"Index offset" specification for axis parameter (Index group 0x4000 + ID)
Index offset (Hex) | Access | Axis type | Data type | Phys. unit | Definition range | Description | Note |
0x00n00000 | read | every (Structure for all axis parameters) | { |
| General AXIS PARAMETER STRUCTURE (NC/CNC), also contains the sub-elements such as encoder, controller and drive (s. MC_ReadParameterSet in TcMc.lib) |
UINT32 | 1 |
| Axis ID | ||||
UINT8[30+1+1] | e.g. mm |
| Axis name | ||||
UINT32 | 1 |
| Axis type | ||||
| 512 bytes | ||||
0x00000001 | read | every | UINT32 | 1 |
| Axis ID |
0x00000002 | read | every | UINT8[30+1] | 1 |
| Axis name |
0x00000003 | read | every | UINT32 | ENUM |
| Axis type |
0x00000004 | read | every | UINT32 | µs |
| Cycle time axis (SEC) |
0x00000005 | read | every | UINT8[10+1] | 1 |
| physical unit |
0x00000006 | Read/Write | every | REAL64 | e.g. mm/s |
| ref. velocity in cam direction |
0x00000007 | Read/Write | every | REAL64 | e.g. mm/s |
| ref. velocity in sync direction |
0x00000008 | Read/Write | every | REAL64 | e.g. mm/s |
| velocity hand slow |
0x00000009 | Read/Write | every | REAL64 | e.g. mm/s |
| velocity hand fast |
0x0000000A | Read/Write | every | REAL64 | e.g. mm/s |
| velocity rapid traverse |
0x0000000F | Read/Write | every | UINT16 | 1 | 0/1 | position range monitoring? |
0x00000010 | Read/Write | every | REAL64 | e.g. mm |
| position range window |
0x00000011 | Read/Write | every | UINT16 | 1 | 0/1 | motion monitoring? |
0x00000012 | Read/Write | every | REAL64 | s |
| motion monitoring time |
0x00000013 | Read/Write | every | UINT16 | 1 | 0/1 | loop? |
0x00000014 | Read/Write | every | REAL64 | e.g. mm |
| Looping distance (±) |
0x00000015 | Read/Write | every | UINT16 | 1 | 0/1 | target position monitoring? |
0x00000016 | Read/Write | every | REAL64 | e.g. mm |
| target position window |
0x00000017 | Read/Write | every | REAL64 | s |
| target position monitoring time |
0x00000018 | Read/Write | every | REAL64 | e.g. mm |
| pulse way in pos. direction |
0x00000019 | Read/Write | every | REAL64 | e.g. mm |
| pulse way in neg. direction |
0x0000001A | Read/Write | every | UINT32 | ENUM (≥0) |
| Error reaction mode: 0: instantaneous (default) 1: delayed (e.g. for Master/Slave coupling) | From TC 2.11 |
0x0000001B | Read/Write | every | REAL64 | s | [0...1000] | Error delay time (if delayed error reaction is selected) | From TC 2.11 |
0x0000001C | Read/Write | every | UINT16 | 1 | 0/1 | Couple slaves via actual values if not ready to operate? | From TC 2.11 |
0x0000001D | Read/Write | every | REAL64 | e.g. mm/s^2 | [0, 0.01...1.0E10] | Acceleration for transition profile for switching from SET to ACTUAL values (fading of position): | From TC 2.11 R2 |
0x0000001E | Read/Write | every | UINT32 | ENUM (≥0) |
| Fast Axis Stop Signal Type: Signal type selection to force a Fast Axis Stop (s. Bit 7 from Drive->nStatus4)"0 (SignalType_OFF)","1 (SignalType_RisingEdge)","2 (SignalType_FallingEdge)","3 (SignalType_BothEdges)","4 (SignalType_HighActive)","5 (SignalType_LowActive)" | from TC 2.11 R3 |
0x00000020 | Read/Write | every | UINT16 | 1 | 0/1 | Allow motion commands for slave axis? Default: FALSE | From TC 2.11 |
