Axis parameters
P-AXIS-00328 | Enabling of distance control (spindle with touch probe) | ||
Description | The distance control for a spindle with touch probe is enabled with this parameter. The activation is done by a special command in the NC program [PROG//section 'Distance controlled spindles']. | ||
Parameter | lr_param.distance_control_on | ||
Data type | BOOLEAN | ||
Data range | 0/1 | ||
Axis types | T, R | ||
Dimension | T: ---- | R: ---- | |
Default value | 0 | ||
drive types. | SERCOS, Profidrive, CANopen | ||
Remarks |
| ||
P-AXIS-00413 | Filtering of sensor values | |
Description | Sensor values may be noisy. To keep excitation of the machine low, the setpoints for distance control can be smoothed by a filter. The parameter specified the number of values that are used for filtering. | |
Parameter | kenngr.dist_ctrl[i].n_cycles (where i=0) | |
Data type | SGN32 | |
Data range | 0 ≤ n_cycles < 100 | |
Axis types | T, R | |
Dimension | T: ---- | R: ---- |
Default value | 4 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.n_cycles continues to be available. | |
P-AXIS-00414 | Maximum position offset | |
Description | The correction value of the axis that was calculated via distance control may not exceed this machine data item. An error message is issued if this value is exceeded. The correction value is limited. | |
Parameter | kenngr.dist_ctrl[i].max_deviation (where i=0) | |
Data type | SGN32 | |
Data range | 0 ≤ max_deviation < MAX(SGN32) | |
Axis types | T, R | |
Dimension | T: 0.1µm | R: 0.0001 ° |
Default value | 50000 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.max_deviation continues to be available. | |
P-AXIS-00415 | Maximum velocity | |
Description | The parameter defines the maximum velocity at which a position offset is cleared. | |
Parameter | kenngr.dist_ctrl[i].v_max (where i=0) | |
Data type | SGN32 | |
Data range | 0 ≤ v_max < MAX(SGN32) | |
Axis types | T, R | |
Dimension | T: 0.001 mm/s | R: 0,001°/s |
Default value | 5000 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.v_max continues to be available. | |
P-AXIS-00416 | Maximum acceleration | |
Description | The parameter defines the maximum acceleration at which a position offset is executed. Correction of the distance is limited dynamically with respect to maximum acceleration to limit the resulting excitation. If no acceleration is specified, the maximum axis acceleration is used automatically (see P-AXIS-00008). | |
Parameter | kenngr.dist_ctrl[i].a_max (where i=0) | |
Data type | SGN32 | |
Data range | 0 ≤ a_max < MAX(SGN32) | |
Axis types | T, R | |
Dimension | T: 1 mm/s² | R: 1°/s² |
Default value | 0 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | When this parameter is 0, the maximum axis acceleration P-AXIS-00008 is used.
Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.a_max continues to be available. | |
P-AXIS-00417 | Maximum permissible change speed of measured distance | |
Description | The parameter defines the maximum permissible change in velocity of the measured distance. When distance control is activated, the sensor actual values are monitored for their change velocity. | |
Parameter | kenngr.dist_ctrl[i].max_act_value_change (where i=0) | |
Data type | SGN32 | |
Data range | 0 ≤ max_act_value_change < MAX(SGN32) | |
Axis types | T, R | |
Dimension | T: µm/s | R: 0.0001°/s |
Default value | 5000 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.max_act_value_change continues to be available. | |
P-AXIS-00418 | Reference point offset for measuring system | |
Description | The value range of the sensor measuring system can be moved by an offset using this machine data item. This is necessary in the case of absolute sensors, for example, to define the reference point, i.e. the sensor position that is adjusted if the spindle touches the ideal workpiece surface. | |
Parameter | kenngr.dist_ctrl[i].ref_offset (where i=0) | |
Data type | SGN32 | |
Data range | MIN(SGN32) ≤ ref_offset < MAX(SGN32) | |
Axis types | T, R | |
Dimension | T: 0.1µm | R: 0.0001 ° |
Default value | 0 (No offset) | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.ref_offset continues to be available. | |
P-AXIS-00419 | Upper limit for measuring system | |
Description | The parameter defines the upper limit of the sensor. An error message is output if this limit is exceeded when distance control is active. | |
