ItpResetEx2
from library version 6.1.21 and TwinCAT version 2.10 Build 1304
ItpResetEx2 1:
The function block 'ItpResetEx2' executes a channel reset, which deletes all existing tables of the NC channel. In contrast to the outdated function block ItpReset, an active channel is stopped first, before the reset is executed. This simplifies programming in the PLC, since no explicit check is necessary to ascertain whether the axes are still in motion.
Interface
bExecute       : BOOL;
tTimeOut       : TIME;
sNciToPlc      : NciChannelToPlc;
NciChannelToPlc
bBusy          : BOOL;
bErr           : BOOL;
nErrId         : UDINT;
Input
Data type
bExecute
The command is triggered by a rising edge at this input.
tTimeOut
TIME
ADS timeout delay (the bBusy signal can be active for longer than tTimeOut)
Input & output
Data type
sNciToPlc
NciChannelToPlc
The structure of the cyclic channel interface from the NCI to the PLC. This structure is only accessed for reading.
Output
Data type
bBusy
This output remains TRUE as long as the axes are stopped according to their set value and the function block has executed the reset successfully, or an error is present at bErr. While Busy = TRUE, no new command will be accepted at the inputs.
bErr
This output is switched to TRUE as soon as an error occurs during the execution of a command. The command-specific error code is contained in 'nErrId'. Is reset to FALSE by the execution of a command at the inputs.
nErrId
UDINT
Contains the command-specific error code of the most recently executed command. Is reset to 0 by the execution of a command at the inputs. The error numbers in ErrId can be looked up in the ADS error documentation or in the NC error documentation (error codes above 0x4000).
Development Environment
Target System Type
PLC Libraries to include
TwinCAT v2.10.0
PC (i386)
TcNci.lib