FB_BA_RampLmt
FB_BA_RampLmt 1:
The function block FB_BA_RampLmt limits the increase or decrease speed of an input signal.
As fIn rises, the output fOut is limited to the slope of (fHi-fLo)/nTiUp.
When fIn decreases, the output fOut is limited to the slope of (fHi-fLo)/nTiDwn.
When the function block is activated (rising edge on bEn), the function block output fOut is initially set equal to the input fIn before it begins to track fIn. If the function block is not active (bEn = FALSE), then fOut = 0.
FB_BA_RampLmt 2:
fLo must be less than fHi. If fLo is greater than fHi, fLo is limited to fHi. According to the calculation shown, this means that the output fOut immediately follows the input fIn.
If the nTiUp or nTiDwn times are set to 0, this is handled internally, and the fOut output follows the fIn input immediately.
FB_BA_RampLmt 3:
FUNCTION_BLOCK FB_BA_RampLmt
  bEn            : BOOL;
  fIn            : REAL;
  bSync          : BOOL;
  fSync          : REAL;
  fHi            : REAL;
  fLo            : REAL;
  nTiUp          : UDINT;
  nTiDwn         : UDINT;
  fOut           : REAL;
FB_BA_RampLmt 4: Inputs
Type
bEn
Function block enable; when a rising edge occurs, fOut is set to fIn. If bEn is FALSE, then fOut = 0.0.
fIn
REAL
Input value of the ramp function
bSync
When a rising edge is applied to bSync, the output is set to fSync, so that in the next cycle, the system ramps up or down from this value.
This functionality is enabled only if the function block is also enabled in the same cycle using bEn.
fSync
REAL
Value to which the output is synchronized using bSync.
fHi
REAL
Upper interpolation point for calculating the ramps
fLo
REAL
Lower interpolation point for calculating the ramps. fHi must be greater than fLo; otherwise an error is output!
nTiUp
UDINT
Rise time [s].
nTiDwn
UDINT
Fall time [s].
FB_BA_RampLmt 5: Outputs
Type
fOut
REAL
Output signal, slope-limited through the ramps.