"Index offset" specification for axis functions (Index group 0x4200 + ID)
Index offset (Hex) | Access | Axis type | Data type | Phys. unit | Definition range | Description | Note |
0x00000001 | Write | every | VOID |
| Reset axis | For FIFO axes too! |
0x00000002 | Write | every | VOID |
| Stop axis | For FIFO axes too! |
0x00000003 | Write | every | VOID |
| Clear axis (task) | For FIFO axes too! |
0x00000004 | Write | every | { |
| Emergency stop (with controlled ramp) | Only for PTP axes! |
REAL64 | e.g. mm/s^2 | > 0.0 | Deceleration (must be greater than or equal to the original deceleration) | ||||
REAL64 | e.g. mm/s^3 | > 0.0 | Jerk (must greater than or equal to the original jerk) | ||||
0x00000005 | Write | PTP axis | { |
| Parameterizable stop (with controlled ramp) | Only for PTP axes! Reserved function, |
REAL64 | e.g. mm/s^2 | > 0.0 | Deceleration | ||||
REAL64 | e.g. mm/s^3 | > 0.0 | Jerk | ||||
0x00000009 | Write | PTP axis | { |
| Oriented stop (oriented end position) | Only for PTP axes! |
REAL64 | e.g. degrees | ≥ 0.0 | Modulo end position (modulo target position) | ||||
REAL64 | e.g. mm/s^2 | > 0.0 | Deceleration (currently not active) | ||||
REAL64 | e.g. mm/s^3 | > 0.0 | Jerk (not yet implemented) | ||||
0x00000010 | Write | every | VOID |
| Reference axis ("calibration") |
0x00000011 | Write | every | { |
| New end position axis | Modified from TwinCAT 3 |
UINT32 | ENUM | s. appendix | End position type (see appendix) | ||||
UINT32 |
| Reserve (TwinCAT 3) | ||||
REAL64 | e.g. mm | ±∞ | New end position (target position) | ||||
0x00000012 | Write | every | { |
| New end position and new velocity axis |
UINT32 | ENUM | s. appendix | Command type (s. appendix) | ||||
REAL64 | e.g. mm/s | ≥ 0.0 | New final velocity (requested travel velocity) | ||||
REAL64 | e.g. mm | ±∞ | Optional: Switchover position from which the new travel profile is activated | ||||
0x00000015 | Write | every | { |
| New dynamic parameters for active positioning |
REAL64 | e.g. mm/s^2 | > 0.0 | Acceleration | ||||
REAL64 | e.g. mm/s^3 | > 0.0 | Optional: Jerk (not yet implemented) | ||||
0x00000016 | ReadWrite | every SERVO | Write(80 bytes) |
| Universal Axis Start (UAS): | Always to SEC Port 501! Modified from TwinCAT 3 |
UINT32 | ENUM | s. appendix | Start type (s. appendix) |
UINT32 | 1 | ≥ 0 | Bit mask for checks and operation modes |
REAL64 | e.g. mm | ±∞ | End position (target position) |
REAL64 | e.g. mm/s | ≥ 0.0 | Required velocity Vrequ |
REAL64 | e.g. mm/s^2 | ≥ 0.0 | Optional: Acceleration |
REAL64 | e.g. mm/s^2 | ≥ 0.0 | Optional: Deceleration |
REAL64 | e.g. mm/s^3 | ≥ 0.0 | Optional: Jerk |
UINT32 | ENUM | s. appendix | Buffer mode (command buffer) |
UINT32 |
REAL64 | e.g. mm | ±∞ | Optional: Blending position (command blending position) |
REAL64 | e.g. mm/s | ≥ 0.0 | Optional: Initial segment velocity Vi |