0x00000021 | Read/Write | every | UINT16 | 1 | 0/1 | Allow motion commands for axes with active external setpoint generation? | from TC 2.11 R2 |
0x00000026 | Read/Write | every | UINT32 | 1 |
| interpretation of the units (position, velocity, time) Bit 0: Velocity in x/min instead of x/s Bit 1: Position in thousandths of the base unit Bit 2: Modulo position display | See encoder! bit array |
0x00000027 | Read/Write | every | REAL64 | e.g. mm/s |
| max. allowed velocity |
0x00000028 | Read/Write | every | REAL64 | e.g. mm |
| motion monitoring window |
0x00000029 | Read/Write | every | UINT16 | 1 | 0/1 | PEH time monitoring? | Posi. end and accurate stop |
0x0000002A | Read/Write | every | REAL64 | s |
| PEH monitoring time |
0x0000002B | Read/Write | every | UINT16 | 1 | 0/1 | Backlash compensation? |
0x0000002C | Read/Write | every | REAL64 | e.g. mm |
| Backlash |
0x00000030 | read | every | UINT16 | 1 | [0,1] | Persistent data e.g. for actual position and reference state of the encoder? | boot parameter |
0x00000031 | read | every | { | AmsAddr | 1 | Read the hardware AMS address (AMS Net ID and device port) | ALT! |
0x00000031 | read | every | { | AmsAddr ChannelNo | 1 | Read the hardware AMS address (AMS Net ID and device port) and the channel number (0=Channel A, 1=Channel B) |
0x00000033 | read | every | { | 1 | 0/1 | General APPLICATION REQUEST STRUCTURE (NC/NCI), (see MC_ReadApplicationRequest in TcMc2.lib) | From TC 2.11 R2 |
0x00000051 | read | Channel: every | UINT32 |
| Channel ID |
0x00000052 | read | Channel: every | UINT8[30+1] |
| Channel name |
0x00000053 | read | Channel: every | UINT32 |
| Channel type |
0x00000054 | read | Group: every | UINT32 |
| Group ID |
0x00000055 | read | Group: every | UINT8[30+1] |
| Group name |
0x00000056 | read | Group: every | UINT32 |
| Group type |
0x00000057 | read | every | UINT32 |
| Number of encoders |
0x00000058 | read | every | UINT32 |
| Number of controllers |
0x00000059 | read | every | UINT32 |
| Number of drives |
0x0000005A | read | every | { |
| read all sub-elements of an axis: |
UINT32[ 9 ] | 1 | [0, 1...255] | Axis encoder IDs | ||||
UINT32[ 9 ] | 1 | [0, 1...255] | Axis controller IDs | ||||
UINT32[ 9 ] | 1 | [0, 1...255] | Axis drive IDs | ||||
} 108 bytes |
0x00000101 | Read/Write | Servo | REAL64 | e.g. mm/s^2 |
| Acceleration |
0x00000102 | Read/Write | Servo | REAL64 | e.g. mm/s^2 |
| Deceleration |
0x00000103 | Read/Write | Servo | REAL64 | e.g. mm/s^3 |
| Jerk |
0x00000104 | Read/Write | Servo | REAL64 | s | [0.0 ... 1.0] | Deceleration time between velocity and position values of the setpoint generator in seconds | Default value: 0.0 s |
0x00000105 | Read/Write | Servo | UINT32 | ENUM |
| Override type for velocity: 1: Related to internal reduced velocity (without iteration) 2: Related to original external start velocity (without iteration) 3: Related to internal reduced velocity (optimization by means of iteration) 4: Related to original external start velocity (optimization by means of iteration) | Default value: type 1 |
0x00000106 | Read/Write | Servo | REAL64 | 1 | [0.0 ... 1.0E6] | Maximum allowed velocity jump for dynamic reduction D V = factor * min(A+, A-) * DT | Default value: 0.0 |
0x00000107 | Read/Write | Servo | UINT16 | 1 | [0,1] | Activates acceleration and jerk limitation for the auxiliary axis (Q1 to Q5) | Default value: 1 |
