Channel parameters
P-CHAN-00001
Default effect of acceleration weighting at program start
Default value to set acceleration weighting.
Parameter
prog_start.slope.acceleration
Data type
SGN16
Data range
0: Weighting acts on all accelerations (default)
1: Weighting acts on aaccel
2: Weighting acts on adecel
Dimension
Default value
0
Remarks
P-CHAN-00002
Path acceleration limit
If no change is made to the parameter values by NC programming, this value limits path acceleration after it is activated in the NC program.
Parameter
vector.acceleration
Data type
REAL64
Data range
0 ... Maximum acceleration, application-specific
Dimension
mm/min² or mm/s² *
Default value
100000000
Remarks
* The dimension used depends on P-CHAN-00351.
Parameterisation example:
vector.acceleration 1800000
The specified default value is in mm/min².
P-CHAN-00009
Reduction of tangential transition velocity between circles
Tangential block transitions between circles with different radii and circles and linear blocks and vice versa lead to a jerk depending on circle radius. A jerk produced by activating this function can be reduced in order to reduce the excitation of vibrations on the machine when non-linear velocity profiles are active. At tangential block transitions, the speed is reduced dependent on the permissible jerk. The calculation is based on axis-specific jerk parameters for non-linear speed profiles (see also [AXIS] documentation).
On the other hand, the reduction of speed at tangential block transitions is not acceptable with specific machining technologies since the machining process has a very sensitive reaction to a reduction in velocity.
Parameter
corr_v_trans_jerk
Data type
BOOLEAN
Data range
0: No inclusion of jerk at tangential block transitions.
1: Inclusion of jerk at tangential block transitions.
Dimension
Default value
0
Remarks
P-CHAN-00056
Limiting maximum channel override
This parameter limits the maximum override in the channel.
Parameter
max_vb_override
Data type
UNS16
Data range
0 ≤ max_vb_override ≤ 2000 (maximum value of channel override, application-specific)
Dimension
0.1%
Default value
1000
Remarks
Parameterisation example: The limit of the maximum channel override is 150%.
max_vb_override     1500
P-CHAN-00071
Default acceleration profile at program start
Default value for the selected acceleration profile type with path motions and oscillating axis motions.
Parameter
prog_start.slope.profile
Data type
SGN16
Data range
0: Step-shaped acceleration profile, (default, linear profile)
1: Trapezoidal acceleration profile
2: Sine-square acceleration profile
3: Trapezoidal HSC acceleration profile (across blocks)
Dimension
Default value
0
Remarks
The acceleration profile and the associated acceleration and ramp time weighting can be programmed in the NC program with the #SLOPE [TYPE..] command [PROG].
The maximum of the weighted ramp times P-AXIS-00195 is always effective with the trapezoidal HSC acceleration profile. P-AXIS-00198.
For every independent axis, the acceleration profile can also be programmed specifically in the NC command with the key word SLOPE_TYPE [PROG].
P-CHAN-00073
Default effect of ramp time weighting at program start
Default value for setting ramp time weighting. This value is only relevant for trapezoidal or sine-square acceleration profiles.
Parameter
prog_start.slope.ramp_time
Data type
SGN16
Data range
0: Weighting affects all ramp times (default)
1: Weighting acts on TR,accel,inc
2: Weighting acts on TR,accel,red
3: Weighting acts on TR,decel,inc
4: Weighting acts on TR,decel,red
Dimension
Default value
0
Remarks
P-CHAN-00078
Resolution of rotary axes
This value represents the conversion factor between the path motions or the positions programmed in the NC program and the internal representation for position values with rotary axes.
Parameter
rund_aufloes
Data type
REAL64
Data range
0 < rund_aufloes < MAX(REAL64)
Dimension
Default value
10000
Remarks
Not to be confused with the resolution of the drive encoder P-AXIS-00234/P-AXIS-00235.
As of CNC Build V2.11.2026.09 P-CHAN-00315 replaces the parameters lin_aufloes, rund_aufloes and spind_aufloes (P-CHAN-00034, P-CHAN-00035 and P-CHAN-00036). It is recommended to use only P-CHAN-00315 as of this CNC Build.
Parameterisation example: All rotary axes are specified in the dimension 'Degree' [°] in the NC program.
rund_aufloes     10000
P-CHAN-00090
Path velocity limit
If no change is made to the parameter values by NC programming, this value limits path velocity after it is activated in the NC program.
Parameter
vector.velocity
Data type
REAL64
Data range
Dimension
mm/min
Default value
2000000000
Remarks
vector.velocity 1500
P-CHAN-00090
Path velocity limit
Parameter
vector.velocity
Data type
REAL64
Data range
0 ... Maximum acceleration, application-specific SLOPE_VB_MAX
Dimension
mm/min
Default value
0
Remarks
vector.deceleration     2000000
P-CHAN-00097
Valid deceleration ramp at FEEDHOLD
This parameter defines the deceleration ramp used when FEEDHOLD is active.
When P-CHAN-00097 is set, the parameterised delay is dependent on the slope used.
