"Index offset" specification for drive parameter (Index group 0x7000 + ID)
Index offset (Hex) | Access | Drive type | Data type | Phys. unit | Definition range | Description | Note |
0x00000001 | Read | every | UINT32 | 1 | [1 ... 255] | Drive ID |
0x00000002 | Read | every | UINT8[30+1] | 1 | 30 characters | Drive name |
0x00000003 | Read | every | UINT32 | 1 | s. ENUM (>0) |
0x00000004 | Read/Write | every | UINT32 | 1 | Byteoffset | Input address offset (I/O-Input-Image) | change I/O address |
0x00000005 | Read/Write | every | UINT32 | 1 | Byteoffset | Output address offset (I/O-Output-Image) | change I/O address |
0x00000006 | Read/Write | every | UINT16 | 1 | [0,1] | motor polarity |
0x0000000A | Read/Write | every | UINT32 | 1 | s. ENUM (>0) | drive mode |
0x0000000B | Read/Write | every | REAL64 | % | [-1.0 ... 1.0] | Minimum output limit (output limitation) (Default setting: -1.0 == -100%) |
0x0000000C | Read/Write | every | REAL64 | % | [-1.0 ... 1.0] | Maximum output limit (output limitation) (Default setting: 1.0 == 100%) |
0x0000000D | Read | every | UINT32 | INC |
| Maximum number of output increments (output mask) |
0x00000010 | Read/Write | every | UINT32 | 1 |
| Internal Drive Control double word to determine the drive operation modes | Reserved! |
0x00000011 | Read/Write | every | UINT32 | 1 | ≥ 5 | Internal drive reset counter (time in NC cycles for enable and reset) | Reserved! |
0x00000020 | Read/Write | every | UINT32 | 1 | s. ENUM (≥0) | Drive dead time compensation mode 0: Off (Default) 1: On (with velocity) 2: On (with velocity and acceleration) | s. appendix |
0x00000021 | Read/Write | every | UINT32 | 1 |
| Control double word (32 bits) for the drive dead time compensation: Bit 0 = 0: relative I/O times (default) Bit 0 = 1: absolute I/O times |
0x00000022 | Read/Write | every | INT32 | ns | [±1.0E+9] | Sum of the parameterized time shifts for the drive dead time compensation (typically positive numerical values) |
0x00000101 | Read/Write | Servo | REAL64 | e.g. mm/s | >0.0 | Reference velocity at reference output (velocity pre-control) | Base Unit / s |
0x00000102 | Read/Write | Servo | REAL64 | % | [0.0 ... 5.0] | reference output in percent |
0x00000103 | Read | Servo | REAL64 | e.g. mm/s | >0.0 | resulting velocity at 100% output | Base Unit / s |
0x00000104 | Read/Write | Servo | REAL64 | e.g. mm/s | ±∞ | velocity offset (DAC offset) for drift calibration (offset calibration) of the axis | Base Unit / s |
0x00000105 | Read/Write | Servo (Sercos, Profi Drive, AX200x, CANopen) | REAL64 | 1 | [0.0 ... 100000000.0] | velocity scaling (scaling factor to react to the weight in the drive) | For Sercos, Profi Drive, AX200x, CANopen |
0x00000106 | Read/Write | Profi Drive DSC | UINT32 | 0.001 * 1/s | ≥ 0 | Profibus/Profi Drive DSC: Position control gain Kpc | Only for Profi Drive DSC |
0x00000107 | Read/Write | Profi Drive DSC | REAL64 | 1 | ≥ 0.0 | Profibus/Profi Drive DSC: Scaling for calculation of 'XERR' (default: 1.0) | Only for Profi Drive DSC |
0x00000109 | Read/Write | Servo | REAL64 | 1 | [0.0 ... 100000000.0] | position scaling (scaling factor to react to the weight in the drive) | For Sercos, CANopen |