0x00000108 | Read/Write | Servo | REAL64 | e.g. mm | [0.0..1000.0] | Radius of the tolerance sphere for the auxiliary axes | From TC V2.9 B932 |
0x00000109 | Read/Write | Servo | REAL64 | e.g. mm | [0.0..10000.0] | Maximum allowed position deviation if the tolerance sphere is reduced Only for auxiliary axes | From TC V2.9 B1013 |
0x0000010A | Read/Write | Servo | REAL64 | e.g. mm/s^2 | [0.01 ... 1.0E20] | Fast Axis Stop: Acceleration (s.a. Fast Axis Stop Signal Type) | From TC 2.11 R3 |
0x0000010B | Read/Write | Servo | REAL64 | e.g. mm/s^2 | [0.01 ... 1.0E20] | Fast Axis Stop: Deceleration (s.a. Fast Axis Stop Signal Type) | From TC 2.11 R3 |
0x0000010C | Read/Write | Servo | REAL64 | e.g. mm/s^3 | [0.1 ... 1.0E30] | Fast Axis Stop: Jerk (s.a. Fast Axis Stop Signal Type) | From TC 2.11 R3 |
0x00000201 | Read/Write | Stepper motor | UINT32 | ENUM |
| operation mode stepper motor |
0x00000202 | Read/Write | Stepper motor | REAL64 | e.g. mm/STEP | [1.0E-6 ... 1000.0] | Distance scaling of a motor step |
0x00000203 | Read/Write | Stepper motor | REAL64 | e.g. mm/s | [0.0 ... 1000.0] | Minimum velocity for velocity profile |
0x00000204 | Read/Write | Stepper motor | UINT32 | 1 | [0 ... 100] | Number of steps per frequency/velocity step |
0x00000205 | Read/Write | Stepper motor | UINT32 | 1 |
| Motor mask as sync pulse | Not implemented! |
0x00000301 | Read/Write | high/low | REAL64 | e.g. mm | [0.0 ... 100000.0] | Creep distance in pos. direction |
0x00000302 | Read/Write | high/low | REAL64 | e.g. mm | [0.0 ... 100000.0] | Creep distance in neg. direction |
0x00000303 | Read/Write | high/low | REAL64 | e.g. mm | [0.0 ... 100000.0] | Braking distance in pos. direction |
0x00000304 | Read/Write | high/low | REAL64 | e.g. mm | [0.0 ... 100000.0] | Braking distance in neg. direction |
0x00000305 | Read/Write | high/low | REAL64 | s | [0.0 ... 60.0] | Braking deceleration in pos. direction |
0x00000306 | Read/Write | high/low | REAL64 | s | [0.0 ... 60.0] | Braking deceleration in neg. direction |
0x00000307 | Read/Write | high/low | REAL64 | s | [0.0 ... 60.0] | Switching time from high to low speed |
0x00000308 | Read/Write | high/low | REAL64 | e.g. mm | [0.0 ... 100000.0] | Creep distance stop |
0x00000309 | Read/Write | high/low | REAL64 | s | [0.0 ... 60.0] | Delay time to release brake |
0x0000030A | Read/Write | high/low | REAL64 | s | [0.0 ... 60.0] | Pulse time in pos. direction |
0x0000030B | Read/Write | high/low | REAL64 | s | [0.0 ... 60.0] | Pulse time in neg. direction |
ENCODER |
0x00n10001 | read | Encoder: every | UINT32 | 1 | [1 ... 255] | Encoder ID n = 0: Standard encoder for the axis n > 0: n-th encoder for the axis (optional) |
0x00n10002 | read | Encoder: every | UINT8[30+1] | 1 | 30 characters | Encoder name |
0x00n10003 | read | Encoder: every | UINT32 | 1 | s. ENUM (>0) |
0x00n10004 | Read/Write | Encoder: every | UINT32 | 1 | Byteoffset | Input address offset (I/O-Input-Image) | change I/O address |
0x00n10005 | Read/Write | Encoder: every | UINT32 | 1 | Byteoffset | Output address offset (I/O-Output-Image) | change I/O address |
