FB_AmsLogger
The "TwinCAT AMS Logger" is a component of the "TwinCAT ADS Monitor" (..\TwinCAT\AdsMonitor\Logger\TcAmsLog.exe). The logger records the AMS/ADS commands on the data carrier. The recording can be displayed and analyzed later, e.g. during troubleshooting with the "TwinCAT AMS ADS Viewer".
The FB_AmsLogger function block can be used to start or stop the recording from a PLC program. The FB_AmsLogger function block can only communicate with an existing/running instance of TcAmsLog.exe. In other words, TcAmsLog.exe must already have been started, e.g. manually via the Start menu or via the NT_StartProcess function block.
sNetId : T_AmsNetId := '';
eMode : E_AmsLoggerMode := AMSLOGGER_RUN;
sCfgFilePath : T_MaxString := '';
bExecute : BOOL;
sNetId | T_AmsNetID | The network address of the TwinCAT computer on which the status of the "TwinCAT AMS Logger" should be modified can be specified here. An empty string can be specified for the logger on the local computer. |
eMode | The new status to which the "TwinCAT AMS Logger" is to be set (start/stop recording). | |
sCfgFilePath | T_MaxString | (Optional) path for a "TwinCAT AMS Logger" configuration file. Currently not yet implemented and reserved for future applications (enter an empty string). |
bExecute | BOOL | The function block is enabled by a positive edge at this input. |
tTimeout | TIME | States the length of the timeout that may not be exceeded by execution of the ADS command. |
Outputs
nErrId : UDINT;
bBusy | BOOL | When the function block is enabled, this output is set and remains set until a feedback is received. |
bError | BOOL | If an error occurs during the transmission of the command, this output is set after the bBusy output is reset. |
nErrId | UDINT | Returns the ADS error number when the bError output is set. |
Example:
When the PLC program starts an instance of TcAmsLog.exe is started on a local system. When the bRecord variable is set to TRUE, the recording of the AMS/ADS command is started. It is stopped when the variable is reset to FALSE.
Declaration part:
PROGRAM MAIN
bRecord : BOOL := TRUE;(* TRUE => start recording, FALSE => stop recording *)
fbStartProcess : NT_StartProcess := ( NETID := '', PATHSTR: = 'c:\TwinCAT\AdsMonitor\Logger\TcAmsLog.exe',
DIRNAME:= 'c:\TwinCAT\AdsMonitor\Logger', COMNDLINE := '', TMOUT := DEFAULT_ADS_TIMEOUT );
fbAmsLogger : FB_AmsLogger := ( sNetID := '', eMode := AMSLOGGER_STOP, sCfgFilePath := '', tTimeout := DEFAULT_ADS_TIMEOUT );
state : BYTE;
nErrID : UDINT;
eCurrMode : E_AmsLoggerMode := AMSLOGGER_STOP;(* Current mode/state *)
eNewMode : E_AmsLoggerMode := AMSLOGGER_STOP;(* New mode/state *)
timer : TON := ( PT := T#5s );
END_VARImplementation:
CASE state OF
0:(* Start instance of TcAmsLogger.exe *)
fbStartProcess( START := FALSE );
fbStartProcess( START:= TRUE );
state := 1;
1:(* Wait until command execution started *)
fbStartProcess( START := FALSE, BUSY=>bBusy, ERR=>bError, ERRID=>nErrID );
IF NOT bBusy THEN
IF NOT bError THEN(* Success *)
state := 2;
ELSE(* Error *)
state := 100;
END_IF
END_IF
2:(*Wait until instance started or new AMS logger mode/state set *)
timer( IN := TRUE );
IF timer.Q THEN
timer( IN := FALSE );
state := 3;
END_IF
3:(* Change TcAmsLog.exe mode/state *)
eNewMode := SEL( bRecord, AMSLOGGER_STOP, AMSLOGGER_RUN);
IF ( eNewMode <> eCurrMode ) THEN
fbAmsLogger( bExecute := FALSE );
fbAmsLogger( eMode:= eNewMode, bExecute := TRUE );
state := 4;
END_IF
4:(* Wait until command execution started *)
fbAmsLogger( bExecute := FALSE, bBusy=>bBusy, bError=>bError, nErrID=>nErrID );
IF NOT bBusy THEN
eCurrMode := eNewMode;
state := 2;
ELSE(* Error *)
state := 100;
END_IF
END_IF
100:(* Error state *)
END_CASERequirements
Development environment | Target platform | PLC libraries to be integrated (category group) |
TwinCAT v3.1.0 | PC or CX (x86, x64, Arm®) | Tc2_Utilities (System) |