Power Values Period 1Ph
Power Values Period 1Ph 1:
The Power Values Period module calculates the power values of the connected loads. These include the fundamental components and the phase shift angle. For this purpose, only the first harmonics of the input signal are used for the calculation in addition to the signal curve in the time range. The advantage of these algorithms is the high dynamics of the calculations. The results refer to a configurable number of signal periods. The period duration refers to the frequency specified at the input at the start of the period. The statistical results refer to the entire runtime or the time at which the statistical results were last reset.
In the Beckhoff Information System you will find the documentation of the corresponding PLC function block FB_PMA_PowerValues_Period_1Ph.
In the Beckhoff Information System you will find the documentation of the TF3650 TwinCAT 3 Power Monitoring function with descriptions of the corresponding PLC library.
Configuration parameters
  • Buffer Length: Length of the input buffer.
  • Sample Rate [Hz]: Sample rate (samples per second) of the input signal.
  • Min Input Current [A]: Minimum input value (RMS) of the current. This parameter prevents the calculation of input values that are too small.
  • Periods: Number of periods that influence the calculation. (Period length = sample rate/frequency).
Input values
Output values