0x00n10006 | Read/Write | Encoder: every | REAL64 | e.g. mm/INC | [1.0E-12 ... 1.0E+30] | resulting scaling factor (numerator / denominator) Note: from TC 3.0 the scaling factor consists of two components – numerator and denominator (default: 1.0). |
0x00n10007 | Read/Write | Encoder: every | REAL64 | e.g. mm | [±1.0E+9] | Position offset |
0x00n10008 | Read/Write | Encoder: every | UINT16 | 1 | [0,1] | Encoder count direction |
0x00n10009 | Read/Write | Encoder: every | REAL64 | e.g. mm | [0.001 ... 1.0E+9] | modulo factor |
0x00n1000A | Read/Write | Encoder: every | UINT32 | 1 | s. ENUM (>0) |
0x00n1000B | Read/Write | Encoder: every | UINT16 | 1 | 0/1 | soft end min. monitoring? |
0x00n1000C | Read/Write | Encoder: every | UINT16 | 1 | 0/1 | Soft end max. monitoring |
0x00n1000D | Read/Write | Encoder: every | REAL64 | mm |
| Soft end position min. |
0x00n1000E | Read/Write | Encoder: every | REAL64 | mm |
| Soft end position max. |
0x00n1000F | Read/Write | Encoder: every | UINT32 | 1 | s. ENUM (≥0) | Encoder evaluation direction (enable for log. counting direction) | s. appendix |
0x00n10010 | Read/Write | Encoder: every | REAL64 | s | [0.0...60.0] | Filter time for position actual value in seconds (P-T1) |
0x00n10011 | Read/Write | Encoder: every | REAL64 | s | [0.0...60.0] | Filter time for velocity actual value in seconds (P-T1) |
0x00n10012 | Read/Write | Encoder: every | REAL64 | s | [0.0...60.0] | Filter time for acceleration actual value in seconds (P-T1) |
0x00n10013 | Read/Write | Encoder: every | UINT8[10+1] | 1 |
| physical unit | Not implemented! |
0x00n10014 | Read/Write | Encoder: every | UINT32 | 1 |
| interpretation of the units (position, velocity, time) Bit 0: Velocity in x/min instead of x/s Bit 1: Position in thousandths of the base unit | Not implemented! bit array |
0x00n10015 | read | Encoder: every | UINT32 | INC | [0x0... 0xFFFFFFFF] | Encoder mask (maximum value of the encoder actual value in increments) Note: From TwinCAT 2.11 R2 the encoder mask may be any numerical value (e.g. 3600000) and does not have to correspond to a continuous sequence of binary ones (2n-1). | Read-only parameter see also "Encoder Sub Mask" parameter |
0x00n10016 | Read/Write | Encoder: every | UINT16 | 1 | 0/1 | Actual position correction (measurement system error correction)? |
0x00n10017 | Read/Write | Encoder: every | REAL64 | s | [0.0...60.0] | Filter time for actual position correction in seconds (P-T1) |
0x00n10019 | Read/Write | Encoder: every | UINT32 | 1 | s. ENUM (≥0) | s. appendix | |
0x00n1001A | Read/Write | Encoder: every | UINT32 | 1 | s. ENUM (≥0) | Not implemented! | |
0x00n1001B | Read/Write | Encoder: every | REAL64 | e.g. mm | [≥0, modulo factor/2] | Tolerance window for modulo-start |
0x00n1001C | read | Encoder: every | UINT32 | 1 | s. ENUM (≥0) |
0x00n1001D | read | Encoder: every | UINT16 | 1 | 0/1 | Incremental or absolute encoder? 0: Incremental encoder type 1: Absolute encoder type |
0x00n10023 | Read/Write | Encoder: every | REAL64 | e.g. mm/INC | [1.0E-12 ... 1.0E+30] | Component of the scaling factor: numerator (=> scaling factor numerator / scaling factor denominator) | From TC 3.0 |
0x00n10024 | Read/Write | Encoder: every | REAL64 | 1 | [1.0E-12 ... 1.0E+30] | Component of the scaling factor: denominator (=> scaling factor numerator / scaling factor denominator) Default: 1.0 | From TC 3.0 |
