If you try to move a parked axis, the error message P-ERR-70265 is output.

No actions are executed in the drive.

Data type

MC_CONTROL_BOOL_UNIT, see description of Control unit

Special features

PROFIDRIVE drives:

When this control unit is active, the bit 0x80 in set in the control word 2 (STW2).

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.lr_mc_control.deactivate_axis

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

BOOL

Value range

[TRUE = axis is deactivated,

FALSE = axis is active (default mode)]

Redirection

ST element

.enable_w

Timestamp

Description

This control unit transfers the timestamp of a digital input terminal to the CNC via the HLI.

Data type

MC_CONTROL_SGN64_UNIT, see description of Control unit

Access

PLC reads request_r + state_r and writes command_w + enable_w

ST path

gpAx[axis_idx]^.lr_mc_control.timestamp

Commanded, requested and return values

ST element

.command_w

.request_r

.state_r

Data type

LINT

Unit

[ns]

Value range

[MIN_SGN64, MAX_SGN64]

Redirection

ST element

.enable_w

Special features

If the timestamp is used for the function “Measure with distributed clocks timestamp”, the probing_signal control unit must also be enabled.

Available as of CNC Build V3.01.3079.28