0x0000010A | Read/Write | Servo | REAL64 | 1 | [0.0 ... 100000000.0] | acceleration scaling (scaling factor to react to the weight in the drive) | For Sercos, Profi Drive, AX200x, CANopen |
0x0000010B | Read/Write | Servo | REAL64 | 1 | [0.0 ... 100000000.0] | Torque scaling (rotary motor) or force scaling (linear motor) (scaling factor to react to the weight in the drive) | For Sercos, Profi Drive, AX200x, CANopen |
0x0000010D | Read/Write | Servo (Sercos, CANopen) | REAL64 | s | [0.0 ... 1.0] | Damping time for drive velocity output | For Sercos, CANopen |
0x0000010E | Read/Write | Servo (Sercos, CANopen) | REAL64 | s | [0.0 ... 1.0] | Damping time for drive acceleration output | For Sercos, CANopen |
0x0000010F | Read/Write | Servo (Sercos, CANopen) | REAL64 | s | [0.0 ... 1.0] | Damping time for drive torque output or force output | For Sercos, CANopen |
0x00000110 | Read/Write | Servo (Sercos, CANopen) | UINT32 | 1 | s. ENUM (≥0) | Optional output filtering of the set position value: Filter type 0: OFF (default) 1: Moving Average 2: P-Tn | For Sercos, CANopen |
0x00000111 | Read/Write | Servo (Sercos, CANopen) | REAL64 | s | [0.0 ... 1.0] | Optional output filtering of the position setpoint: The maximum filter time depends on the NC cycle time and is limited to the following maximum value: 1 ms => 64 ms | For Sercos, CANopen |
0x00000112 | Read/Write | Servo (Sercos, CANopen) | UINT32 | 1 | [0 ... 10] | Optional output filtering of the position setpoint: Filter order 'n' (only for P-Tn type) | For Sercos, CANopen |
0x00000120 | Read/Write | Servo/hydraulics/ | UINT32 | 1 | ≥ 0 | Table ID (0: no table) | Only for KL4xxx, M2400, Universal |
0x00000121 | Read/Write | Servo/hydraulics | UINT32 | 1 | ≥ 0 | Interpolation type 0: linear 2: Spline | Only for KL4xxx, M2400, Universal |
0x00000122 | Read/Write | Servo/hydraulics | REAL64 | % | [-1.0 ... 1.0] | Output offset in percent Acts according to the characteristic evaluation! | Only for KL4xxx, M2400, Universal |
0x00000151 | Read/Write | Servo/non-linear | REAL64 | 1 | [0.0 ... 100.0] | Quadrant equalizing factor (relation between quadrants I and III) |
0x00000152 | Read/Write | Servo / non-linear | REAL64 | 1 | [0.01 ... 1.0] | velocity reference point in percent (1.0 == 100 %) |
0x00000153 | Read/Write | Servo / non-linear | REAL64 | 1 | [0.01 ... 1.0] | Output reference point in percent (1.0 == 100%) |
0x00000301 | Read/Write | Stepper motor | UINT8 |
| Bit mask: Cycle 1 |
0x00000302 | Read/Write | Stepper motor | UINT8 |
| Bit mask: Cycle 2 |
0x00000303 | Read/Write | Stepper motor | UINT8 |
| Bit mask: Cycle 3 |
0x00000304 | Read/Write | Stepper motor | UINT8 |
| Bit mask: Cycle 4 |
0x00000305 | Read/Write | Stepper motor | UINT8 |
| Bit mask: Cycle 5 |
0x00000306 | Read/Write | Stepper motor | UINT8 |
| Bit mask: Cycle 6 |
0x00000307 | Read/Write | Stepper motor | UINT8 |
| Bit mask: Cycle 7 |
0x00000308 | Read/Write | Stepper motor | UINT8 |
| Bit mask: Cycle 8 |
0x00000310 | Read/Write | Stepper motor | UINT8 |
| Bit mask: Holding current |