FB_KL3228Config
FB_KL3228Config 1:
The FB_KL3228Config function block is used to parameterize a KL3228: 8-channel input terminal for resistance sensors.
FB_KL3228Config 2:
The function block only parameterizes one terminal channel. For parameterizing all channels, the corresponding number of function blocks has to be instantiated. A mixed configuration (e.g. different sensor types) is possible.
FB_KL3228Config 3: Inputs
    bConfigurate         : BOOL;
    bReadConfig          : BOOL;
    iSetSensorType       : INT;
    tTimeout             : TIME;
Type
bConfigurate
A rising edge starts the configuration sequence. First, the general terminal data, i.e. "terminal name", "special version" and "firmware version", are read. Then, the specified settings are written to the corresponding registers and finally read again for verification and information. The read information is displayed at the function block outputs. During this sequence the output bBusy is TRUE, and no further command, e.g. bReadConfig, is accepted.
bReadConfig
A rising edge starts a read sequence. The general terminal data “terminal name”, “special version” and “firmware version” are read, followed by the set configuration parameters. The read information is displayed at the function block outputs. During the read sequence the output bBusy is TRUE, and no further command, e.g. bConfigurate, is accepted.
iSetSensorType
INT
This input is used to set the sensor. The setting is based on the table below.
tTimeout
TIME
The terminal configuration or reading of the configuration must be completed within the time entered here. Otherwise an error with a corresponding error number is issued at the outputs bError and iErrorId.
iSetSensorType
Element
0
PT1000
1
NI1000
2
RSNI1000 (NI1000 according to Landis&Staefa characteristics: 1000 Ω at 0 °C and 1500 Ω at 100 °C).
FB_KL3228Config 4: Inputs/outputs
    stInData  : ST_KL1501InData;
    stOutData : ST_KL1501OutData;
Type
stInData
ST_KL1501InData
Reference to the structure of the input process image.
stOutData
ST_KL1501OutData
Reference to the structure of the output process image.
FB_KL3228Config 5: Outputs
    bBusy            : BOOL;
    bError           : BOOL;
    iErrorId         : UDINT;
    iState           : USINT;
    iDataIn          : INT;
    iTerminalType    : WORD;
    iSpecialType     : WORD;
    iFirmwareVersion : WORD;
    sDescription     : STRING;
    sSensorType      : STRING;
Type
bBusy
As long as the read or configuration sequence is in progress, this output is TRUE.
This output is switched to TRUE, if an error occurred while a command (Configure or Read) is executed. The command-specific error code is contained in iErrorId.
iErrorId
UDINT
Contains the command-specific error code of the most recently executed command. It is reset to 0 by activating the function block again via the inputs bConfigurate or bReadConfig. See error codes.
iState
USINT
Corresponds to the status variable of the process data stInData.iState, see VAR_IN_OUT. During command execution (bBusy = TRUE) this output is set to 0. This output is therefore suitable for assessing the status of the terminal in normal operation. Interfering states during configuration and reading through the register communication are hidden.
iDataIn
UDINT
Corresponds to the data variable of the process data stInData.iDataIn, see VAR_IN_OUT. During command execution (bBusy = TRUE) this output retains the value it had before the command was called. This makes the output suitable for direct process data processing during normal operation of the terminal. Interfering states during configuration and reading through the register communication are hidden.
iTerminalType
WORD
Contents of register 8 (terminal name). When used with the correct terminal, the content should be 0x05DD (1501dec).
iSpecialType
WORD
Contents of register 29 (special version)
iFirmwareVersion
WORD
Contents of register 9 (firmware version)
sDescription
STRING
Terminal name, special version and firmware version as string (e.g. 'terminal KL1501-0000 / firmware 1C').
sSensorType
STRING
Set sensor type in plain text.
Development environment
Target platform
IO Hardware
PLC libraries to include
TwinCAT v3.1.4018.26
PC/CX
KL3201, KL3202, KL3204
Tc2_IoFunctions from v3.3.5.0