REAL64 | e.g. mm/s | ≥ 0.0 | Optional: Segment end velocity Vf |
Read |
UINT16 | 1 | ≥ 0 | Command number (job number) |
UINT16 | 1 | ≥ 0 | Command status |
0x00000017 | ReadWrite | SERVO | Write(80 bytes) |
| "Master/slave decoupling" and "Universal axis start (UAS)": Merge of decoupling command of a slave axis (IdxOffset: 0x00000041) and the subsequent universal axis start (UAS) (IdxOffset: 0x00000016) | Not yet released! |
UINT32 | 1 | ≥ 0 | Bit mask for checks and operation modes (Default value: 0) |
REAL64 | e.g. mm/s^2 | ≥ 0.0 | Acceleration |
REAL64 | e.g. mm/s^2 | ≥ 0.0 | Deceleration |
REAL64 | e.g. mm/s^3 | ≥ 0.0 | Jerk |
UINT32 |
Read |
0x00000018 | Write | every | VOID |
| Release axis lock for motion commands (TcMc2) |
0x00000019 | Write | every | UINT32 | 1 | > 0 | Set external axis error (runtime error) | Caution when using! |
0x00n0001A | Write | every | { |
| Set actual axis position | Caution when using! For FIFO axes too! Always to SEC Port 501! Modified from TwinCAT 3 |
UINT32 | ENUM | s. appendix | Actual position type (see appendix) | ||||
UINT32 |
REAL64 | e.g. mm | ±∞ | Actual position for axes n = 0: standard encoder of the axis n > 0: n-th encoder for the axis (optional) | ||||
0x00n0001B | Write | every | UINT32 | 1 | 0/1 | Set reference flag ("calibrate flag") n = 0: Standard encoder for the axis n > 0: n-th encoder for the axis (optional) | Caution when using! For FIFO axes too! |
0x00n0001C | Write | SERVO | { |
| Set only actual axis position without manipulating the set position (also for slave and with active process) | Caution when using! |
REAL64 | e.g. mm | ±∞ | Actual position for axes n = 0: standard encoder of the axes > 0: nth encoder of the axis (optional) Caution when using! | ||||
0x00n0001D | Write | every | { |
| Actual value setting of the axis on the drive side n = 0: Standard encoder for the axis n > 0: n-th encoder for the axis (optional) | Caution when using! Only for CANopen! |
REAL64 | e.g. mm | ±∞ | Actual position for axis | ||||
0x00n0001E | Write | every | { |
| Set a new encoder scaling factor on the fly (in motion of the axis) | Caution when using! Always to SEC Port 501! Modified from TwinCAT 3 |
UINT16 | ENUM | 1 | Encoder scaling factor type 1: Absolute 2: Relative | ||||
UINT16 |
| ControlWord | ||||
UINT32 |
REAL64 | e.g. mm/INC | [1.0E-8 ... 100.0] | New encoder scaling factor n > 0: n-th encoder for the axis (optional) | ||||
0x00n0001F | Write | every | { |
| Set actual axis position on the fly (in motion of the axis) | Caution when using! Always to SEC Port 501! |
UINT32 | ENUM |
| Position type for setting actual value on the fly 1: Absolute 2: Relative | ||||
UINT32 | 1 |
| Control double word, e.g. for "clearing the lag error" | ||||
REAL64 |
| Reserve | ||||
REAL64 | e.g. mm | ±∞ | New actual axis position | ||||
UINT32 |
| Reserve | ||||
UINT32 |
| Reserve | ||||
0x00000020 | Write | every 1D start | { |