0x00n10025 | Read/Write | Encoder: every | { | e.g. mm/INC | [1.0E-12 ... 1.0E+30] | Component of the scaling factor: numerator Component of the scaling factor: denominator (=> scaling factor numerator / scaling factor denominator) | From TC 3.0 |
0x00n10030 | Read/Write | Encoder: every | UINT32 | 1 |
| Internal Encoder Control DWORD for specifying the operation modes and properties | From 211R3 B2227 |
0x00n10101 | Read/Write | E: INC | UINT16 | 1 | [0,1] | inverse search direction for ref.cam? |
0x00n10102 | Read/Write | E: INC | UINT16 | 1 | [0,1] | inverse search direction for sync pulse? |
0x00n10103 | Read/Write | E: INC | REAL64 | e.g. mm | [±1000000.0] | Reference position |
0x00n10104 | Read/Write | E: INC | UINT16 | 1 | [0,1] | distance monitoring between Ref. cams and sync pulse active? | Not implemented! |
0x00n10105 | Read/Write | E: INC | UINT32 | INC | [0 ... 65536] | minimum gap between Ref. cams and sync pulse in increments | Not implemented! |
0x00n10106 | Read/Write | E: INC | UINT16 | 1 | [0,1] | external sync pulse? |
0x00n10107 | Read/Write | E: INC | UINT32 | 1 | s. ENUM (>0) | Reference mode | s. appendix |
0x00n10108 | Read/Write | E: INC | UINT32 | 1 | [0x0000000F... 0xFFFFFFFF] Binary mask: (2n - 1) | Encoder Sub Mask (maximum value of the absolute range of the encoder actual value in increments) Used, for example, as a reference mark for the referencing mode "Software Sync" and for the NC Retain Data "ABSOLUTE (MODULO)", "INCREMENTAL (SINGLETURN ABSOLUTE)" ) Note 1: The Encoder Sub Mask must be smaller than or equal to the Encoder Mask. Note 2: The Encoder Mask must be an integer multiple of the Encoder Sub Mask. Note 3: The Encoder Sub Mask must be a continuous sequence of binary ones (2n-1), e.g. 0x000FFFFF. | NEW see also "Encoder Mask" |
0x00n10110 | Read/Write | E: INC (encoder simulation) | REAL64 | 1 | [0.0 ... 1000000.0] | scaling/weight of the noise part for the simulation encoder |
CONTROLLER: |
0x00n20001 | Read | Controller: every | UINT32 | 1 | [1 ... 255] | Controller ID n = 0: Standard axis controller n > 0: n-th controller of the axis (optional) |
0x00n20002 | Read | Controller: every | UINT8[30+1] | 1 | 30 characters | Controller name |
0x00n20003 | Read | Controller: every | UINT32 | 1 | s. ENUM (>0) |
0x00n2000A | Read/Write | Controller: every |
| 1 | s. ENUM (>0) | Controller mode
0x00n2000B | Read/Write | Controller: every | REAL64 | % | [0.0 ... 1.0] | Weighting of the velocity pre-control (default value: 1.0 = 100 %) |
0x00n20010 | Read/Write | Controller: every | UINT16 | 1 | 0/1 | Lag error monitoring Pos.? |
0x00n20011 | Read/Write | Controller: every | UINT16 | 1 | 0/1 | Lag error monitoring Velocity? |
0x00n20012 | Read/Write | Controller: every | REAL64 | e.g. mm |
| max. lag error position |
0x00n20013 | Read/Write | Controller: every | REAL64 | s |
| Max. lag error filter time position |
0x00n20014 | Read/Write | Controller: every | REAL64 | e.g. mm/s |
| max. lag error velocity |
0x00n20015 | Read/Write | Controller: every | REAL64 | s |
| Max. lag error filter time velocity |
0x00n20100 | Read/Write | P/PID (Pos., (velocity) | REAL64 | 1 | [0.0...1.0] | Maximum output limitation (±) for controller total output | (Default value: 0.5 == 50%) |