Parameter | kenngr.dist_ctrl[i].max_pos (where i=0) | |
Data type | SGN32 | |
Data range | 0 ≤ max_pos < MAX(SGN32) | |
Axis types | T, R | |
Dimension | T: 0.1µm | R: 0.0001 ° |
Default value | 50000 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.max_pos continues to be available. | |
P-AXIS-00420 | Lower limit for measuring system | |
Description | The following value defines the lower limit of the sensor. An error message is generated if it is exceeded while distance control is active. | |
Parameter | kenngr.dist_ctrl[i].min_pos (where i=0) | |
Data type | SGN32 | |
Data range | 0 ≤ min_pos < MAX(SGN32) | |
Axis types | T, R | |
Dimension | T: 0.1µm | R: 0.0001 ° |
Default value | -50000 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.min_pos continues to be available. | |
P-AXIS-00421 | Tolerance band for limits | |
Description | This parameter defines a minimum distance from the minimum and maximum sensor positions. If this distance is undershot, the CNC generates the error messages ID 70330 or ID 70576. If the tolerance band is specified by zero, the limits of the minimum and maximum sensor positions from the axis parameters P-AXIS-00419 and P-AXIS-00420 have a direct effect. | |
Parameter | kenngr.dist_ctrl[i].tolerance (where i=0) | |
Data type | SGN32 | |
Data range | 0 ≤ tolerance < MAX(SGN32) | |
Axis types | T, R | |
Dimension | T: 0.1µm | R: 0.0001 ° |
Default value | 0 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameters kenngr.distc.tolerance and kenngr.distc.toleranz continue to be available. | |
P-AXIS-00428 | Consideration of distance control in software limit switch monitoring | |
Description | This parameter defines whether the calculated distance control offset is included in the software limit switch monitor (see [FCT-A2]). | |
Parameter | kenngr.dist_ctrl[i].check_sw_limit_switch (where i=0) | |
Data type | BOOLEAN | |
Data range | 0: Offset of distance control is not considered in software limit switch monitoring (default). 1: Offset of distance control is considered in software limit switch monitoring. | |
Axis types | T, R, S | |
Dimension | T: ---- | R,S: ---- |
Default value | 0 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.check_sw_limit_switch continues to be available. | |
P-AXIS-00500 | Option: Coupling of distance sensor and motor encoder | |
Description | Both the distance sensor and the axis motor encoder can be used as an extension. The inverse coupling of the two encoders (motor, distance) means that motor oscillations are not transmitted to distance control and this can reduce any tendency to oscillate. In addition, the position lag of the axes can be included in a programmed motion in the control direction. The following modes can be parameterised:
Note: For this mode, the following parameters must also be correctly set in the axis list of the axes involved: - P-AXIS-00099 - P-AXIS-00191 - P-AXIS-00833 | |
Parameter | kenngr.dist_ctrl[i].mode_dist_use_both_encoder (where i=0) | |
Data type | BOOLEAN | |
Data range | OFF | |
Axis types | T, R | |
Dimension | T: ---- | R: ---- |
Default value | OFF | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Parameter available as of V3.1.3080.12 or V3.1.3107.44. kenngr.distc.mode_dist_use_both_encoder continues to be available. | |
P-AXIS-00501 | Option: Adaptive weighting of acceleration | |
Description | To reduce a possible oscillation the acceleration can be reduced for small deviations. | |
Parameter | kenngr.dist_ctrl[i].use_adaptive_acceleration (where i=0) | |
Data type | BOOLEAN | |
Data range | 0: No adaptive weighting of acceleration 1: Adaptive weighting of acceleration active | |
Axis types | T, R | |
Dimension | T: ---- | R: ---- |
Default value | 0 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | In addition the following limits for acceleration and distance error must be configured: P-AXIS-00502 or P-AXIS-00416 and P-AXIS-00504 or P-AXIS-00505
Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.use_adaptive_acceleration continues to be available. | |

P-AXIS-00502 | Minimum acceleration | |
Description | The parameter defines the minimum acceleration of distance control. | |
Parameter | kenngr.dist_ctrl[i].a_min (where i=0) | |
Data type | UNS32 | |
Data range | 1 ... MAX (UNS32) | |
