"Index offset" specification for table parameter (Index group 0xA000 + ID)
Index offset (Hex)
Access
Table type
Data type
Phys. unit
Definition range
Note
0x00000001
Read
every
UINT32
1
[1 ... 255]
Table ID
0x00000002
Read
every
UINT8[30+1]
1
30 characters
Table name
0x00000003
Read
every
UINT32
1
s. ENUM (>0)
Table sub types
0x00000004
Read
every
UINT32
1
s. ENUM (>0)
Table main types
0x00000010
Read
every
UINT32
1
[0... 16777216]
Number of lines (n)
0x00000011
Read
every
UINT32
1
[0... 16777216]
Number of columns (m)
0x00000012
Read
every
UINT32
1
≥0
Number of total elements (n*m)
0x00000013
Read
equidistant table
REAL64
e.g. mm
≥0.0
Step size (position delta) (equidistant tables)
Base Unit
0x00000014
Read
cyclical table
REAL64
e.g. degrees
≥0.0
Master period (cyclical tables)
Base Unit
0x00000015
Read
cyclical table
REAL64
e.g. degrees
≥0.0
Slave difference per master period (cyclic tables)
Base Unit
0x0000001A
Read/Write
"Motion Function" (laws of motion)
Activation type for online changes of table data (MF only)
Modified from TC3
UINT32
ENUM
s. appendix
Activation mode
0: 'instantaneous' (default)
1: 'master cam pos.'
2: 'master' axis pos.'
3: 'next cycle'
4: 'next cycle once'
5: 'as soon as possible'
6: 'off'
7: 'delete queued data'
UINT32
Reserve (TC3)
REAL64
e.g. mm
Activation position
UINT32
ENUM
s. appendix
Master scaling type
0: user defined (default)
1: scaling with auto offset
2: off
UINT32
ENUM
s. appendix
Slave scaling type
2: off
0x00000020
Read/Write
every
Write single value [n,m]:
UINT32
1
[0 ... 16777216]
n-th line
UINT32
1
[0 ... 16777216]
m-th column
REAL64
e.g. mm
Single value
0x00000021
ReadWrite
every
*REAL64
e.g. mm
Read slave position for the specified master position (related to the "raw values" in the table)
0x00000022
ReadWrite
Write
Read the "Motion Function" as a "point cloud"
Only possible on a line-by-line basis!
(integer multiple)
Changed in TC3
UINT 16
1
0 /1
Prompt consistent data adoption?
UINT16
1
Bit mask (≥0)
Select bit mask (number of columns m is master position plus number of bits):
Bit 0: Pos (Slave)
Bit 1: Velo (Slave)
Bit 2: Acc (Slave)
Bit 3: Jerk (Slave)
UINT32
Reserve (TC3)
REAL64
e.g. mm
Startposition (Master)
REAL64
e.g. mm
> 0.0
Step size
Read
REAL64[x*m]
e.g. mm
Read from x lines from the master start position: (x*m) values (one or more lines)
0x00000023
ReadWrite
every
Write
Read slave values for the specified master position (related to the "raw values" in the table)
REAL64
e.g. mm
Master position
Read
REAL64
e.g. mm
Slave position
REAL64
mm/s
Slave velocity
REAL64
mm/s^2
Slave acceleration
0x00000024
ReadWrite
every
Write
Calculation of the master position for a given slave position
REAL64
e.g. mm
Slave position
REAL64
e.g. mm
Start position of the master
REAL64
e.g. mm
Offset to the slave position of the cam plate
REAL64
1
Scaling of the slave position of the cam plate
REAL64
e.g. mm
Offset to the master position of the cam plate
REAL64
1
Scaling of the master position of the cam plate
REAL64
Position accuracy of the master (default: 1.0E-3)
REAL64[5]
Reserved (40 bytes)
Read
UINT32
Lower master position valid
UINT32
Upper master position valid
REAL64
e.g. mm
Lower absolute master axis position
REAL64
e.g. mm
Upper absolute master axis position
REAL64
e.g. mm
Lower master cam plate position
REAL64
e.g. mm
Upper master cam plate position
REAL64
e.g. mm
Lower slave position offset
REAL64
e.g. mm
Upper slave position offset
REAL64[5]
Reserved (40 bytes)
0x00000050
Read/Write
every
REAL64 [64]
1
Characteristic values in the table
0x00000050
ReadWrite
every
Write
Read the characteristic values in a table in relation to the nominal master velocity
Modified from TC3
REAL64 [64]
Optional nominal master reference velocity "fMasterVeloNom" (standardized => 1.0 mm/s),
the remaining elements are not evaluated
Read
REAL64 [64]
0x00000115
Write
monotonic linear, monotonic cyclic,
Set/change the table scaling:
REAL64
1
[ ± 1000000.0]
Original weighting of the table
REAL64
e.g. mm
[ ± 1000000.0]
Master column position offset
REAL64
1
[ ± 1000000.0]
Scaling of the master column
REAL64
e.g. mm
[ ± 1000000.0]
Position offset of the slave column
REAL64
1
[ ± 1000000.0]
Scaling of the slave column
REAL64
e.g. mm
[ ± 1000000.0]
Lower range limit (starting position)
REAL64
e.g. mm
[ ± 1000000.0]
Upper range limit (end position)
0x01000000 +n-th start line
Read/Write[<=16777216]
every
REAL64[x*m] }
e.g. mm
Read/write from x lines from the nth line: (x*m) values (one or more lines) Value range n: [0 ... 16777216]
Only possible on a line-by-line basis! (integer multiple)
0x02000000 +m-th start column
every
REAL64[x*n] }
e.g. mm
Read/write x columns from the mth column: (x*n) values (one or more columns)Value range m: [0 ... 16777216]
Only possible on a column-by-column basis! (integer multiple)
0x04000000 +n
Read
Reserved
0x05000000 +n-th start line
"Motion Function" (motion laws) Data:STRUCT [x*m]
Read/write x lines from the nth line: (x*m) structures (one or more lines) Value range n: [0 ... 16777216]
(integer multiple)
Modified from TC3
UINT32
1
Abs. point index
(not evaluated)
UINT16
ENUM
Function type
1: Polynomial 1
15: Polynomial 5
UINT16
ENUM
Point type
0: default
1: ignore
REAL64
mm
Master position
REAL64
mm
Slave position
REAL64
mm /s
Slave speed
REAL64
mm/s^2
Slave acceleration
REAL64
mm/s^3
Slave jerk
0x06000000 +m-th start column
"Motion Function" (motion laws) Data:STRUCT [x* n ]
Read/write x columns from the mth column: (x*n) structures (one or more columns) Value range m: [0 ... 16777216]
(integer multiple)
Modified from TC3
UINT32
1
Abs. point index
(not evaluated)
UINT16
ENUM
Function type
1: Polynomial 1
15: Polynomial 5
UINT16
ENUM
Point type
0: default
1: ignore
INT32
1
Rel. address index at end point
(Default: 1)
UINT32
Reserve (TC3)
REAL64
mm
Master position
REAL64
mm
Slave position
REAL64
mm/s
Slave speed
REAL64
mm/s^2
Slave acceleration
REAL64
mm/s^3
Slave jerk