MC_StepBlockDetection
MC_StepBlockDetection 1:
This function block performs the search for a physical object that mechanically blocks the movement.
To avoid mechanical damage, the movement is usually performed with reduced torque ("TorqueLimit"). Since the actual value is subject to fluctuations, a tolerance must also be specified ("TorqueTolerance").
The condition for successful completion of the sequence consists of two parts.
Firstly, the torque within the specified "TorqueTolerance" must correspond to the "TorqueLimit" and secondly, the actual velocity for the time "DetectionVelocityTime" must be below the "DetectionVelocityLimit".
The "..Detection" version of this function block does not manipulate the current position of the axis at the end of the sequence, but instead returns the detected position to the user as "RecordedPosition".
MC_StepBlockDetection 2: Inputs
    Execute                : BOOL;
    Direction              : MC_Home_Direction;
    Velocity               : LREAL;
    Acceleration           : LREAL;
    Deceleration           : LREAL;
    Jerk                   : LREAL;
    DetectionVelocityLimit : LREAL;
    DetectionVelocityTime  : TIME;
    TimeLimit              : TIME;
    DistanceLimit          : LREAL;
    TorqueLimit            : LREAL;
    TorqueTolerance        : LREAL;
    BufferMode             : MC_BufferMode;
    Options                : ST_Home_Options3;
Type
Execute
The command is executed with a rising edge at the Execute input.
Direction
MC_Home_Direction
Enumeration that defines the initial direction of movement for the search procedure.
Velocity
LREAL
Maximum travel velocity (>0).
Acceleration
LREAL
Acceleration (≥0). If the value is 0, the standard acceleration from the axis configuration applies.
Deceleration
LREAL
Deceleration (≥0). If the value is 0, the standard deceleration from the axis configuration applies.
Jerk
LREAL
Jerk (≥0). If the value is 0, the standard jerk from the axis configuration applies.
LREAL
Limit velocity that must be adhered to (value must be below this) for the time DetectionVelocityTime in order to detect driving against the fixed stop.
TIME
Time for detecting the velocity undershoot when driving against the fixed stop.
TimeLimit
TIME
Exceeding this time leads to the search procedure being aborted.
DistanceLimit
LREAL
Exceeding this distance in relation to the start position leads to the search procedure being aborted.
TorqueLimit
LREAL
The motor torque is limited to this value in order to avoid mechanical damage.
TorqueTolerance
LREAL
Tolerance related to the TorqueLimit within which driving against the fixed stop is detected.
BufferMode
MC_BufferMode
Not implemented
Options
ST_Home_Options3
DisableDriveAccess: Set to FALSE for Beckhoff drives. Usually to TRUE for third-party drives (see info).
InstantLagReduction: When referencing to a mechanical fixed stop, the sudden stop produces a lag error in the NC axis, which is dissipated with the parameterized dynamic values in the further course. This can lead to an assumed delay when observing the sequence, but it is useful with "soft" fixed stops in particular. The lag error is dissipated abruptly by setting this flag.
MC_StepBlockDetection 3:
If DisableDriveAccess = TRUE, the user is responsible for modifying and reconstructing required drive parameters. The parameters required for the intended homing sequence must be agreed with the manufacturer of the third-party drive.
MC_StepBlockDetection 4:/MC_StepBlockDetection 5: Inputs/outputs
    Axis      : AXIS_REF;
    Parameter : MC_HomingParameter;
Type
Axis
AXIS_REF
Axis data structure of the type AXIS_REF, which uniquely addresses an axis in the system. Among other parameters it contains the current axis status, including position, velocity or error state.
Parameters
MC_HomingParameter
Data structure of the type MC_HomingParameter, which must be transferred from function block to function block over the entire homing sequence.
MC_StepBlockDetection 6: Outputs
    Done             : BOOL;
    Busy             : BOOL;
    Active           : BOOL;
    CommandAborted   : BOOL;
    Error            : BOOL;
    ErrorID          : UDINT;
    RecordedPosition : LREAL;
Type
Done
Becomes TRUE if the command was completed successfully.
Busy
The Busy output becomes TRUE when the command is started with Execute and remains TRUE for as long as the command is processed. When Busy becomes FALSE again, the function block is ready for a new order. At the same time one of the outputs, Done, CommandAborted, or Error, is set.
Active
Indicates that the command is executed.
CommandAborted
Becomes TRUE, if the command could not be fully executed.
Error
Becomes TRUE as soon as an error occurs.
ErrorID
UDINT
If the error output is set, this parameter supplies the error number.
RecordedPosition
LREAL
Axis position at which the event was recorded.
