NT_Reboot
The Windows NT operating system can be restarted with the aid of the "NT_Reboot" function block. The function largely corresponds to the Restart command on the Windows taskbar. A delay before execution of the Restart command can be defined via the DELAY parameter.
NETID : T_AmsNetId;
DELAY : DWORD;
START : BOOL;
TMOUT : TIME := DEFAULT_ADS_TIMEOUT;
NETID: It is possible here to provide the AmsNetId of the TwinCAT computer that is to be re-booted (type: T_AmsNetID). If the restart is to take place on the local computer, an empty string can be entered.
DELAY: The delay time, in seconds, before the Restart command is executed.
START: the block is activated by a positive edge at this input.
TMOUT: States the length of the timeout that may not be exceeded by execution of the ADS command.
BUSY : BOOL;
ERR : BOOL;
ERRID : UDINT;
BUSY: When the function block is activated this output is set. It remains set until a feedback is received.
ERR: If an error should occur during the transfer of the command, then this output is set once the BUSY output was reset.
ERRID: Supplies the ADS error number when the ERR output is set.
Development environment | Target platform | PLC libraries to be integrated (category group) |
TwinCAT v3.1.0 | PC or CX (WES7/Win7/Win10: TC RT x86/x64, WEC6/7: TC RT x86, WEC7: TC CE7 ARMV7) | Tc2_Utilities (System) |