| Standard axis start: | Modified from TwinCAT 3 |
UINT32 | ENUM | s. appendix | Start type (s. appendix) | ||||
UINT32 |
REAL64 | e.g. mm | ±∞ | End position (target position) | ||||
REAL64 | e.g. mm/s | ≥0.0 | Required velocity | ||||
0x00000021 | Write | every 1D start | { |
| Extended axis start (SERVO): | Modified from TwinCAT 3 |
UINT32 |
REAL64 | e.g. mm/s | ≥ 0.0 | Required velocity | ||||
UINT32 | 0/1 | 0/1 | Standard acceleration? | ||||
UINT32 |
REAL64 | e.g. mm/s^2 | ≥ 0.0 | Acceleration | ||||
UINT32 | 0/1 | 0/1 | Standard deceleration? | ||||
UINT32 |
REAL64 | e.g. mm/s^2 | ≥ 0.0 | Deceleration | ||||
UINT32 | 0/1 | 0/1 | Standard jerk? | ||||
UINT32 |
REAL64 | e.g. mm/s^3 | ≥ 0.0 | Jerk | ||||
0x00000022 | Write | SERVO(MW) | { |
| Special axis start (SERVO): | Reserved start function, no standard! Modified from TwinCAT 3 |
UINT32 |
REAL64 | mm/s | ≥ 0.0 | Required start velocity | ||||
REAL64 | e.g. mm | ±∞ | Position for a new velocity level | ||||
REAL64 | e.g. mm/s | ≥ 0.0 | New end velocity level | ||||
UINT32 |
UINT32 |
UINT32 |
0x00000023 | Write | SERVO | { |
| Start external setpoint specification (setting by cyclic axis interface PLCtoNC) | Modified from TwinCAT 3 |
UINT32 | ENUM | 1: Absolute 2: Relative | |||||
UINT32 |
REAL64 | e.g. mm | ±∞ | New end position (target position) optional! | ||||
REAL64 |
0x00000024 | Write | SERVO | VOID |
| Stop/disable external setpoint specification |
0x00000025 | Write | SERVO | { |
| Start reversing operation for positioning (SERVO): | Modified from TwinCAT 3 |
UINT32 | ENUM | 1 | Start type (default: 1) | ||||
UINT32 |
REAL64 | e.g. mm | ±∞ | End position 1 (target position) | ||||
REAL64 | e.g. mm | ±∞ | End position 2 (target position) | ||||
REAL64 | 0/1 | 0/1 | Required velocity | ||||
REAL64 | s | ≥ 0.0 | Idle time | ||||
0x00000026 | Write | every | { |
| Start drive output | Modified from TwinCAT 3 |
UINT32 | ENUM | s. appendix | Output type (s. appendix) | ||||
UINT32 |
REAL64 | e.g. % | ±∞ | Required output value (e.g. %) | ||||
0x00000027 | Write | every | VOID |
| Stop drive output |
0x00000028 | Write | every | { |
| Change the drive output: |
0x00000029 | Write | every | VOID |
| Instantaneously adopt current override value and freeze until next override change! | Reserved function, no standard! |
0x0000002A | Write | every | { |
| Calculate and set encoder offset | Reserved function, no standard! |
0x0000002B | ReadWrite | every | WriteData: s. 'UAS' |
| Stop external setpoint generator and continuous endless motion ('UAS': Universal axis start) | Reserved function, no standard! |
0x0000002C | Write | every | UINT32 |
| ≥ 0 | Set "homing state" (for internal use) | New from TwinCAT 3 |
0x0000002D | ReadWrite | Servo | Write |
| Switches an NC-controlled axis to "Cyclic Synchronous Torque Mode" (CST) and sets a torque setpoint for it. | Danger during use!