0x00n20102 | Read/Write | P/PID (pos.) | REAL64 | e.g. mm/s/ mm | [0.0...1000.0] | Proportional gain kp or kv Unit: Base Unit / s / Base Unit | Position control |
0x00n20103 | Read/Write | PID (pos.) | REAL64 | s | [0.0 ... 60.0] | Integral action time Tn | Position control |
0x00n20104 | Read/Write | PID (pos.) | REAL64 | s | [0.0 ... 60.0] | Derivative action time Tv | Position control |
0x00n20105 | Read/Write | PID (pos.) | REAL64 | s | [0.0 ... 60.0] | Damping time Td | Position control |
0x00n20106 | Read/Write | PP (Pos.) | REAL64 | e.g. mm/s/ mm | [0.0...1000.0] | Additional proportional gain, kp or kv respectively, that applies above a limiting velocity in percent. Unit: Base Unit / s / Base Unit | Position control |
0x00n20107 | Read/Write | PP (Pos.) | REAL64 | % | [0.0...1.0] | Threshold velocity in percent above which the additional proportional gain, kp or kv, applies |
0x00n20108 | Read/Write | P/PID (Acc.) | REAL64 | s | [0.0 ... 100.0] | Proportional gain ka | Acceleration pre-control |
0x00n2010D | Read/Write | P/PID | REAL64 | mm | [0.0 ... 10000.0] | "dead band" for position error (control deviation) (for P/PID controllers with velocity or torque interface) | reserved function |
0x00n2010F | Read/Write | P/PP/PID (pos.) | REAL64 | (mm/s) / mm | [0.0...1000.0] | Slave coupling difference control: Proportional gain kcp | Slave coupling difference control |
0x00n20110 | Read/Write | P (Pos.) | UINT16 | 1 | 0/1 | Automatic offset calibration: active/passive |
0x00n20111 | Read/Write | P (Pos.) | UINT16 | 1 | 0/1 | Automatic offset calibration: hold mode |
0x00n20112 | Read/Write | P (Pos.) | UINT16 | 1 | 0/1 | Automatic offset calibration: Fading mode |
0x00n20114 | Read/Write | P (Pos.) | REAL64 | % | [0.0 ... 1.0] | Automatic offset calibration: pre-control limit |
0x00n20115 | Read/Write | P (Pos.) | REAL64 | s | [0.1 ... 60.0] | Automatic offset calibration: time constant |
0x00n20116 | Read/Write | PID (pos.) | REAL64 | % | [0.0...1.0] | Maximum output limitation (±) for I part in percent (default setting: 0.1 = 10%) |
0x00n20117 | Read/Write | PID (pos.) | REAL64 | % | [0.0...1.0] | Maximum output limitation (±) for D part in percent (default setting: 0.1 = 10%) |
0x00n20118 | Read/Write | PID (pos.) | UINT16 | 1 | 0/1 | Deactivation of the I part during an active positioning process (assuming I part active)? (Default setting: 0 = FALSE) |
0x00n20120 | Read/Write | P/PID (pos.) | REAL64 | s | ≥0 | PT-1 filter value for position error (pos. control deviation) | Reserved function, no standard! |
0x00n20202 | Read/Write | P/PID (velocity) | REAL64 | 1 | [0.0...1000.0] | Proportional gain kp or kv | Velocity control |
0x00n20203 | Read/Write | PID (velocity) | REAL64 | s | [0.0 ... 60.0] | Integral action time Tn | Velocity control |
0x00n20204 | Read/Write | PID (velocity) | REAL64 | s | [0.0 ... 60.0] | Derivative action time Tv | Velocity control |
0x00n20205 | Read/Write | PID (velocity) | REAL64 | s | [0.0 ... 60.0] | Damping time Td | Velocity control |
0x00n20206 | Read/Write | PID (velocity) | REAL64 | % | [0.0...1.0] | Maximum output limitation (±) for I part in percent (default setting: 0.1 = 10%) | Velocity control |