Axis types | T, R | |
Dimension | T: mm/s² | R: mm/s² |
Default value | 500 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.a_min continues to be available. | |
P-AXIS-00504 | Minimum distance error | |
Description | The parameter defines the minimum distance error for distance control up to which the minimum acceleration (P-AXIS-00502) is used. | |
Parameter | kenngr.dist_ctrl[i].dist_error_a_min (where i=0) | |
Data type | UNS32 | |
Data range | 0 ≤ P-AXIS-00504 < MAX(UNS32) | |
Axis types | T, R | |
Dimension | T: 0.1µm | R: 0.0001 ° |
Default value | 1000 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.dist_error_a_min continues to be available. | |
P-AXIS-00505 | Maximum distance error | |
Description | The parameter defines the maximum distance error for distance control from which the maximum acceleration (P-AXIS-00416) is used. | |
Parameter | kenngr.dist_ctrl[i].dist_error_a_max (where i=0) | |
Data type | UNS32 | |
Data range | 0 ≤ P-AXIS-00505 < MAX(UNS32) | |
Axis types | T, R | |
Dimension | T: 0.1µm | R: 0.0001 ° |
Default value | 5000 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.dist_error_a_max continues to be available. | |
P-AXIS-00507 | Order of the filter | |
Description | The filter order describes its behaviour in the event of a drop in frequency response. The following applies: Frequency drop = - P-AXIS-00507 * 20 dB/decade | |
Parameter | kenngr.dist_ctrl[i].low_pass_filter_order (where i=0) | |
Data type | UNS32 | |
Data range | 0 … 6 | |
Axis types | T, R | |
Dimension | T: ---- | R: ---- |
Default value | 4 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.low_pass_filter_order continues to be available. | |
P-AXIS-00508 | Filter cut-off frequency | |
Description | The parameter defines the value of a filter's characteristic frequency. | |
Parameter | kenngr.dist_ctrl[i].low_pass_filter_fg_f0 (where i=0) | |
Data type | REAL64 | |
Data range | 0 ≤ low_pass_filter_fg_f0 < MAX(REAL64) | |
Axis types | T, R | |
Dimension | T: Hz | R: Hz |
Default value | 25 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.low_pass_filter_fg_f0 continues to be available. | |
P-AXIS-00509 | Option: Dead time reduction | |
Description | The dead time of distance control can be reduced by an optimised schedule of the CNC. | |
Parameter | kenngr.dist_ctrl[i].optimized_scheduling (where i=0) | |
Data type | BOOLEAN | |
Data range | 0: Without optimised scheduling 1: Optimised scheduling active | |
Axis types | T, R | |
Dimension | T: ---- | R: ---- |
Default value | 0 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.optimized_scheduling continues to be available. | |
P-AXIS-00533 | Weighting factor for velocity of lowering movement | |
Description | This parameter weights the velocity (see P-AXIS-00415) of the lowering movement (towards the workpiece). This can be useful since the lifting movement is normally highly dynamic in order to avoid an obstacle or elevation quickly. Due to the weighting factor, it is possible to use a reduced velocity for (re-)approaching the workpiece. | |
Parameter | kenngr.dist_ctrl[i].v_weight_down (where i=0) | |
Data type | UNS32 | |
Data range | 0 ≤ v_weight_down < 2000 | |
Axis types | T, R | |
Dimension | T: 0.1% | R: 0.1% |
Default value | 0 * | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | * The weighting is deactivated; lifting and lowering movements use the identical velocity P-AXIS-00415.
Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.v_weight_down (available as of V2.11.2807.13) continues to be available.
| |
P-AXIS-00534 | Weighting factor for acceleration of lowering movement | |
Description | This parameter weights the velocity (see P-AXIS-00416) of the lowering movement (towards the workpiece). This can be useful since the lifting movement is normally highly dynamic in order to avoid an obstacle or elevation quickly. Due to the weighting factor, it is possible to use a reduced acceleration for (re-)approaching the workpiece. | |
Parameter | kenngr.dist_ctrl[i].a_weight_down | |
Data type | UNS32 | |
Data range | 0 ≤ a_weight_down < 2000 | |
Axis types | T, R | |
Dimension | T: 0.1% | R: 0.1% |
Default value | 0 * | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | * The weighting is deactivated; lifting and lowering movements use the identical acceleration P-AXIS-00416.
Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.a_weight_down (as of V2.11.2807.13) continues to be available. | |
P-AXIS-00422 | Numerator distance resolution of the additive sensor measuring system | |
Description | The distance resolution of the sensor measuring system is specified as the quotient P-AXIS-00423 in the dimension [increments/0.1 µm] for translatory axes or [increments/10^-4°] for rotary axes. The number of sensor increments must be specified in P-AXIS-00422. | |
Parameter | lr_hw[i].encoder_resolution_num | |
Data type | UNS32 | |
Data range | 0 < encoder_resolution_num < MAX(UNS32) | |
Axis types | T, R, S | |
Dimension | T: increments | R,S: increments |
Default value | 1 | |
Drive types | ---- | |
Remarks | This entry is valid for 'lr_hw[i].*' with i ≥ 1! The resolution of the motor sensor 'lr_hw[0].*' is defined by P-AXIS-00233 and P-AXIS-00234. | |
P-AXIS-00423 | Denominator distance resolution of the additive sensor measuring system | |
Description | The distance resolution of the sensor measuring system is specified as the quotient P-AXIS-00422 / P-AXIS-00423 in the dimension [increments/0.1 µm] for translatory axes or [increments/10^-4°] for rotary axes. The amount of the travel range must be specified in this parameter. | |
Parameter | lr_hw[i].encoder_resolution_denom | |
Data type | UNS32 | |
Data range | 0 ≤ encoder_resolution_denom < MAX(UNS32) | |
Axis types | T, R, S | |
Dimension | T: 0.1 µm | R,S: 0.0001° |
Default value | 1 | |
Drive types | ---- | |
Remarks | This entry is valid for 'lr_hw[i].*' with i ≥ 1! The resolution of the motor sensor 'lr_hw[0].*' is defined by P-AXIS-00233 and P-AXIS-00234. | |
P-AXIS-00230 | Sign reversal of actual value | |
Description | This parameter defines the sign reversal of the actual value. | |
Parameter | lr_hw[i].vz_istw | |
Data type | BOOLEAN | |
Data range | 0/1 | |
Axis types | T, R, S | |
Dimension | T: ---- | R,S: ---- |
Default value | 0 | |
Drive types | ---- | |
Remarks | These entries are not taken over when the axis parameters list is updated. Updates only become effective when the controller is rebooted. | |
P-AXIS-00424 | Handling of the additive sensor values | |
Description | This parameter defines whether the sensor positions are to be considered as linear or modulo values. By default, it can be handled according to the axis type or an individual default can be defined. When sensor values are handled according to the set axis type (see P-AXIS-00018), values are considered linear for the TRANSLATOR axis type, while modulo handling applies to the ROTATOR axis type. | |
Parameter | lr_hw[i].mode_act_pos | |
Data type | UNS16 | |
Data range | 0, 1, 2 where: 0: depending on axis type (default) 1 : linear 2 : modulo | |
Axis types | T, R | |
Dimension | T: ---- | R: ---- |
Default value | 0 | |
Drive types | ---- | |
Remarks | This entry is valid for 'lr_hw[i].*' with i ≥ 1! The setting of the sensor value range for the motor sensor 'lr_hw[0].*' is defined by P-AXIS-00122. | |
P-AXIS-00759 | Weighting the distance control output values | |
Description | The parameter weights the cyclic output value of distance control. This may affect distance control dynamics. For kp values less than 1.0, distance control dynamics are reduced; for kp value greater than 1.0, dynamics are increased. | |
Parameter | kenngr.dist_ctrl[i].kp (where i=0) | |
Data type | REAL64 | |
Data range | 0.0 < kp <= 2.0 | |
Axis types | T, R | |
Dimension | T: ---- | R: ---- |
Default value | 1.0 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | A kp factor less than 1 reduces a possible distance control oscillation and steadies the control in the event of minor distance errors.
Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.kp (as of V2.11.2809.06 and V3.1.3079.06 continues to be available. | |
P-AXIS-00764 | Integral (I) action time of the PID controller | |
Description | This parameter weights the I component of the PID controller. The integral action time defines the time after which the P and I components of the manipulated variable are equal. A large integral action time produces greater control stability. The shorter the integration action time, the greater the I component and the faster the control. Disable the I component by i_tn = 0. | |
Parameter | kenngr.dist_ctrl[i].i_tn (where i=0) | |
Data type | REAL64 | |
Data range | 0.0 <= i_tn <= 50.0 | |
Axis types | T, R | |
Dimension | T: s | R: s |
Default value | 0.0 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | To begin with, it is advisable to select a high initial value for the integral action time setting (e.g. 5) to avoid instability in the control loop. You can then reduce the integral action time step by step to obtain the effect you require. If there are no permanent control deviations, do not use the I component at first.
Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.i_tn (as of V2.11.2809.06 and V3.1.3079.06) continues to be available. | |
P-AXIS-00765 | Derivative (D) action time of the PID controller | |
Description | This parameter weights the D component of the PID controller. The derivative action time defines the time after which the P and D components of the manipulated variable are equal. The derivative action time stabilises controller behaviour and reduces oscillations. The larger the derivative action time, the stronger the D component. Disable the D component by d_tv=0. | |
Parameter | kenngr.dist_ctrl[i].d_tv (where i=0) | |
Data type | REAL64 | |
Data range | 0.0 <= d_tv <= 2.0 | |
Axis types | T, R | |
Dimension | T: s | R: s |
Default value | 0.0 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | To begin with, it is advisable to select a low initial value for the derivative action time setting to avoid instability in the control loop (e.g.: 0.01). You can then reduce the derivative action time step by step to obtain the effect you require.
Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.d_tv (as of V2.11.2809.06 and V3.1.3079.06) continues to be available. | |
P-AXIS-00782 | Filter type for smoothing sensor data | |
Description | Sensor values may be noisy. The oscillation tendency can better be suppressed by using a suitable filter . You can select the following filter types for distance control:
| |
Parameter | kenngr.dist_ctrl[i].filter_type (where i=0) | |
Data type | STRING | |
Data range | DEFAULT MOVING_AVERAGE LOWPASS KALMAN_MA EXPO_MEAN KALMAN_EXPO | |
Axis types | T, R | |
Dimension | T: ---- | R: ---- |
Default value | DEFAULT | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | In addition, the following filter parameters are required for each of the filter types::
Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.filter_type continues to be available. | |
P-AXIS-00783 | Uncertainty of measured values | |
Description | The parameter specifies the degree of deviation of the measured value from the actual values. The higher this value, the better the filter effect. However, possible overshoots are amplified. | |
Parameter | kenngr.dist_ctrl[i].kalman_sigma (where i=0) | |
Data type | REAL64 | |
Data range | 1.0 ≤ P-AXIS-00783 ≤ 10000.0 | |
Axis types | T, R | |
Dimension | T: ---- | R: ---- |
Default value | 4 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.kalman_sigma continues to be available. | |
P-AXIS-00784 | Smoothing factor | |
Description | The parameter specifies the weighting of the current measured value. Example: With a smoothing factor of 0.5, the current value is applied to the average value at a rate of 50%. | |
Parameter | kenngr.dist_ctrl[i].smoothing_factor (where i=0) | |
Data type | REAL64 | |
Data range | 0 < P-AXIS-00784 ≤ 1.0 | |
Axis types | T, R | |
Dimension | T: ---- | R: ---- |
Default value | 0.7 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of Build V3.1.3080.12 or V3.1.3107.44 For compatibility reasons, the parameter kenngr.distc.smoothing_factor continues to be available. | |
P-AXIS-00868 | Tolerance window in which the control deviation must be in order to fulfil the waiting condition. | |
Description | When the NC command “WAIT” is executed, the system waits until the control deviation of distance control lies within a defined time window (P-AXIS-00869) for a specified period of time. Only then is the next NC command executed. The parameter defines the tolerance window of the control deviation to fulfil the waiting condition. | |
Parameter | kenngr.dist_ctrl[i].window | |
Data type | REAL64 | |
Axis types | T, R | |
Dimension | T: 0.1 µm | R: 0.1 µm |
Default value | 1000 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of V3.1.3136.0 The maximum waiting time is defined by P-AXIS-00870. | |
P-AXIS-00869 | Number of cycles that the control deviation must remain within the tolerance window in order to fulfil the waiting condition. | |
Description | When the NC command “WAIT” is executed, the system waits until the control deviation of distance control remains within a defined time window (P-AXIS-00869) for a specified period of time. Only then is the next NC command executed. The parameter defines the number of cycles that the control deviation must remain within the tolerance window to fulfil the waiting condition. | |
Parameter | kenngr.dist_ctrl[i].cycles_in_window | |
Data type | UNS32 | |
Data range | 0 < P-AXIS-00869 ≤ MAX(UNS32) | |
Axis types | T, R | |
Dimension | T: ---- | R, S: ---- |
Default value | 1 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of V3.1.3136.0 The maximum waiting time is defined by P-AXIS-00870. | |
P-AXIS-00870 | Maximum waiting time to fulfil the waiting condition | |
Description | When the NC command “WAIT” is executed, the system waits until the control deviation of distance control remains for a specified period of time (P-AXIS-00869) within a defined time window (P-AXIS-00868). Only then is the next NC command executed. The parameter defines the maximum waiting time to fulfil the waiting condition. If the waiting condition is not fulfilled within this period of time, error 70696 is output. | |
Parameter | kenngr.dist_ctrl[i].max_wait_time | |
Data type | UNS32 | |
Data range | 0 < P-AXIS-00870 ≤ MAX(UNS32) | |
Axis types | T, R | |
Dimension | T: µs | R, S: ---- |
Default value | 8000000 | |
Drive types | SERCOS, Profidrive, CANopen | |
Remarks | Available as of V3.1.3136.0 | |