UINT32 |
| Torque-axis start type: 0x3001: Absolute 0x3002: Relative | ||||
UINT32 | 1 (bit array) |
| Internal control mask (bit array): 00000000_00000001 (bit 0): Use manual torque for initialization. 10000000_000000000 (bit 31): Update/refresh parameter for current command in 'ContinuousUpdate' mode (fTorqueRamp, fVelocityLimitHigh, fVelocityLimitLow), do not increase cmd no. | ||||
UINT32 | 0/1 | 0/1 | Mode: 0: Default (discrete) 1: ContinuousUpdate | ||||
UINT32 | ENUM | see appendix | Buffer mode only ABORTING possible | ||||
REAL64 | Nm or % | [0.0 … 1.0E10] | Torque target value (signed value) | ||||
REAL64 | Nm/s or %/s | [0.0 … 1.0E10] | Torque change velocity | ||||
REAL64 | e.g. mm/s | [0.0 ... 1.0E10] | Velocity limit high | ||||
REAL64 | e.g. mm/s | [0.0 … 1.0E10] | Velocity limit low | ||||
REAL64 | e.g. mm/s^2 | [0.0 … 1.0E10] | Acceleration | ||||
REAL64 | e.g. mm/s^2 | [0.0 … 1.0E10] | Deceleration | ||||
REAL64 | Nm or % | [0.0 … 1.0E10] | Optional: Manual torque start value (sync value) | ||||
Read |
UINT16 | 1 | >=0 | Command number (job number) | ||||
UINT16 | 1 | >=0 | Command status | ||||
0x0000002E |
| Reserved |
0x0000002F |
| Reserved |
0x00000030 | Write | SERVO | { |
| Start section compensation (SERVO) | Only affects older TwinCAT 2 systems |
UINT32 | ENUM | s. appendix | Compensation type (see appendix) | ||||
UINT32 |
REAL64 | e.g. mm/s^2 | ≥ 0.0 | Max. acceleration increase | ||||
REAL64 | e.g. mm/s^2 | ≥ 0.0 | Max. deceleration increase | ||||
REAL64 | e.g. mm/s | > 0.0 | Max. increase velocity | ||||
REAL64 | e.g. mm/s | > 0.0 | Base velocity for the process | ||||
REAL64 | e.g. mm | ±∞ | Path difference to be compensated | ||||
REAL64 | e.g. mm | > 0.0 | Path distance for compensation | ||||
0x00000030 | ReadWrite | SERVO returns the actually implemented parameters as return values | { |
| Start section compensation (SERVO) | Changed from TwinCAT 2 211R3 TwinCAT 3 |
UINT32 |
REAL64 | e.g. mm/s^2 | ≥ 0.0 | => Max. acceleration increase <= Returns the implemented acceleration increase (new in 'TcMc2.lib' or 'Tc2_MC2.library') | ||||
REAL64 | e.g. mm/s^2 | ≥ 0.0 | => Max. deceleration increase <= Returns the implemented deceleration increase (new in 'TcMc2.lib' or 'Tc2_MC2.library') | ||||
REAL64 | e.g. mm/s | > 0.0 | => Requested max. increase velocity <= Returns the implemented increase velocity | ||||
REAL64 | e.g. mm | ±∞ | => Requested path difference to be compensated <= Returns the implemented path difference | ||||
REAL64 | e.g. mm | > 0.0 | => Requested max. distance for compensation <= Returns implemented distance | ||||
UINT32 | 1 | ≥ 0 | <= Returns Warning ID (e.g. 0x4243) | ||||
UINT32 |
0x00000031 | Write | SERVO | VOID |
| Stop section compensation (SERVO) |
0x00000032 | Write | SERVO | { |
| Start reversing operation with velocity jumps (SERVO): (can be used to determine the velocity step response) | Modified from TwinCAT 3 |
UINT32 |
REAL64 | e.g. mm/s | ±∞ | Required velocity 1 | ||||
REAL64 | e.g. mm/s | ±∞ | Required velocity 2 | ||||
REAL64 | s | > 0.0 | Travel time for velocity 1 and 2 | ||||