0x00n20207 | Read/Write | PID (velocity) | REAL64 | % | [0.0...1.0] | Maximum output limitation (±) for D part in percent (default setting: 0.1 = 10%) | Velocity control |
0x00n2020D | Read/Write | P/PID (velocity) | REAL64 | mm/s | [0.0 ... 10000.0] | "dead band" for velocity error (control deviation) (for P/PID controllers with velocity or torque interface) | reserved function |
0x00n20220 | Read/Write | P/PID (velocity) | REAL64 | s | ≥0 | PT-2 filter value for velocity error (vel. control deviation) | Velocity control, not standard! |
0x00n20221 | Read/Write | P/PID (velocity) | REAL64 | s | ≥0 | PT-1 filter value for velocity error (vel. control deviation) | Reserved function, no standard! |
0x00n20250 | Read/Write | P/PI (observer) | UINT32 | 1 | s. ENUM (≥0) | Observer mode for control in the torque interface 0: OFF (default) 1: LUENBERGER | From TC 2.10 Build 1320 |
0x00n20251 | Read/Write | P/PI (observer) | REAL64 | Nm / A | >0.0 | Motor: Torque constant KT |
0x00n20252 | Read/Write | P/PI (observer) | REAL64 | kg m2 | >0.0 | Motor: Moment of inertia JM |
0x00n20253 | Read/Write | P/PI (observer) | REAL64 | Hz | [100.0 ... 2000.0] Default: 500 | Bandwidth f0 |
0x00n20254 | Read/Write | P/PI (observer) | REAL64 | 1 | [0.0 ... 2.0] Default: 1.0 | Correction factor kc |
0x00n20255 | Read/Write | P/PI (observer) | REAL64 | s | [0.0 ... 0.01] Default: 0.001 | Velocity filter (1st order): time constant T |
0x00n20A03 | Read/Write | P/PID (MW) | REAL64 | cm^2 | [0.0 ... 1000000] | Cylinder area AA of the A side in cm^2 | Reserved parameters! |
0x00n20A04 | Read/Write | P/PID (MW) | REAL64 | cm^2 | [0.0 ... 1000000] | Cylinder area AB of the B side in cm^2 | Reserved parameters! |
0x00n20A05 | Read/Write | P/PID (MW) | REAL64 | cm^3/s | [0.0 ... 1000000] | Nominal volume flow Qnom in cm^3/s | Reserved parameters! |
0x00n20A06 | Read/Write | P/PID (MW) | REAL64 | bar | [0.0 ... 1000000] | Nominal pressure or valve pressure drop Pnom in bar | Reserved parameters! |
0x00n20A07 | Read/Write | P/PID (MW) | UINT32 | 1 | [1 ... 255] | Axis ID for the system pressure Po | Reserved parameters! |
DRIVE: |
0x00n30001 | Read | Drive: every | UINT32 | 1 | [1 ... 255] | Drive ID |
0x00n30002 | Read | Drive: every | UINT8[30+1] | 1 | 30 characters | Drive name |
0x00n30003 | Read | Drive: every | UINT32 | 1 | s. ENUM (>0) |
0x00n30004 | Read/Write | Drive: every | UINT32 | 1 | Byteoffset | Input address offset (I/O-Input-Image) | change I/O address |
0x00n30005 | Read/Write | Drive: every | UINT32 | 1 | Byteoffset | Output address offset (I/O-Output-Image) | change I/O address |
0x00n30006 | Read/Write | Drive: every | UINT16 | 1 | [0,1] | motor polarity |
0x00n3000A | Read/Write | Drive: every | UINT32 | 1 | s. ENUM (>0) | drive mode |
0x00n3000B | Read/Write | Drive: every | REAL64 | % | [-1.0 ... 1.0] | Minimum output limit (output limitation) (Default setting: -1.0 = -100%) |
0x00n3000C | Read/Write | Drive: every | REAL64 | % | [-1.0 ... 1.0] | Maximum output limit (output limitation) (default setting: 1.0 = 100%) |
0x00n3000D | Read | Drive: every | UINT32 | INC |
| Maximum number of output increments (output mask) |
0x00n30010 | Read/Write | Drive: every | UINT32 | 1 |
