MP_EPIV_R6
This function block is used to control a control ball valve of series EP..R-R6+BAC.
MP_Address is used to specify the MP-Bus device with which the function block is to communicate. bStart activates communication with the MP-Bus device. bBusy indicates that the function block is active. If bStart remains TRUE, the device is addressed cyclically with a period specified by the time in TMPolling. The time should be set longer than 1 s. bError is used to indicate an error in communication with the actuator. The type of the error can be read with iErrorId.
MP_Address : USINT := 1;
bStart : BOOL;
strDataKL6771 : DataKL6771;
TMpolling : TIME := t#10s;
nOverrideControl_Write : E_MPBus_Override_6wayMPIV := MPBus_6wayMPIV_None;
rSetPoint_Write : LREAL;
MP_Address: MP-Bus address of the slave.
bStart: a positive edge starts the function block. If this remains continuously TRUE, the function block will be activated cyclically with a period specified by the time in TMPolling.
strDataKL6771: the data structure with which the KL6771 function block must be linked (see DataKL6771).
TMpolling: the time for which the function block should address the actuator. Default 10 s, minimum time 1 s.
nOverrideControl_Write: the relative setpoint is ignored in override control mode (see E_MPBus_Override_6wayMPIV). Overriding is disabled if the command is not repeated within 120 minutes.
rSetPoint_Write: 0...100 %.
iErrorId : MP_Error;
nOverrideControl_Read : E_MPBus_Override_6wayMPIV;
rSetPoint_Read : LREAL;
rRelativePos_Read : LREAL;
rAbsolutePos_Read : LREAL;
rRelativeFlow_Read : LREAL;
bErrorStateFlowSensorErr : BOOL;
bErrorStateActuator_can_not_move : BOOL;
st_StateEV : st_StateEV;
rAbsoluteFlow_UnitSel : LREAL;
bBusy: this bit is set for as long as the function block is active.
bError: the output becomes TRUE as soon as an error occurs. This error is described via the iErrorId variable.
iErrorId: this output outputs an error code in the event of an error (see MP_Error). bError goes TRUE at the same time.
nOverrideControl_Read: current override control mode (see E_MPBus_Override_6wayMPIV).
rSetPoint_Read: setpoint in % (0...100 %).
rRelativePos_Read: relative position in % (0...100 %).
rAbsolutePos_Read: absolute position in °.
rRelativeFlow_Read: relative flow rate in % (0...100 %).
bErrorStateFlowSensorErr: flow sensor is faulty.
bErrorStateActuator_can_not_move: actuator cannot move.
st_StateEV: only devices from 27 March 2014 (see St_StateEV).
rAbsoluteFlow_UnitSel: absolute flow rate in UnitSel (0...4294967295).