UINT32 | 1 | 0, 1,2,3... | Optional: Number of repetitions, | ||||
UINT32 |
0x00000033 | Write | SERVO | { |
| Sine oscillation sequence - used as single sinus oscillation (sinus generator) - used as sinus oscillation sequence (e.g. for bode plot) | Modified from TwinCAT 3 |
UINT32 | ENUM | 1 | Start type (fixed to start type 1 yet) | ||||
UINT32 |
REAL64 | e.g. mm/s | > 0.0 | Base amplitude (e.g. 2.5 mm/s) | ||||
REAL64 | Hz | [0.0 .... 10.0] | Base frequency (e.g. 1.953125 Hz) | ||||
REAL64 | e.g. mm/s | ≥ 0.0 | Start amplitude at begin (e.g. 0.0 mm/s) | ||||
REAL64 | e.g. mm/REV | > 0.0 | Feed constant motor (per motor turn) (e.g. 10.0 mm/REV) | ||||
REAL64 | Hz | ≥ 1.0 | Frequency range: start frequency (e.g. 20.0 Hz) | ||||
REAL64 | Hz | ≤ 1/(2*dT) | Frequency range: stop frequency (e.g. 500.0 Hz) | ||||
REAL64 | s | > 0.0 | Step duration (e.g. 2,048s) | ||||
UINT32 | 1 | [1 ... 200] | Number of measurements (step cycles) (e.g. 20) | ||||
UINT32 | 1 |
| Number of parallel measurements (e.g. 1) not used yet! | ||||
0x00000034 | Write | SERVO | { |
| Phasing - Start Phasing - Stop Phasing |
UINT32 | ENUM | 1 | PhasingType: 1: ABSOLUTE | ||||
UINT32 | 1 | ≥ 0 | Control Mask Bit 0: Continuous Update | ||||
UINT32 | 1 | ≥ 0 | Master axis ID | ||||
UINT32 |
| Reserve | ||||
REAL64 | e.g. mm | ±∞ | Phase shift | ||||
REAL64 | e.g. mm/s | > 0.0 | Velocity | ||||
REAL64[4] |
| Reserve | ||||
UINT32 |
| Reserve | ||||
UINT32 | 1 | ENUM | Buffer mode | ||||
REAL64 | e.g. mm | ±∞ | Blending position | ||||
0x00n0003B | Write | PTP axis | VOID |
| Triggers NC encoder reinitilization to valid IO values n = 0: Standard encoder of the axis n > 0: n-th encoder of the axis (optional) | Danger during use! The axis status index offset 0x00n10018 can be used to read out whether NC encoder reinitilization has been completed. Port 501 |
0x00000040 (0x00n00040) | Write | Master/Slave coupling (SERVO) | { |
| Master/Slave coupling (SERVO): | Extension for "flying saw"! Angle >0.0 and £ 90.0 degrees (parallel saw: 90.0 degrees) |
UINT32 | ENUM | s. appendix | Slave type/coupling type (see appendix) | ||||
UINT32 | 1 | [1...255] | Axis ID of the master axis/group | ||||
UINT32 | 1 | [0...8] | Subindex n of the master axis (default: value: 0) | ||||
UINT32 | 1 | [0...8] | Subindex n of the slave axis (default: value: 0) | ||||
REAL64 | 1 | [±1000000.0] | Parameter 1: Linear: Gear ratio FlySawVelo: Reserve FlySaw: Abs. synchron position master [mm] | ||||
REAL64 | 1 | [±1000000.0] | Parameter 2:Linear: Reserve FlySawVelo: Reserve FlySawPos: Abs. synchron position slave [mm] | ||||
REAL64 | 1 | [±1000000.0] | Parameter 3: Linear: Reserve FlySawVelo: Angle of inclination in [DEGREES] FlySawPos: Angle of inclination in [DEGREES] | ||||
REAL64 | 1 | [±1000000.0] | Parameter 4:Linear: Reserve FlySawVelo: Gear ratio FlySawPos: Gear ratio | ||||
| Master/Slave coupling (SERVO): | Multi master coupling Version V1 and V2 Modified from TwinCAT 3 |
UINT32 | 1 | [1...8] | Subindex n of the master axis (default: value: 0) | ||||
UINT32 | 1 | [1...8] | Subindex n of the slave axis (default: value: 0) | ||||
