FB_DALIV2EnableDAPCSequence
This command starts a Direct Arc Power Control (DAPC) sequence. Following this command, DirectArcPowerControl commands must be sent using the function block FB_DALIV2DirectArcPowerControl(). There must not be any more than 200 ms between the individual commands; otherwise the sequence will be ended.
![]() | This command can only be executed by DALI devices that comply with the IEC 62386 standard. |
bStart : BOOL;
nAddr : BYTE;
bStart: The block is activated by a rising edge at this input.
nAddr: The address of a participating device or of a group.
eAddrType: Short address, group address or broadcast.
eCommandPriority: The priority (high, middle, low) this command has when executed by the library.
nErrorId : UDINT;
bBusy: When the block is activated the output is set, and it remains active until execution of the command has been completed.
bError: This output is switched to TRUE if an error occurs during the execution of a command. The command-specific error code is contained in nErrorId. Is reset to FALSE by the execution of an instruction at the inputs.
nErrorId: Contains the command-specific error code of the most recently executed command. Is reset to 0 by the execution of an instruction at the inputs. See Error codes.
stCommandBuffer: A reference to the structure for communication with the FB_DALIV2Communication() (KL6811) or FB_KL6821Communication() (KL6821) block.
