FB_KL27x1Config
FB_KL27x1Config 1:
The FB_KL27x1Config function block is used to parameterize a KL2751 / KL2761: 1-channel dimmer terminal.
FB_KL27x1Config 2: Inputs
    bConfigurate            : BOOL;
    bReadConfig             : BOOL;
    bSetDimRampAbsolute     : BOOL;
    iSetRampTime            : INT;
    bSetWatchdogDisable     : BOOL;
    iSetWatchdogTimeout     : UINT;
    iSetTimeoutOnValue      : UINT;
    iSetTimeoutOffValue     : UINT;
    iSetDimmerMode          : INT;
    bSetOnAfterShortCircuit : BOOL;
    bSetLineFrequency60Hz   : BOOL;
    tTimeout                : TIME;
Type
bConfigurate
A rising edge starts the configuration sequence. First, the general terminal data, i.e. "terminal name", "special version" and "firmware version", are read. Then, the specified settings are written to the corresponding registers and finally read again for verification and information. The read information is displayed at the function block outputs. During this sequence the output bBusy is TRUE, and no further command, e.g. bReadConfig, is accepted.
bReadConfig
A rising edge starts a read sequence. The general terminal data “terminal name”, “special version” and “firmware version” are read, followed by the set configuration parameters. The read information is displayed at the function block outputs. During the read sequence the output bBusy is TRUE, and no further command, e.g. bConfigurate, is accepted.
bSetDimRampAbsolute
FALSE: The set ramp time iSetRampTime refers to the complete data area (0 - 32767). The smaller the discontinuity, the shorter the ramp time. TRUE: Each switching step, whatever the size, requires the same time, as entered under iSetRampTime.
iSetRampTime
INT
Ramp time input. The setting is based on the table below.
bSetWatchdogDisable
The internal watchdog is disabled.
iSetWatchdogTimeout
ÚINT
Setting the watchdog time as a multiple of 10 ms.
iSetTimeoutOnValue
UINT
This input specifies the light value that is output when a fieldbus error occurs with current process data > 0.
iSetTimeoutOffValue
UINT
This input specifies the light value that is output when a fieldbus error occurs with current process data = 0.
iSetDimmerMode
INT
This input is used to set the dimmer mode. The setting is based on the table below.
FALSE: After a short circuit the light remains switched off. TRUE: The light is switched on again after a short circuit.
FALSE: Mains frequency = 50 Hz. TRUE: Mains frequency = 60 Hz.
tTimeout
TIME
The terminal configuration or reading of the configuration must be completed within the time entered here. Otherwise an error with a corresponding error number is issued at the outputs bError and iErrorId.
iSetRampTime
Element
0
50 ms
1
100 ms
2
200 ms
3
500 ms
4
1 s
5
2 s
6
5 s
7
10 s
iSetDimmerMode
Element
0
Automatic detection
1
Trailing edge phase control
2
Leading edge phase control
3
Rectifier mode, positive (positive half-wave with leading edge phase control)
4
Rectifier mode, negative (negative half-wave with leading edge phase control)
FB_KL27x1Config 3: Inputs/outputs
    stInData  : ST_KL1501InData;
    stOutData : ST_KL1501OutData;
Type
stInData
ST_KL1501InData
Reference to the structure of the input process image.
stOutData
ST_KL1501OutData
Reference to the structure of the output process image.
FB_KL27x1Config 4: Outputs
    bBusy             : BOOL;
    bError            : BOOL;
    iErrorId          : UDINT;
    iState            : USINT;
    iTerminalType     : WORD;
    iSpecialType      : WORD;
    iFirmwareVersion  : WORD;
    sDescription      : STRING;
    bDimRampAbsolute  : BOOL;
    sRampTime         : STRING;
    bWatchdogDisable  : BOOL;
    tWatchdogTimeout  : TIME;
    iTimeoutOnValue   : UINT;
    iTimeoputOffValue : UINT;
    sDimmerMode       : STRING;
    aAfterShortCirciut: STRING;
    sLineFrequency    : STRING;
Type
bBusy
As long as the read or configuration sequence is in progress, this output is TRUE.
This output is switched to TRUE, if an error occurred while a command (Configure or Read) is executed. The command-specific error code is contained in iErrorId.
iErrorId
UDINT
Contains the command-specific error code of the most recently executed command. It is reset to 0 by activating the function block again via the inputs bConfigurate or bReadConfig. See error codes.
iState
USINT
Corresponds to the status variable of the process data stInData.iState, see VAR_IN_OUT. During command execution (bBusy = TRUE) this output is set to 0. This output is therefore suitable for assessing the status of the terminal in normal operation. Interfering states during configuration and reading through the register communication are hidden.
iTerminalType
WORD
Contents of register 8 (terminal name). When used with the correct terminal, the content should be 0x05DD (1501dec).
iSpecialType
WORD
Contents of register 29 (special version)
iFirmwareVersion
WORD
Contents of register 9 (firmware version)
sDescription
STRING
Terminal name, special version and firmware version as string (e.g. 'terminal KL1501-0000 / firmware 1C').
bDimRampAbsolute
TRUE: The dimming ramp is set absolute, i.e. each switching step requires the same ramp time, as specified under iSetRampTime.
sRampTime
STRING
Set ramp time in plain text.
bWatchdogDisable
TRUE: Watchdog is disabled.
tWatchdogTimeout
TIME
Set watchdog time.
iTimeoutOnValue
UINT
Set light value, which is output when a fieldbus error occurs with current process data > 0.
iTimeoutOffValue
UINT
Set light value, which is output when a fieldbus error occurs with current process data = 0.
sDimmerMode
STRING
Set dimmer mode in plain text.
sAfterShortCircuit
STRING
Set behaviour after short circuit in plain text.
sLineFrequency
STRING
Set mains frequency in plain text.
Development environment
Target platform
IO Hardware
PLC libraries to include
TwinCAT v3.1.4018.26
PC/CX
KL2751, KL2761
Tc2_IoFunctions from v3.3.5.0