With a linear slope, the delay is defined by P-AXIS-00024; if the slop is non-linear, it is defined by P-AXIS-00053 and P-AXIS-00081.
Parameter
use_drive_curr_limit
Data type
BOOLEAN
Data range
0: When FEEDHOLD is set, deceleration takes place using the currently valid deceleration rate.
1: When FEEDHOLD is set, deceleration takes place using the parameterised delay depending on the slope used. If these two parameters are not set, deceleration takes place at the currently valid deceleration rate (P-AXIS-00004).
Dimension
Default value
0
Remarks
P-CHAN-00110
Including jerk in the polynomial
The curvature of the programmed contour (polynomial) results in an axis jerk. If the value is 1 or 3, this jerk is monitored together with the axis-specific dynamic parameters of the geometrical ramp time (P-AXIS-00199).
In addition, an active kinematic compensation movement is included when value 3 is in the polynomial.
If the value is 2, the ramp times P-AXIS-00195… P-AXIS-00198 are used for jerk monitoring.
If a relatively small maximum jerk is specified in the axis, the velocity on the path is reduced accordingly. If this reduction is not wanted for technological reasons, these parameters suppress jerk monitoring in polynomials.
Parameter
check_jerk_on_poly_path
Data type
UNS32
Data range
0: No jerk limiting in the polynomial.
1: Jerk limiting in the polynomial based on P-AXIS-00199 (default).
2: Jerk limiting in the polynomial based on the maximum of P-AXIS-00195, P-AXIS-00196, P-AXIS-00197, P-AXIS-00198.
3: As for value 1 and in addition polynomials in combination with kinematic compensation movement.
Dimension
Default value
1
Remarks
P-CHAN-00195
Command speed of a linear axis in manual operation mode
This parameter defines the Cartesian dynamics of a manual mode axis for an X, Y, Z movement.
Parameter
man_mode.vector_limit.v_max_pos
Data type
UNS32
Data range
1 < v_max_pos < MAX(UNS32)
Dimension
µm/s or 0.001°/s
Default value
0
Remarks
man_mode.vector_limit.v_max_pos     100000 [µm/s]
P-CHAN-00196
Command acceleration of a linear axis in manual operation mode
Parameter
man_mode.vector_limit.a_max_pos
Data type
UNS32
Data range
1 < a_max_pos < MAX(UNS32)
Dimension
mm/s² or °/s²
Default value
0
Remarks
man_mode.vector_limit.a_max_pos     1000 [mm/s²]
P-CHAN-00197
Ramp time of a linear axis in manual operation mode
Parameter
man_mode.vector_limit.tr_pos
Data type
UNS32
Data range
1 < tr_pos < MAX(UNS32)
Dimension
µs
Default value
0
Remarks
man_mode.vector_limit.tr_pos     100000 [µs]
P-CHAN-00198
Command speed of an orientation axis in manual mode
This parameter defines the Cartesian dynamics of a manual mode axis with an A, B, C movement.
Parameter
man_mode.vector_limit.v_max_ori
Data type
UNS32
Data range
1 < v_max_ori < MAX(UNS32)
Dimension
µm/s or 0.001°/s
Default value
0
Remarks
man_mode.vector_limit.v_max_ori      50000 [µm/s]
P-CHAN-00199
Command acceleration of an orientation axis in manual mode
Parameter
man_mode.vector_limit.a_max_ori
Data type
UNS32
Data range
1 < a_max_ori < MAX(UNS32)
Dimension
mm/s² or °/s²
Default value
0
Remarks
man_mode.vector_limit.a_max_ori     500 [mm/s²]
P-CHAN-00200
Ramp time of an orientation axis in manual mode
Parameter
man_mode.vector_limit.tr_ori
Data type
UNS32
Data range
1 < tr_ori < MAX(UNS32)
Dimension
µs
Default value
0
Remarks
man_mode.vector_limit.tr_ori     100000 [µs]
P-CHAN-00208
Path deceleration limit
If no change is made to the parameter values by NC programming, this value limits path deceleration after it is activated in the NC program.
Parameter
vector.deceleration
Data type
REAL64
Data range
0 ... Maximum deceleration, application-specific
Dimension
mm/min² or mm/s² *
Default value
100000000
Remarks
P-CHAN-00351
Unit for path acceleration and path deceleration
This channel parameter switches over the unit of acceleration/deceleration in the #VECTOR LIMIT command. The default unit is mm/min² or mm/min3. This unit is switched over to mm/s² by setting the parameters to MM_S2. The arguments ACC, DEC, RADIAL_ACC and RADIAL_JERK in the NC command are then interpreted in the unit mm/s² or mm/s3.
Parameter
vector.acc_dec_unit
Data type
STRING
Data range
MM_M2: Unit is mm/min2 or mm/min3
MM_S2: Unit is mm/sec2 or mm/sec3
Dimension
Default value
MM_M2
Remarks
This parameter cannot be set using the NC command #VECTOR LIMIT.
vector.acc_dec_unit MM_S2