P-AXIS-00047
Activation of cross compensation
This parameter activates the cross compensation.
Parameter
lr_param.crosscomp
Data type
BOOLEAN
Data range
0/1
Axis types
T
Dimension
T: ----
Default value
0
Drive types
Remarks
P-COMP-00060
Maximum number of table entries for cross compensation
This cross compensation parameter (FCT-C5) saves the memory space required for a particular number of table entries.
The size of the actually used compensation table is defined by `last_index` (P-COMP-00004) and `last_index` must be smaller than `max_points`.
Parameter
kw.crosscomp.max_points
Data type
UNS32
Data range
0 <= P-COMP-00060
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
1001
Remarks
The parameter value can no longer be changed after start-up or after lists are reloaded. Otherwise error ID 110639 is output.
If P-COMP-00060 is not specified (or assigned the value 0), the default value is assigned to P-COMP-00060 for downward compatibility reasons.
To avoid the default assignment, memory can be saved for an axis that does not use cross compensation by assigning the value 1 to P-COMP-00060.
This parameter is available as of CNC Build V3.3079.06
P-COMP-00003
Unit of the length entries
The parameter defines the unit to be used for the length entries of compensation values.
Parameter
kw.crosscomp.unit
Data type
BOOLEAN
Data range
0: Encoder increments
1: Metric (in 0.1 µm)
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
0
Remarks
P-COMP-00004
Last index of compensation value table
This parameter determines the last valid index in the table of the master axis. The table always starts with index 0
Parameter
kw.crosscomp.last_index
Data type
SGN32
Data range
0 ≤ last_index < P-COMP-00060
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
0
Remarks
P-COMP-00060 is available as of Build V3.1.3079.06. The upper limit in previous CNC versions is 1000.
P-COMP-00005
Logical axis number of the master axis
This parameter determines the logical number of the master axis whose command position is used to calculate the input variable of the compensation value table of the slave axis.
Parameter
kw.crosscomp.master_ax_nr
Data type
UNS16
Data range
1 ≤ master_ax_nr ≤ MAX (UNS16)
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
0
Remarks
P-COMP-00026
Number of cycles for ‘smooth switching’
This parameter determines the number of cycles for which cross compensation is activated/deactivated smoothly.
Parameter
kw.crosscomp.n_cycles
Data type
UNS16
Data range
0 ≤ n_cycles ≤ 20 (maximum number of cycles for which cross compensation is activated/deactivated,
application-specific)
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
0
Remarks
P-COMP-00029
Manual activation
Cross compensation is automatically activated by the CNC if it selected in the axis parameters (P-AXIS-00047) and the required conditions are met (e.g. axis is homed).
If the parameter is set to the value 1, cross compensation must be activated explicitly by an NC command (see [PROG//Selecting/deselecting axis compensations in the NC program]. In addition, compensation is deselected at the end of the NC program, at CNC reset and on axis release.
Parameter
kw.crosscomp.manual_activation
Data type
BOOLEAN
Data range
0: Automatic activation
1: Manual activation in NC program
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
0
Remarks
P-COMP-00006
Interpolation point of the master axis
This parameter determines the interpolation points of the master axis on which the slave axis has to be corrected.
Parameter
kw.crosscomp.table[i].setpoint
Data type
SGN32
Data range
MIN(SGN64-1023) ≤ setpoint < MAX(SGN64-1023)
Axis types
T, R, S
Dimension
T: 0.1 µm or increments
R,S: 0.0001° or increments
Default value
0
Remarks
As of V3.1.3132.0 and/or V4.29.0, the data type is REAL64; in earlier versions SGN32. This also affects the related data range.
P-COMP-00007
Compensation values for the slave axis
This parameter determines the relative compensation values for the slave axis at interpolation points 'i'.
Parameter
kw.crosscomp.table[i].correction
Data type
REAL64
Data range
MIN(SGN64-1023) ≤ correction < MAX(SGN64-1023)
Axis types
T, R, S
Dimension
Default value
0
Remarks