| Internal Drive Control DWord to determine the drive operation modes | Reserved! |
0x00n30011 | Read/Write | every | UINT32 | 1 | ≥ 5 | Internal drive reset counter (time in NC cycles for enable and reset) | Reserved! |
0x00n30101 | Read/Write | D: Servo | REAL64 | e.g. mm/s | >0.0 | Reference velocity at reference output (velocity pre-control) |
0x00n30102 | Read/Write | D: Servo | REAL64 | % | [0.0 ... 5.0] | reference output in percent (Default setting: 1.0 = 100%) |
0x00n30103 | Read | D: Servo | REAL64 | e.g. mm/s | >0.0 | resulting velocity at 100% output |
0x00n30104 | Read/Write | D: Servo | REAL64 | e.g. mm/s | ±∞ | velocity offset (DAC offset) for drift calibration (offset calibration) of the axis |
0x00n30105 | Read/Write | D: Servo (Sercos, Profi Drive, AX200x, CANopen) | REAL64 | 1 | [0.0 ... 100000000.0] | velocity scaling (scaling factor to react to the weight in the drive) | For Sercos, Profi Drive, AX200x, CANopen |
0x00n30106 | Read/Write | D: Profi Drive DSC | UINT32 | 0.001 * 1/s | ≥ 0 | Profibus/Profi Drive DSC: Position control gain Kpc | Only for Profi Drive DSC |
0x00n30107 | Read/Write | D: Profi Drive DSC | REAL64 | 1 | ≥ 0.0 | Profibus/Profi Drive DSC: Scaling for calculation of 'XERR' (default: 1.0) | Only for Profi Drive DSC |
0x00n30109 | Read/Write | D: Servo (Sercos, CANopen) | REAL64 | 1 | [0.0 ... 100000000.0] | position scaling (scaling factor to react to the weight in the drive) | For Sercos, CANopen |
0x00n3010A | Read/Write | D: Servo (Sercos, Profi Drive, AX200x, CANopen) | REAL64 | 1 | [0.0 ... 100000000.0] | acceleration scaling (scaling factor to react to the weight in the drive) | For Sercos, Profi Drive, AX200x, CANopen |
0x00n30120 | Read/Write | D: Servo/hydraulics | UINT32 | 1 | ≥ 0 | Table ID (0: no table) | Only for KL4xxx, M2400, Universal |
0x00n30121 | Read/Write | D: Servo/hydraulics | UINT32 | 1 | ≥ 0 | Interpolation type 0: linear 2: Spline | Only for KL4xxx, M2400, Universal |
0x00n30122 | Read/Write | Servo/hydraulics | REAL64 | % | [-1.0 ... 1.0] | Output offset in percent Acts according to the characteristic evaluation! | Only for KL4xxx, M2400, Universal |
0x00n30151 | Read/Write | D: Servo / non-linear | REAL64 | 1 | [0.0 ... 100.0] | Quadrant equalizing factor (relation between quadrants I and III) |
0x00n30152 | Read/Write | D: Servo / non-linear | REAL64 | 1 | [0.01 ... 1.0] | velocity reference point in percent (1.0 = 100 %) |
0x00n30153 | Read/Write | D: Servo / non-linear | REAL64 | 1 | [0.01 ... 1.0] | Output reference point in percent (1.0 = 100 %) |
0x00030301 | Read/Write | D: Stepper motor | UINT8 | 1 |
| Bit mask: Cycle 1 |
0x00030302 | Read/Write | D: Stepper motor | UINT8 | 1 |
| Bit mask: Cycle 2 |
0x00030303 | Read/Write | D: Stepper motor | UINT8 | 1 |
| Bit mask: Cycle 3 |
0x00030304 | Read/Write | D: Stepper motor | UINT8 | 1 |
| Bit mask: Cycle 4 |
0x00030305 | Read/Write | D: Stepper motor | UINT8 | 1 |
| Bit mask: Cycle 5 |
0x00030306 | Read/Write | D: Stepper motor | UINT8 | 1 |
| Bit mask: Cycle 6 |
0x00030307 | Read/Write | D: Stepper motor | UINT8 | 1 |
| Bit mask: Cycle 7 |
0x00030308 | Read/Write | D: Stepper motor | UINT8 | 1 |
| Bit mask: Cycle 8 |
0x00030310 | Read/Write | D: Stepper motor | UINT8 | 1 |
| Bit mask: Holding current |