UINT32 | 1 | [0...255] | Axis ID master 2 | ||||
UINT32 | 1 | [0...255] | Axis ID master 3 | ||||
UINT32 | 1 | [0...255] | Axis ID master 4 | ||||
UINT32 | 1 | [0...255] | Reserve (axis ID master 5) | ||||
UINT32 | 1 | [0...255] | Reserve (axis ID master 6) | ||||
UINT32 | 1 | [0...255] | Reserve (axis ID master 7) | ||||
UINT32 | 1 | [0...255] | Reserve (axis ID master 8) | ||||
UINT32 |
| Maximum acceleration/deceleration of the slave axis | ||||
UINT32 | 1 | ≥ 0 | Control mask, not previously used | ||||
UINT32 |
Extension V2 (Optional): | |||||||
REAL64 | e.g. mm/s^2 | ≥ 0.0 | Maximum deceleration of the slave axis | ||||
REAL64 | e.g. mm/s^3 | ≥ 0.0 | Maximum jerk of the slave axis | ||||
REAL64 | e.g. mm/s | ≥ 0.0 | Maximum velocity of the slave axis | ||||
REAL64 |
| Reserve | ||||
REAL64 |
| Reserve | ||||
} 64 or 104 bytes |
0x00000041 | Write | Master/slave decoupling (SERVO) | VOID |
0x00000041 | Write | Master/Slave decoupling with configurable follow-up function (SERVO) | { |
| Master/slave decoupling with configurable follow-up function (e.g. new end position, new velocity, stop, E-stop) (SERVO) | Not yet released! Modified from TC3 |
UINT32 | ENUM | s. appendix | Decoupling type (see appendix) | ||||
UINT32 |
REAL64 | e.g. mm | ±∞ | Optional: New end position | ||||
REAL64 | e.g. mm/s | > 0.0 | Optional: New requested velocity | ||||
REAL64 | e.g. mm/s^2 | ≥ 0.0 | Optional: Acceleration for new end position, new velocity and emergency stop (E-stop) | ||||
REAL64 | e.g. mm/s^2 | ≥ 0.0 | Optional: Deceleration for new end position, new velocity and emergency stop (E-stop) | ||||
REAL64 | e.g. mm/s^3 | ≥ 0.0 | Optional: Jerk for new end position, new velocity and emergency stop (E-stop) | ||||
0x00000042 | Write | Master/Slave coupling Type: LINEAR (&SPECIAL) | { |
| Change of the coupling parameters (SERVO): |
REAL64 | 1 | [±1000000.0] | Parameter 1: Linear: Gear ratio | ||||
REAL64 | 1 | [±1000000.0] | Parameter 2: Linear: Reserve | ||||
REAL64 | 1 | [±1000000.0] | Parameter 3: Linear: Reserve | ||||
REAL64 | 1 | [±1000000.0] | Parameter 4: Linear: Reserve | ||||
0x00000043 | Write | Master/slave table coupling Type: TABULAR | { |
| Change of the table coupling parameters (SERVO): |
| REAL64 | mm | ±∞ | Slave position offset | |||
| REAL64 | mm | ±∞ | Master position offset | |||
| Change of the table coupling parameters (SERVO): | Also for "Motion Function" |
REAL64 | mm | ±∞ | Slave position offset | ||||
REAL64 | mm | ±∞ | Master position offset | ||||
REAL64 | 1 | ±∞ (<> 0.0) | Slave position scaling | ||||
REAL64 | 1 | ±∞ (<> 0.0) | Master position scaling | ||||
REAL64 | e.g. mm | ±∞ | Absolute master activation position | ||||
0x00000044 | Write | Slave-Stop (SERVO) | VOID |
| Stop the "flying saw" (SERVO) | Only for "flying saw" |
0x00000045 (0x00n00045) | Write | Master/slave table coupling (SERVO) | { |
| Master/slave table coupling (SERVO): |
UINT32 | 1 | [1...255] | Axis ID of the master axis | ||||
UINT32 | 1 | [0...8] | Subindex n of the slave axis (default value: 0) | ||||
