MC_Halt
MC_Halt 1:
The function block MC_Halt is used to stop an axis with a defined deceleration ramp.
In contrast to MC_Stop, the axis is not locked against further movement commands. The axis can therefore be restarted through a further command during the deceleration ramp or after it has come to a halt.
Motion commands can be applied to coupled slave axes, if this option was explicitly activated in the axis parameters. A motion command such as MC_Halt then automatically leads to decoupling of the axis, after which the command is executed. In this case the only available BufferMode is "Aborting".
MC_Halt 2: Inputs
    Execute      : BOOL;
    Deceleration : LREAL;
    Jerk         : LREAL;
    BufferMode   : MC_BufferMode;
    Options      : ST_MoveOptions;
Type
Execute
The command is executed with a rising edge.
Deceleration
LREAL
Deceleration
If the value is ≤ 0, the deceleration parameterized with the last Move command is used. For safety reasons MC_Halt and MC_Stop cannot be executed with weaker dynamics than the currently active motion command. The parameterization is adjusted automatically, if necessary.
Jerk
LREAL
Jerk
If the value is ≤ 0, the jerk parameterized with the last Move command takes effect.
BufferMode
MC_BufferMode
Is evaluated if the axis is already executing another command. MC_Halt becomes active after the current command or aborts it. Transition conditions from the current to the next command are also determined by the BufferMode. If the command is applied to a coupled slave axis, only the BufferMode "Aborting" is possible.
Special characteristics of MC_Halt: the BufferMode "Buffered" shows no effect, because the command is executed only at standstill. The blending modes "MC_BlendingNext" and "MC_BlendingLow" do not change the last target position, although they can result in a change in dynamics (deceleration) of the stop ramp. The modes "MC_BlendingPrevious" and "MC_BlendingHigh" extend the travel to the original target position. The stop ramp is only initiated when this position is reached (defined braking point).
Options
ST_MoveOptions
Data structure containing additional, rarely used parameters. The input can normally remain open.
See also: General rules for MC function blocks
MC_Halt 3: Inputs/outputs
    Axis : AXIS_REF;
Type
Axis
AXIS_REF
Axis data structure that unambiguously addresses an axis in the system. Among other parameters it contains the current axis status, including position, velocity or error state.
MC_Halt 4: Outputs
    Done           : BOOL;
    Busy           : BOOL;
    Active         : BOOL;
    CommandAborted : BOOL;
    Error          : BOOL;
    ErrorID        : UDINT;
Type
Done
TRUE if the axis has been stopped and is stationary.
Busy
TRUE as soon as the command is started with "Execute" and as long as the function block is active. If "Busy" is FALSE, the function block is ready for a new order. At the same time one of the outputs "CommandAborted" or "Error" is set.
Active
Indicates that the command is executed. If the command was buffered, it becomes active once a running command is completed.
CommandAborted
TRUE if the command could not be executed completely. The axis was stopped or the current command was replaced by another Move command.
Error
TRUE, if an error occurs.
ErrorID
UDINT
If the error output is set, this parameter supplies the error number.
Development environment
Target system type
PLC libraries to include
TwinCAT v3.0.0
PC or CX (x86 or x64)
Tc2_MC2