ADSRDDEVINFO
The general device information can be read with this block.
NETID : T_AmsNetId;
PORT : T_AmsPort;
RDINFO : BOOL;
TMOUT : TIME;
NETID : Is a string containing the AMS network identifier of the target device to which the ADS command is directed.
PORT : Contains the port number of the ADS device
RDINFO : The ADS command is triggered by a rising edge at this input.
TMOUT : States the time before the function is cancelled.
BUSY : BOOL;
ERR : BOOL;
ERRID : UDINT;
DEVNAME : STRING(19);
DEVVER : UDINT;
BUSY : This output remains TRUE until the block has executed a command, but at the longest for the duration supplied to the ‘Timeout’ input. While Busy = TRUE, no new command will be accepted at the inputs. Please note that it is not the execution of the service but its acceptance whose time is monitored.
ERR : This output is switched to TRUE if an error occurs during the execution of a command. The command-specific error code is contained in ‘ErrorId’. If the block has a timeout error, ‘Error’ is TRUE and ‘ErrorId’ is 1861 (hexadecimal 0x745). Is reset to FALSE by the execution of a command at the inputs.
ERRID : Contains the command-specific error code of the most recently executed command. Is reset to 0 by the execution of a command at the inputs.
DEVNAME : Contains the name of the ADS device.
DEVVER : Contains the version number of the ADS device.
Example of calling the block in FBD:
In the example, the device information of the first PLC run-time system (port 801) on computer ‘1.1.1.2.7.1’ is read. As a result the name ‘PLC Server’ and the version number 02.00.7 are received.
Development environment | Target system type | PLC libraries to include |
TwinCAT v2.7.0 | PC or CX (x86) | PLCSystem.Lib |
TwinCAT v2.8.0 | PC or CX (x86) | TcSystem.Lib |
TwinCAT v2.10.0 Build >= 1301 | CX (ARM) | TcSystem.Lib |