| SOLO TABLE SECTION | ||||
REAL64 | mm | ±∞ | Slave position offset (type: TABULAR) | ||||
REAL64 | mm | ±∞ | Master position offset (type: TABULAR) | ||||
UINT32 | 1 | [0,1] | Slave positions absolute (type: TABULAR) | ||||
UINT32 | 1 | [0,1] | Master positions absolute (type: TABULAR) | ||||
UINT32 | 1 | [1...255] | Table ID of the coupling table (type: TABULAR) | ||||
| MULTI TABLE SECTION | ||||
UINT16 | 1 | [0...8] | Number of tables (type: MULTITAB) Note: Misused as interpolation type for solo tables | ||||
UNIT16 | 1 | [0...8] | Number of profile tables (type: MULTITAB) | ||||
UNIT32[8] | 1 | [1...255] | Tables IDs of the coupling tables (type: MULTITAB) | ||||
0x00000046 | Write | Master/slave multi-tables | UINT32 | 1 | [1...255] | Correction table activation, correction table ID |
0x00000046 | Write | Master/slave multi-tables | { |
| Activation of correction table | Modified from TwinCAT 3 |
UINT32 | 1 | [1...255] | Correction table ID | ||||
UINT32 |
0x00000047 | Write | Master/slave multi-tables | UINT32 | 1 | [1..255] | Deactivation of profile table at the end of the cycle, table ID of the current monocyclic profile table |
0x00000048 | ReadWrite | Master/slave multi-tables | Write: UINT32 | 1 | [1..255] | Reading the last correction offset: Table ID of the correction table |
Read: REAL32 | e.g. mm | ±∞ | Offset by departing the correction table with the according table ID |
0x00000049 | Write | Master/slave table coupling Type: TABULAR | REAL64 | 1 | ±∞ | Change the slave table scaling factor for the slave table column |
0x0000004A(0x00n0004A) | Write | Master/Slave Universal Table Coupling (SERVO) | { |
| Master/Slave Solo Table Coupling (SERVO): | Modified from TwinCAT 3 |
UINT32 | 1 | 1...255] | Table ID of the coupling table (type: TABULAR) | ||||
UINT32 | 1 |
| Table interpolation type | ||||
REAL64 | mm | ±∞ | Slave position scaling (type: TABULAR) | ||||
REAL64 | mm | ±∞ | Master position scaling (type: TABULAR) | ||||
UINT32 | 1 | [0,1] | Slave position absolute ? | ||||
UINT32 | 1 | [0,1] | Master positions absolute ? | ||||
UINT32 | ENUM | s. appendix | Activation type of the change: 0: 'instantaneous' (default) 1: 'at master cam position' 2: 'at master axis position' 3: 'next cycle' | ||||
UINT32 |
REAL64 | mm | ±∞ | Activation position | ||||
UINT32 | ENUM | s. appendix | Master scaling type: 0: user defined (default) 1: scaling with auto offset 2: off | ||||
UINT32 | ENUM | s. appendix | Slave scaling type: 0: user defined (default) 1: scaling with auto offset 2: off | ||||
UINT32 | 1 |
UINT32 | 1 | [0,1] | Slave position absolute ? (Type: TABULAR) | ||||
UINT32 | 1 | [0,1] | Master positions absolute ? (Type: TABULAR) | ||||
UINT32 |
Extension for MultiCam: | |||||||
UINT32 | ENUM | s. appendix | Cam Operation Mode | ||||
UINT32 | 1 | [1…255] | Reference table ID | ||||
BYTE[104] |
0x0000004B(0x00n0004B) | Write | Master/slave universal flying saw (SERVO) | { |
| Master/slave synchronization coupling (SERVO): | Modified from TwinCAT 3 |
REAL64 | 1 | ±∞ (<> 0.0) | Gear ratio | ||||
REAL64 | mm | ±∞ | Master synchron position | ||||
REAL64 | mm | ±∞ | Slave synchron position | ||||
REAL64 | mm/s | ≥ 0.0 | Slave velocity (optional) | ||||
REAL64 | mm/s^2 | ≥ 0.0 | Slave acceleration (optional) | ||||
REAL64 | mm/s^2 | ≥ 0.0 | Slave deceleration (optional) | ||||
REAL64 | mm/s^3 | ≥ 0.0 | Slave jerk (optional) | ||||
UINT32 | 1 | ≥ 0 | Bit mask (default value: 0) | ||||
UINT32 |
0x0000004D(0x00n0004D) | Write | Master/slave table coupling Type: TABULAR | { |
| Change in table scaling (SERVO): | Modified from TwinCAT 3 |
UINT32 | ENUM | s. appendix | Activation type of the change 0: 'instantaneous' (default) 1: 'at master cam position' 2: 'at master axis position' 3: 'next cycle' | ||||
UINT32 |
REAL64 | e.g. mm | ±∞ | Activation position | ||||
UINT32 | ENUM | s. appendix | Master scaling type 0: user defined (default) 1: scaling with auto offset 2: off | ||||
UINT32 | ENUM | s. appendix | Slave scaling type 0: user defined (default) 1: scaling with auto offset 2: off | ||||
REAL64 | e.g. mm | ±∞ | Master position offset | ||||
REAL64 | e.g. mm | ±∞ | Slave position offset | ||||
REAL64 | 1 | ±∞ | Slave position scaling | ||||
Optional extension for MultiCam: | |||||||
UINT32 | 1 | ≥ 0 | Cam Table ID | ||||
UINT32 |
0x00000050 | Write | every | VOID |
| Deactivate complete axis (disable) |
0x00000051 | Write | every | VOID |
| Activate complete axis (enable) |
0x00000052 | Write | SERVO | { |
| Change of the active axis control loop (triple from encoder, controller and axis interfaces) with/without external setpoint specification: | Modified from TwinCAT 3 |
UINT32 | 1 | ≥ 0 | Number/index of the axis control loop | ||||
UINT32 | ENUM | s. appendix (>0) | Switching type for synchronization behavior 1: 'Standard' | ||||
REAL64 | 1 | ±∞ | Synchronization value for switching (optional) | ||||
UINT32 | 0/ 1 | 0/1 | External setpoint specification by means of axis interface ? Note: Not used so far! | ||||
UINT32 |
0x00000060 | Write | every | VOID |
| Deactivate drive output (disable) |
0x00000061 | Write | every | VOID |
| Activate drive output (enable) |
0x00000062 | Write | high/low | UINT16 | 1 | 0/1 | Release parking brake? 0: automatic activation (default) 1: mandatorily always released Note: |
0x00000063 | Write | only for SERCOS/SoE and CANopen/CoE | { |
| Activate "Drive Operation Mode" (e.g. Position Velo, Torque, etc.) | NEW from TC 3.1 B4022 (NC 4443) Always to SEC Port 501! |
INT32 | ENUM | [0; 1, 2, 3, …] Special cases: ≥ 100: SoE | New "Drive Operation Mode" (generic modes) | ||||
UINT32 | 1 | 0 | Reserve | ||||
0x00000070 | Write | every | VOID |
| Return of the axis from, e.g. a 3D group to its own PTP group |
* The following warning relates to index offset 0x0000002D:
Danger to life or risk of serious injury or damage to property due to unintentional movements of the axis When using the function block, the axis is switched to CST mode. After using the function block (especially after error situations), the axis may still be in CST mode. This can lead to sudden and unplanned movements (especially with lifting axes) when the axis is released.